Rule of thumb for derating PV output based on ambient temp. Is there such a thing?
Fe-Wood
Solar Expert Posts: 96 ✭✭
I finally have my PV panels up and running. I'm wondering if there is a rule of thumb for de-rating PV output based on ambient temp.
As always- Thanks for all your help!
As always- Thanks for all your help!
Comments
-
Re: Rule of thumb for derating PV output based on ambient temp. Is there such a thing?I finally have my PV panels up and running. I'm wondering if there is a rule of thumb for de-rating PV output based on ambient temp.
As always- Thanks for all your help!
Not so much a rule of thumb as a specification. The panels should list temperature coefficients for Vmp, Imp and POWERmp as a function of temperature.
The STC output assumes a panel temp of 25C, so it is an easy calculation from there once you figure out how hot the panels will get in the sun. That heating can be large compared to changes in ambient temperature. And it will depend on how well ventilated the area under the panels is.SMA SB 3000, old BP panels. -
Re: Rule of thumb for derating PV output based on ambient temp. Is there such a thing?
PV modules usually have exact specifications for voltage loss and current gain based on cell temperature. Converting ambient temperature to cell temperature is more complicated as ambient temperature is one of several factors contributing to cell temperature.
If you have one of those infrared thermometers, you can semi-accurately measure cell temperature (will be actually measuring glass temperature) and you can compute from their from the panel specs. -
Re: Rule of thumb for derating PV output based on ambient temp. Is there such a thing?
So, looking at the Data Sheet:
Cs6p - Canadian SolarTemperature Coefficient CS6P-235/240/245/250/255P Electrical Data- Pmax -0.43 %/℃
- Voc -0.34 %/℃
- Isc 0.065 %/℃
- NOCT 45±2℃ (Normal Operating Cell Temperature
So, if you your air temperature is 30C and you have a 15C rise for a cell temperature of 45C, and you are using an MPPT charge controller, the calculation should look something like this:- Power = 245 watts [1 + (-0.43 %/℃ power derate) * (Tcell - Tstd)]
- Power = 245 watts [1+ (-0.0043 /℃ power derate) * (45C - 25C)] = 222.95 watts (note % shifted decimal point removed)
And assume 95% efficient controller:- 222.95 watts * 0.95 = 212 Watt output to battery (ignoring wiring losses)
Our standard rule of thumb for relatively warm locations with typically dirty/aging panels, wiring losses, and less than clear blue sky would be:- 245 watts * 0.77 panel+controller derating = 189 Watts typical maximum power from array+controller
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Rule of thumb for derating PV output based on ambient temp. Is there such a thing?
Thanks guys- I knew it was to vague a question to ask. Ambient temp. being the veriable and all. I guess I'll have to get a infered thermometer someday.
PS
I love the midnight solar Classic lite. The way it fluctuates the voltage to support the amperage needed to support a load... Awesome!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed