Mixing Cables sizes - Is this bad or OK?
KnowledgeSponge
Solar Expert Posts: 173 ✭✭✭
Scenario...
Two batteries connected in Parallel
3/0 cable from battery A+ to battery B+
3/0 cable from battery A- to battery B-
(Temporarily..I pan to go total 3/0 soon)
1/0 cable from battery A+ to Inverter +
1/0 cable from battery A- to Inverter -
(I just happen to have 1/0 cables at the moment).
As long as the load doesn't approach the capacity of the 1/0 cable, is there anything inherently dangerous or potentially damaging about this setup?
Re: Mixing Cables sizes - Is this bad or OK?
Not as long as the 1/0 from the batteries to the inverter is protected by appropriate fuse/breaker.
One change, though:
1/0 cable from battery B- to Inverter -
This will help keep the current even between batteries. -
Re: Mixing Cables sizes - Is this bad or OK?Cariboocoot wrote: »Not as long as the 1/0 from the batteries to the inverter is protected by appropriate fuse/breaker.
One change, though:
If there was a THANKS button....I'd hit it :cool:
What kind of breaker / fuse is commonly used for this? -
1/0 AWG is good for about 150 Amps continuous, so 100 to 125 Amps for the fuse/breaker.
Some options would include the Blue Sea battery terminal post fuses, these 'class T' fuses http://www.solar-electric.com/infubr.html or Bussmann breakers http://www.solar-electric.com/mr60ampdccib.html -
Re: Mixing Cables sizes - Is this bad or OK?Cariboocoot wrote: »1/0 AWG is good for about 150 Amps continuous, so 100 to 125 Amps for the fuse/breaker.
Thank you once again good sir :cool: