Diminished power presenting as low lights
djdenali
Registered Users Posts: 11 ✭
About two weeks ago, the lights in our house began to show about half the power as normal. We have a 12-Volt system (2 pairs or 6-Volt batteries---2 in series and each pair in parallel). I have the wiring connected as shown on page 584 of the 30th anniversary edition of The Solar Living SourceBook ( + of battery 1 to - of battery 2 (series) and + of battery 3 to - of battery 4 (series) THEN, - of battery 1 to - battery 3 then to the sun controller AND + of battery 4 to + of battery 2 then to the sun controller). All connections seem strong. All batteries individual showed 6+ volts.
ANy suggestions on how to get out lights back to full strength? Inverter works fine. Lights are the only load.
Thanks.
david
Thanks.
david
Re: Diminished power presenting as low lightsAbout two weeks ago, the lights in our house began to show about half the power as normal. We have a 12-Volt system (2 pairs or 6-Volt batteries---2 in series and each pair in parallel). I have the wiring connected as shown on page 584 of the 30th anniversary edition of The Solar Living SourceBook ( + of battery 1 to - of battery 2 (series) and + of battery 3 to - of battery 4 (series) THEN, - of battery 1 to - battery 3 then to the sun controller AND + of battery 4 to + of battery 2 then to the sun controller). All connections seem strong. All batteries individual showed 6+ volts.
Thanks.
david -
Well David, welcome to the forum.
What do you have for an inverter? Make / model?
Reason asking, most decent inverters will shut down due to low battery voltage long before you notice any output voltage drop at all. So unless you forgot to take off your sunglasses, I'd suspect problem with the inverter, or the wiring between the inverter and the lights, or a problem with the lights themselves.
The battery voltage you mention - - is that the voltage while under load? -
another question worthy of asking is what is charging them and at what current capacity over how much time? if they aren't getting enough or any charge then they slowly die. -
Thanks for all the responses. I should have noted the inverter has nothing to do with the lights. That was more for informational purposes. We have a 'load' coming from the sun controller directly to the house. The lights are the only load on this sun controller. Again, they worked fine a few weeks back. -
Do you have a link to show us that charge controller? I'll bet that is where your problem lies. Have you re-tightened the screws on the wire since you set it up? They loosen over time, copper 'flows' under pressure and time...
Re: Diminished power presenting as low lightsThanks for all the responses. I should have noted the inverter has nothing to do with the lights. That was more for informational purposes. We have a 'load' coming from the sun controller directly to the house. The lights are the only load on this sun controller. Again, they worked fine a few weeks back.
Wow you have a box that controls the output of the sun! I need one of them !
ThomOff grid since 1984. 430w of panel, 300w suresine , 4 gc batteries 12v system, Rogue mpt3024 charge controller , air breeze windmill, Mikita 2400w generator . Added 2@ 100w panel with a midnight brat -
Re: Diminished power presenting as low lightsBlackcherry04 wrote: »I see, said the blind man. It's much clearer now. The Lights have nothing to do with the Inverter, that was informational. I don't have a clue, dig out the multimeter and check the voltage.
You took my thoughts
But seriously, I really don't understand his setup, definitely not enough information to work with. Coming across as a mystery system, almost wondering if someone is pulling our leg. -
So he's got a Morningstar SunSaver charge controller with LOAD terminals that have some DC lights connected to it.
He's also got four 6 Volt batteries of non-specified size. These are wired as two parallel strings of two. If they are GC2's were looking at 440 Amp hours @ 12 Volts. To charge that you'd need a big array: absolute minimum of 385 Watts (based on 5% current & 17.5 Vmp for the PWM type controller).
The largest single SunSaver is 20 Amp, so it is unlikely the batteries have been properly charged. As a result they have become sulphated, with their capacity diminishing. Like finding you've got AAA batteries in D cell cases; the Voltage may read "right" at rest but there is no capacity there. Apply a load and the Voltage sags quickly.
We do not know the load in Amps/Volts/Watts. We do not know the wiring size or length. Therefor this is all just speculation. -
So, again, thanks for the sincere responses. Picking up a little sarcasm, but can't be too sure. Too clarify, I have other things to do than 'pull anybody's leg' about something like solar power. I am new to this phenomena and trying to gain clarity. The explanation from Cariboocoot sounds like what I'm working with. I am heading out this weekend, but will try to get some information on the return.
I did check each battery individually and they all read above 6 Volts, but do I understand, one needs to do this when the sun is off the panels? In that case, I need to recheck. Slowly, slowly, I'm working through this learning curve. I appreciate the feedback and patience.
david -
Two Voltage readings would help: one with no current going in or out (batteries at rest) and another with the load on but no charging (batteries under load). What you're looking for there is how much change happens between these states. A big Voltage drop indicates a loss of capacity.
- 612 Discussion Forums/Café
- 305 In the Weeds--Member's Choice
