Schneider Conext XW and GenSupp Plus
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »If you feed it split phase and pull 120V off it (step down mode), then it balances the inverter legs almost perfectly. With the transformer in step down configuration feeding the 120V loads, and the split phase loads coming direct off the AC disconnect panel for the inverter, it stays within a 1/2 amp between the two legs on both the inverter and the generator.
I looked at the wiring diagram, and the wiring for the step down configuration looks to be exact the same as if we would wire balancing configuration and then put all the 120V loads on a single leg - L2. -
Yeah, that's not a very good diagram. Basically, you can just wire the transformer 1 & 4 right into L1 and L2 on your inverter. Then hook the transformer 2 & 3 ( transformer center tap, which is actually the other ends of the identical primary and secondary windings in an auto transformer) to the inverter's neutral. And leave everything else as is - this is what Bill was suggesting. But my experience with this is that the transformer assists the low current leg but it doesn't provide perfect split phase balancing just wired in parallel with the inverter output with 120V loads on both legs. You can still get a leg imbalance up to 25%, which is better than without the transformer.
But if you feed all the 120V loads off ONE leg with the transformer then you get perfect balance at all times. I don't know if this applies to the Xantrex T240, but it does with the Outback PSX-240.
It's best to have a separate 120V panel because to put all your 120V loads on one bus bar in a split phase panel requires blank spaces between each single pole breaker. That can be done, but a separate 120V panel really cleans things up. That's my opinion on it.
Here - here's a better diagram showing split phase to split phase balancing:
When you balance by putting the transformer in parallel like this, as you can see the current can flow direct from the source to the load. And if that's the path of least resistance that's where it will go instead of thru the transformer windings. Split phase to split phase balancing actually requires somewhat of a voltage drop on the high current leg (and current flowing in the neutral) in order for it work. And that's why you can still get an imbalance. It helps, and this is the same method the XW's GenSupp Plus uses. But it's not perfect.
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »But my experience with this is that the transformer assists the low current leg but it doesn't provide perfect split phase balancing just wired in parallel with the inverter output with 120V loads on both legs. You can still get a leg imbalance up to 25%, which is better than without the transformer.
I see. So, it works much better if you only take 120V loads from L2, but do not use L1.
I have only two 240V loads. They're in different buildings 300 ft apart, and the inverter is in the garage, which is 100 ft away. And all the cables have reduced neutral. So, it's not very practical for me to re-wire. Probably I should look into replacing 120V with 240V loads instead. -
It's legal to use one size smaller neutral than the legs on 240V because the neutral only has to carry the imbalance between the legs. But when you wire for 120V only the neutral has to be the same size.
We actually have a couple 120V loads on our 240V panel because the 120V panel got full of breakers over the years and we added a couple more circuits. One of the loads that's on one leg of that split phase panel is the microwave. Just a few minutes ago my wife was heating up some leftovers for me for supper (yeah, eating late tonite) so I went to the meters menu and scrolled down to look at the current on L1 and L2 while the microwave was going. I think the microwave pulls 12 amps and it showed L1 at 7.8 and L2 (the leg the microwave is on) at 9.8. That's a 20% imbalance.
When the microwave turned off, leaving only 120V loads on, it dropped to 2.8 amps on both legs.
The way I have our auto transformer wired it should provide balancing for 120V loads on that 240V panel because it's in parallel with it and the inverter output, as shown in the above diagram I posted. It is also supplying our 120V panel with a "tap" off L1. Without the transformer there would've been a big imbalance with L2 at 15 amps and L1 at 2.8.
But if I run an extension cord from the microwave to one of the outlets that's on that 120V panel L1 and L2 from the inverter will stay perfectly balanced.
So - without rewiring anything just putting a PSX-240 in parallel with your XW (per the above diagram I posted) will help keep it more balanced, and your generator too.
I don't know what causes this, exactly. In theory the thing should perfectly balance split phase to split phase like it shows in the diagram. If you unbalance the load, power flows in the neutral and causes one side of the transformer to assist the other. It must be differences in the neutrals, resistance in the transformer windings, or something, that causes it to not be perfect like it is when you use it in pure step-down. It would take a whole lot of investigating to figure that out.
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »It's legal to use one size smaller neutral than the legs on 240V because the neutral only has to carry the imbalance between the legs. But when you wire for 120V only the neutral has to be the same size.
That's exactly why I cannot rewire.ChrisOlson wrote: »I think the microwave pulls 12 amps and it showed L1 at 7.8 and L2 (the leg the microwave is on) at 9.8. That's a 20% imbalance.
That's not too bad if you look at it in A instead of %. That's only 2A difference. Much better than 3 on L1 and 15 on L2!ChrisOlson wrote: »But if I run an extension cord from the microwave to one of the outlets that's on that 120V panel L1 and L2 from the inverter will stay perfectly balanced.
You can try to put the microwave's breaker on the opposite leg inside the same panel and see what happens.ChrisOlson wrote: »It would take a whole lot of investigating to figure that out.
I think one of the possible reasons is XW measurement errors. I found that some of its measurements are not very accurate. 2A may be well within the error. -
Re: Schneider Conext XW and GenSupp PlusYou can try to put the microwave's breaker on the opposite leg inside the same panel and see what happens.
Already did that and then it imbalances the other way a slight amount.
I think the difference between our split phase panel and the 120V panel is that the neutral return current from the 120V panel has to go thru the transformer and it forces L2 to assist L1. From the split phase panel the path of least resistance for the neutral is directly back to the inverter.
I had my AC clamp-on meter on L1 and L2 in the XW Conduit Box when we put the inverter in, and compared it to the SCP readings. The SCP was within a half amp at light loads and 1 amp at 7,200 watts. So there's some measurement error there, but it's not drastic. I've also compared the AC clamp-on meter readings to the AC2 readings in the SCP and found about the same amount of error - which is basically nothing.
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »I think the difference between our split phase panel and the 120V panel is that the neutral return current from the 120V panel has to go thru the transformer and it forces L2 to assist L1. From the split phase panel the path of least resistance for the neutral is directly back to the inverter.
Different wire resistances along different paths may create voltage differences which are translated into current differences by the transformer. Most likely that's what you see. If so, higher currents will produce more imbalance.
But I don't think it's bad. 2A difference is rather a good result. Perhaps not perfect, but good. -
Exactly. I think it would help your charging situation, to keep the generator loaded better. I don't know what size wire you used on your runs but we got #4 THHN from the inverter to the panels, including the neutral. Although the ground is #8.
Chris -
You know, I woke up with another wild hair idea this morning. I'm going to put the transformer on the Load Center panel itself in split-phase to split-phase balancing configuration and see what that does. That will eliminate the neutrals back to the disconnect. You get into this mind set that the transformer has to be by the power source, and it doesn't. It can be installed anywhere you want to balance a split-phase load with it
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »Exactly. I think it would help your charging situation, to keep the generator loaded better. I don't know what size wire you used on your runs but we got #4 THHN from the inverter to the panels, including the neutral. Although the ground is #8.
I had everything wired with #3, but when I came to connect it to XW, I saw a big sign inside saying #6 max, so I re-wired with #6.ChrisOlson wrote: »You know, I woke up with another wild hair idea this morning. I'm going to put the transformer on the Load Center panel itself in split-phase to split-phase balancing configuration and see what that does. That will eliminate the neutrals back to the disconnect. You get into this mind set that the transformer has to be by the power source, and it doesn't. It can be installed anywhere you want to balance a split-phase load with it
This might work even better. Also, it may be a good idea to make hot wires between the transformer and inverter of the same length. -
Yeah, I saw that sign about #6 too. But #4 will fit in the hole
I rewired that transformer on the Load Center panel this morning. I don't believe it, but it works! With a highly imbalanced load I see 1.5 - 1.8 amps difference. But with normal loads in a properly balanced panel (without the transformer), it maintains almost perfect balance.
It was the neutral from the Load Center to the Main Disconnect/Inverter that was causing it. With the transformer directly on the Load Center panel, neutral current can get to the transformer so it can balance instead of returning on the path of least resistance back to the inverter.
Learn something new every day.
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »Yeah, I saw that sign about #6 too. But #4 will fit in the hole
#3 fits into the hole too, but it feels too stiff for the connector. I thougt that they probably had put that sign up because many people broke away terminals trying to put in too thick a wire. So, I decided not to try too hard and changed to #6.ChrisOlson wrote: »Learn something new every day.
Thank you Chris for all that testing. Now I know that it works well and how to connect it. It's now time for me to think if I need to install it or not.
I'm going to say that whether or not you need a balancing transformer depends on how hard you intend to push the inverter and charger. If you want the max from it you'll be putting a transformer on it. That's one of the inherent issues with split-phase power, and one we never had to deal with when we had the SW Plus inverters because when you use the transformer in step-up for 120 -> 240V everything is inherently balanced.
I was pleased to see that GenSupp Plus does a reasonable job of balancing the generator IF you're using Gen Support AND you have a smaller than 5 kW generator. But OTOH, the PSX-240 is incredibly efficient - it's idle power consumption is less than 10 watts (at least I can't measure it with my Fluke meter that has 0.1 amp resolution because it stays right on a big fat zero). I have pushed that PSX-240 right to it's raw limits in step-up mode with the SW Plus and generator support and I have never had it even get warm to the touch or start the cooling fan in it. So IMHO, worrying about "losses" by using the transformer is about as useful as worrying about driving up hills with your car is going to hurt the gas mileage.
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »I'm going to say that whether or not you need a balancing transformer depends on how hard you intend to push the inverter and charger. If you want the max from it you'll be putting a transformer on it. That's one of the inherent issues with split-phase power, and one we never had to deal with when we had the SW Plus inverters because when you use the transformer in step-up for 120 -> 240V everything is inherently balanced.
I'm not worrying about losses that much. 1.5% is very little, and then there's no loss at all when the loads are already balanced. I generally like how everything's working now. My concern is that a single-sided load causes XW to slow down charging. That is not because I want to push it to the limit, but because XW charging becomes less stable when it does that, and generator doesn't run even any more, but starts to oscillate between 59 and 61Hz. My understanding that it is better for the generator to run steady. It may also have bad effect on appliances too.
My wife says that this is not a problem because we can avoid using loads while generator is running. That certainly would solve the problem.
Another thought is that may be pushing the generator that much is not such a good idea. May be it will live longer if I limit the charging load to, say, 70A, even if it means more working hours. -
Re: Schneider Conext XW and GenSupp PlusMy wife says that this is not a problem because we can avoid using loads while generator is running. That certainly would solve the problem.
How can your wife do that? My wife, I'm pretty sure, dreams at night about coming up with new methods to load test equipment
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »How can your wife do that? My wife, I'm pretty sure, dreams at night about coming up with new methods to load test equipment
I have my doubts too
Just for giggles I made a little video demonstrating the difference in the noise the inverter makes with and without the transformer on it.
[video=youtube_share;BC_KZRM__ZI]
http://youtu.be/BC_KZRM__ZI[/video]
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »Just for giggles I made a little video demonstrating the difference in the noise the inverter makes with and without the transformer on it.
Thanks Chris. That noise that it makes without transformer. Mine sounds exactly like this. -
Yeah - load the inverter to 6-7 kW and then it sounds like a 125 kVA 480/277 utility transformer, even with the auto transformer. But the higher the loads go on it, the more chance you have of a leg imbalance causing an issue. If you're pushing it to 5.5 kW load, as an example, and then your wife throws something in the microwave and turns that on, adding the additional 12 amps load on one leg causes it to get REALLY loud. But with the transformer on it it handles the overload with ease and runs quieter.
After experimenting with it, and trying to overload the inverter just to see how much it will take (without successfully getting it to shut down from overload) I firmly believe that using the auto transformer is a win-win.
Chris -
Re: Schneider Conext XW and GenSupp PlusCould you explain more on that. In the XW there's a "Breaker size" setting for AC2. If the (charging current + load) on any leg approaches 80% of that, XW dials down the charhing and, in case of a small generator, may drop it completely.
Again, in response to NorthGuy -
Kind of an old thread now. But I have tried to duplicate this issue that I believe you said was sometimes caused by your garage door opener? If I understand correctly, you said the inverter would be charging batteries and if you operated the opener it would cause the XW to drop your charging instantly?
I have not been able to duplicate this here. We don't have a garage door opener. But this is one thing I tried:
The AGS started the generator for Load Amps due to 6.85 kW load on the inverter. Of course, it shuts the gen off if the load drops below the Stop Load setting for one minute. One of the loads shut off and it had enough extra from the generator to start charging batteries a bit while it waited for the loads to drop below the Stop Load setting. I watched it for a bit and a second load shut off, causing loads to drop below the Stop Load and it dialed the charger up to 27 amps.
I had my air compressor in the shop turned on (17 amps @ 120V), but the Main breaker in the distribution panel shut off so there was no power to the shop. I turned that breaker on, which is right by the inverter where I could watch it. I don't know what the surge load on that 2.5 hp air compressor, but it's pretty substantial. It made the generator grunt when I turned it on but it didn't drop the charger - it just cut the charger back to about 5-7 amps.
I turned the breakers off to the auto transformer and tried it. Then it dropped the charger and since the gen was overloaded on one leg by the air compressor it immediately switched to Gen Support.
At no time did it ever unload the generator and let it free-run with both tests. The generator stayed at rated output on the first test (with the transformer) despite everything I did to it, at all times. On the second test the generator output dropped to about 75% rated load (due to overload on one leg and the inverter supporting back to rated load) and the other leg at only about 50% rated load - with no charging power going to the bank.
But either way the XW was smooth as silk in how it handled the charger to keep the generator within its limits. I think the only difference between my setup and yours is that I'm using Gen Support and you're not.
So here's something you could try to see if it prevents this; our generator will actually put out 31 amps on surge (7 kVA with a voltage drop to 228V and freq drop to 56 Hz) for about 2 seconds. I have tweaked my AC2 Breaker Size up to 40 amps, then set Gen Support to 15 amps (3.6 kVA - max continuous output). You could try setting your AC2 Breaker Size up a bit so the inverter thinks the generator is bigger than it really is (so it will let the generator deliver surge for motor starting without going into "panic" due to hitting the AC2 "hard" limit). Then enable Gen Support and set the Support Amps to what the generator can deliver continuous and keep the freq at or near 60 Hz (should be around 4.8 kVA for your NG fueled 8 kW Guardian, or 20 amps).
If you want to run the freq lower than 60 (REALLY bad for sensitive electronics and digital clocks) you can push it harder than 20 amps on the Support Amps setting, if you want. The reason I mention that is because when you enable Gen Support, during battery charging it will limit how much current the charger can use based on the Support Amps setting - it won't let it go over that setting for obvious reasons.
I don't know if you're up to trying that, but it would prove or disprove my theory that using the Gen Support helps the whole thing work smoother.
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »Kind of an old thread now. But I have tried to duplicate this issue that I believe you said was sometimes caused by your garage door opener? If I understand correctly, you said the inverter would be charging batteries and if you operated the opener it would cause the XW to drop your charging instantly?
It was like this:
-XW is charging at 100A. With loads it's close to 30A on both legs.
-Motor starts (garage door opener is close to test), putting up a surge. I don't think it's a bad one.
-XW quickly decreases charging load to 20-30A (sort of panic mode?)
-Generator speeds up too much
-XW drops it (I guess for speeding)ChrisOlson wrote: »I have tweaked my AC2 Breaker Size up to 40 amps, then set Gen Support to 15 amps (3.6 kVA - max continuous output). You could try setting your AC2 Breaker Size up a bit so the inverter thinks the generator is bigger than it really is (so it will let the generator deliver surge for motor starting without going into "panic" due to hitting the AC2 "hard" limit).
At first, I hoped that the breaker size would keep the generator under 7.5kW and had set it to 38A. Then I ended up setting the breaker size much higer. Practically disabled the protection. Without protection it does work. Generator can take short surges and XW doesn't interfere. However, XW will not dial back charging in case of overload, so it is possible to overload the generator. I would definitely use protection if it worked better.
XW is actually programmed to slow down chargig when generator voltage drops down, so it might prevent overload, but I didn't try to overload it on purpose. -
Re: Schneider Conext XW and GenSupp Plus-XW quickly decreases charging load to 20-30A (sort of panic mode?)
No, that seems normal in my testing. It instantly adjusts the charger amps during a surge load to help the generator out so it can handle the surge better. If the surge is real big it can momentarily stop charging, but it brings the charger right back once it determines what the constant load is (at least that's what it does here).-XW drops it (I guess for speeding)
Yep - the governor on the generator doesn't react fast enough and it goes over-freq.Generator can take short surges and XW doesn't interfere. However, XW will not dial back charging in case of overload, so it is possible to overload the generator.
This is what I was talking about - if you enable Gen Support then the XW DOES dial the charger back even with the inflated AC2 Breaker Size setting. It adjusts the amps to the charger to about one amp below what you have the Gen Support amps set at. And in addition, if you try to overload the generator (by adding loads) it cuts the charger back until the loads exceed what the generator can put out, then switches to GenSupport mode and assists the generator and prevents the overload.
I've found it virtually impossible to overload our generator, no matter what I throw at it, with Gen Support enabled and properly set - even with the AC2 Breaker size set to 40 amps, which is double the size of the actual circuit breaker on the generator.
Chris -
Re: Schneider Conext XW and GenSupp PlusChrisOlson wrote: »Yep - the governor on the generator doesn't react fast enough and it goes over-freq.
Yes, if you remove 6kW at once it cannot keep up. For some reason, it can take load increases (e.g. surges) much better.ChrisOlson wrote: »This is what I was talking about - if you enable Gen Support then the XW DOES dial the charger back even with the inflated AC2 Breaker Size setting. It adjusts the amps to the charger to about one amp below what you have the Gen Support amps set at.
I should try various settings for Gen Support. May be it'll work better than AC2 breaker size.
How does Gen Support handle unbalanced loads? Does it watch for the highest of the legs (as AC breaker size does), or for the average of the legs? -
Re: Schneider Conext XW and GenSupp PlusHow does Gen Support handle unbalanced loads?
It starts supporting the generator based on the highest loaded leg.
Chris -
But unless you have two 120 volt inverters or a balancing transformer, the support current it provides will go equally to both legs of 240, yes?ChrisOlson wrote: »It starts supporting the generator based on the highest loaded leg.
Chris
Which would reduce the total load on the generator, as well as the load on each leg from the generator, but might actually increase the imbalance ratio.SMA SB 3000, old BP panels. -
Re: Schneider Conext XW and GenSupp PlusBut unless you have two 120 volt inverters or a balancing transformer, the support current it provides will go equally to both legs of 240, yes?
Using the auto transformer makes the thing perform better under imbalance between the legs. I have determined that without even a shadow of doubt.
What is does without the transformer; say you have Gen Support set at 20 amps. You have a 25 amp load on L1 and a 15 amp load on L2. The inverter will let the generator carry the 15 amp load on L2 and it will reduce the load to the generator on L1 to 20 amps. The inverter will supply the 5 amps on L1 required to meet the load.
If you use GenSupp Plus the inverter hooks its transformer center tap to the gen neutral and it balances the generator a little more, and the inverter makes up the remainder to the load on both legs instead of just one.
So basically it attempts to leg balance the generator as much as is feasible and the inverter handles an imbalance to meet the remainder of the load.
In the same situation with an auto transformer, it will not even go into Gen Support because the transformer causes the inverter (and generator) to "see" a balanced load of 20 amps on both legs.
Despite how some folks like to complain about the XW, it is after all a split phase inverter and therefore it has to deal with the problems inherent in split phase power systems. And frankly, split phase power is a huge kludge. The European 230V three-wire system is MUCH better. So, putting the XW thru its paces, I find it hard to fault it in how it handles things. Coming from the world of generators myself, the XW6048 is WAY more capable than a 5.7 kVA split phase generator is - so much more capable that it would take at least a 10 kVA generator to match what the XW can do with split phase imbalances.
People get used to things "Just Working" on utility power with a split phase system. But utility transformers have a virtually unlimited power source behind them so they can handle these things without a problem. But inverters and generators do not have unlimited power behind them and when you start dealing with split phase imbalances you are regularly overloading one side of the system. It's the nature of the beast.
Chris -
Chris, thanks for all the work. I have my first SW 3024 ordered and on the way it is essentially half of the XW 6048 with 120 V output. The goal is to get it to run on a Honda EU 2000 with the same success you have had. It looks like the ACin, Generator Support amps, and charger % is about all you have to work with. The trick for me is if it will be able to pull the Honda EU 2000 to pull in and out of the ECO throttle without overwhelming it. It's sounding like that it will end up being like North's, where the generator won't be able to react to the changes fast enough, I had those same issues with the Magnum, The OutBack has not been field tested yet. Interesting to fool with, if the programmers would do a little ramping of the demands instead of slamming things on and off like a switch.
Two summer's I leased a boat to Holly Carburetor to do their first Fuel Injection for a Marine Environment. They had a " Bread Board " with at least 200 trimmers on it. They would come day after day, tweeking and adjusting every perimeter. Eventually they got it down to the chip level and used laptops for their adjustments. It was interesting to chat with them and see all that goes into R&D to deliver a product that works the same way the users do.
It will be interesting to hear about the SW. At least with the XW I would not use a generator with ECO Throttle with heavy loads. When the XW calls for surge from the generator it wants it right now - and the gen had better be able to deliver right now or it will tell it take a hike and come back when it grows some hair on its chest.
Chris -
May just have to scrap using the ECO mode, it's nice for certain loads, but does have limitations. I might try to remote the on/off switch for it.ChrisOlson wrote: »It will be interesting to hear about the SW. At least with the XW I would not use a generator with ECO Throttle with heavy loads. When the XW calls for surge from the generator it wants it right now - and the gen had better be able to deliver right now or it will tell it take a hike and come back when it grows some hair on its chest.
Chris
I am already concerned about this. One to two seconds is a lifetime.
"The Freedom SW supports the generator (or other power source) when the
AC load current drawn from the generator exceeds the GenSup Amps
setting for 1 to 2 seconds.
The system can enter this state if the battery voltage is above Low Battery
CutOut (LBCO) plus 1 volt and generator support is enabled." -
Re: Schneider Conext XW and GenSupp PlusBlackcherry04 wrote: »I am already concerned about this. One to two seconds is a lifetime.
Yep. The SW Plus and the XW are the same way. That generator had better be able to deliver the surge (our Honda EM-SX can do it for 10 seconds) and maintain voltage and freq in spec. Can't use a pansy generator on an inverter with Gen Support if you want to push the generator to full load. You can always set the Gen Support amps down to compensate for a week-kneed generator. But then it won't run at full load.
Chris