I recently installed a Trimetric 2025 in my rv and it seams to work fine. I then installed the Xantrex prowatt 600. It seams to work fine also but when I put a load on the inverter it does not show as a load in the Trimetric. The Trimetric shows other dc voltage loads but not the inverter. Any ideas? Thanks
Comments
-
Re: Xantrex Prowatt 600
The only explanation is that the inverter has been wired to the wrong side of the Trimetric's shunt so that current flowing to it is not measured. -
Re: Xantrex Prowatt 600
Well I have the negative cable from the inverter connected to the negative terminal on the battery and positive inverter cable thru an 80 amp breaker to the positive battery terminal. I then have a negative cable to the shunt with the one small wire to Trimetric. The other side of the shunt goes to a rv chassi ground. Maybe I have the wires from the trimetric switched on the shunt. I'll keep working on it. Thanks. -
Re: Xantrex Prowatt 600
All the current from (to) the negative MUST go through the shunt for it to work properly
like Batt>>> shunt>>> Inverter
..........................>>>> charger etc
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Xantrex Prowatt 600ironbridge wrote: »Well I have the negative cable from the inverter connected to the negative terminal on the battery and positive inverter cable thru an 80 amp breaker to the positive battery terminal. I then have a negative cable to the shunt with the one small wire to Trimetric. The other side of the shunt goes to a rv chassi ground. Maybe I have the wires from the trimetric switched on the shunt. I'll keep working on it. Thanks.
That sounds like the inverter connects directly to the battery, thus bypassing the shunt.
The only wire connecting to the battery negative should be from the shunt. Everything else goes on the other shunt terminal (except the Trimetric sense wires). -
Re: Xantrex Prowatt 600
I originally had the negative inverter wire going to the shunt side that comes from the negative battery terminal. I had the same result. So...should I put the negative wire to the chassi ground side of the shunt? Thanks -
Re: Xantrex Prowatt 600ironbridge wrote: »I originally had the negative inverter wire going to the shunt side that comes from the negative battery terminal. I had the same result. So...should I put the negative wire to the chassi ground side of the shunt? Thanks
That description is the same as putting the inverter negative on the battery post.
It should be like this:
Battery (-) --- SHUNT --- everything else (loads, charge sources, chassis ground).
This is the only way the Trimetric can 'see' all the current going in or out of the battery. -
Re: Xantrex Prowatt 600
Ok thanks a lot. I'll switch it tomorrow after work. Thanks for the help.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed