Re: AGS settings for Outback FM60
The "bottom end" of a 24 Volt system is 21 Volts. 23 to 24 is still going to be okay. You've drained them deeply, but as Bill said not "dead". I have my low Voltage disconnect set at 24 for this reason: 24 Volts under load is most assuredly above 50% SOC.
Float is typically 1 Volt less than Absorb on a 24 Volt system (if you've no other guidelines to go by). -
Re: AGS settings for Outback FM60
Great.
One battery string disconnected so I can test its' voltages later. Sure was nice to see absorbtion on the one bank even though its solid cloud! More panels for the two strings, right?
Same plan? Use single bank for a while with max. absorb times, see how its capacity holds up and maybe in a week EQ it?
Then once its in good shape, work on the other and if the two strings are close in voltage (within 0.?V) parallel them back together? -
Re: AGS settings for Outback FM60
Basic formula for getting the right amount of panels for a battery bank: 10% of the Amp hour capacity for peak potential charge current. In other words, for every 100 Amp hours (at whatever Voltage) of battery you try for 10 Amps of current (at the system nominal Voltage). This isn't an absolute and it is not necessary to see that Voltage every charge period, it's simply a short cut to having enough panel. Coupled with 25% DOD and the right Absorb time length (as you've learned the hard way) you get a balanced system that will work right about 90% of the time. Caveat: there are always exceptions.
By charging half your battery bank at a time you can put a greater percentile of current to it, bringing it up faster which allows for more time spent in Absorb. Just don't leave those other batteries off charge for too long or they will get worse.
What you're looking for is a resting Voltage that is both high enough and lasts long enough (like overnight) to indicate the battery is actually fully charged. -
Re: AGS settings for Outback FM60
Checking rest voltage on the disconnected bank of batteries after 3 hrs, this is what they say: 6.27, 6.25, 6.31, 6.29 with the specs saying 6.40 as fully charged that's 97-98% charged. Doesn't seem too bad? -
Re: AGS settings for Outback FM60Checking rest voltage on the disconnected bank of batteries after 3 hrs, this is what they say: 6.27, 6.25, 6.31, 6.29 with the specs saying 6.40 as fully charged that's 97-98% charged. Doesn't seem too bad?
-
Re: AGS settings for Outback FM60
From an earlier post I made here:A 48 Volt Bank at resting voltage at 77F is around 45% state of charge (see generic bank voltage chart from Battery FAQ--12.00 volts).
However, the actual resting voltage is really dependent on the initial specific gravity of the electrolyte fill...
So, what was your "full charge" Specific Gravity?
One thread here
Another thread here
So, to pull from earlier posts:
Well mixed electrolyte is important--so if you notice all cells not coming back to "full charge" level of s.g., then there is a good chance that "mixing" (equalization) will bring the s.g. back up to your logged readings (keep these as your "good batteries" / "fully equalized" numbers.
The amount of variation you are seeing is not that great (less than 0.030 between all cells). And having "high" s.g. is not always a good thing either.
I ran across this page on why different types of batteries have different starting s.g. fills... Is pretty interesting:Specific Gravity vs Applications
1.285 Heavily cycled batteries such as for forklifts (traction).
1.260 Automotive (SLI)
1.250 UPS – Standby with high momentary discharge current requirement.
1.215 Geral applications such as power utility and telephone.
As mentioned earlier, the specific gravity (spgr.) of a fully charged industrial battery, or traction battery, is generally 1.285, depending on the manufacturer and type. Some manufacturers use specific gravities as high as 1.320 in an attempt to gain additional Ah capacity, but at the cost of a shorter cycle life.
...
Higher Gravity = vs Lower Gravity =
More capacity / Less capacity
Shorter life / Longer life
Higher momentary discharge rates / Lower momentary discharge rates
Less adaptable to "floating: operation / More adaptable to "floating" operation
More standing loss / Less standing lossSpecific gravity = single-cell open-circuit voltage - 0.845 (example: 2.13v – 0.845 = 1.285)
Or
Single-cell open circuit voltage = specific gravity + 0.845.
So, if you are getting 46 volts after resting, if the formula is correct (and your battery is around 77F) your specific gravity should be:- 46v/24cells - 0.845 = 1.072 (dead?)
- 47v/24cells - 0.845 = 1.113 (~20% state of charge)
- specific gravity changes by +.001 for every -3 degrees Fahrenheit.
By the way, do you have a Battery Monitor?
-Bill
If you look at the (simplified) equation for voltage vs specific gravity--The difference in state of charge is a simple difference in voltage or specific gravity (offset by a constant).
So, in your case the high-low voltage gives you a difference of 0.060 volts or a difference of 0.060 sg units.
From what I have read, a couple battery vendors (flooded cell) recommend equalization if the SG is different from low to high cell by more than 0.015 to 0.030 SG units (sg is a ratio--so it is really unit-less).
To be honest, I have never looked at SG of a sealed battery in quite that way before--But, it would appear that if you can do a slow charge (around 2.5% to 5% maximum?) rate of charge at a "slightly" elevated Absorb voltage (or at least hold absorb voltage for hours)--And see if you can bring the cells up to a stable "full charge" (full charge for a flooded cell is 2.5 to 5% current flow and SG not changing between readings taken 30-60 minutes apart)...
It probably would be best to charge cells "singly" at 2.4 volt each--But not many people have 2.4 volt (relatively) high current chargers floating around (i.e., around 1-5 amp charger per 100 AH cell).
Remember you are over charging the series cells that are already at 100% SOC so you can "leak" current to recharge any weak cells back to 100% too. So you don't want too much current through the "good cells" to cause them to overheat and vent--thereby creating a whole battery bank of bad cells.
Anyway--more of a point of discussion here--Not claiming this is the "answer".
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: AGS settings for Outback FM60
OK. Lifeline has a suggested capacity test - basically discharging with a 25A load and timing it, then checking the numbers. I am not able to do that down here, or know of a company that can so that is another reason I'm relying on all you gurus for the great advice. How long can I leave the disconnected bank without charging?
I'm thinking I'll need at least ten days to work on the connected bank before moving to the other one - is that acceptable? -
Re: AGS settings for Outback FM60
Quick fix is to disconnect bank 2, charge bank 1 all the way to float, then reverse and charge second bank2, so that you get both as 'full' ( a relative term right now)as possible. Then proceed with your corrective charging program.
I think that iis the best you could do in this circumstance.
Note that you should do a daily V check on both banks to be sure bank 1 is improving and that bank2 is stable. If B2 starts to drop, give it a boost or full charge if possible.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: AGS settings for Outback FM60
Maybe I'm getting confused (wait 'til you're old, children ) but I thought we were talking AGM's here. If so, exposed plates is probably not an issue (although sulphation still can be).
How long you can leave batteries without charging depends a lot on how charged they are to begin with. More than 75% is pretty safe. Fortunately AGM's have a very low self-discharge rate. -
Re: AGS settings for Outback FM60OK. Lifeline has a suggested capacity test - basically discharging with a 25A load and timing it, then checking the numbers. I am not able to do that down here, or know of a company that can so that is another reason I'm relying on all you gurus for the great advice. How long can I leave the disconnected bank without charging?
I'm thinking I'll need at least ten days to work on the connected bank before moving to the other one - is that acceptable?
Again, I use my overnight Load as the test, If all of a sudden I am @ 24.2 instead of 24.4 in the morning and the Amp's consumed are the same and charging and Loads were the same, I'v lost capacity.
On the batteries you have pulled, just check the voltage on them every couple days. -
Re: AGS settings for Outback FM60Cariboocoot wrote: »Maybe I'm getting confused (wait 'til you're old, children ) but I thought we were talking AGM's here. If so, exposed plates is probably not an issue (although sulphation still can be).
How long you can leave batteries without charging depends a lot on how charged they are to begin with. More than 75% is pretty safe. Fortunately AGM's have a very low self-discharge rate. -
Re: AGS settings for Outback FM60
Sounds good.
Thanx again everybody.
If you're interested, I'll let you know how things work out? -
Re: AGS settings for Outback FM60Blackcherry04 wrote: »Exposed to the Electrolyte !!!! If a Plate is Sulfated, it is NOT exposed to the electrolyte, The Coating Sulfate is Blocking it.
Yeah, I knew I was probably getting confused.
It's been a rough year!
Uh-oh ... this is only the first day! -
Re: AGS settings for Outback FM60
Sure--Finding out how things work out is important for everyone that follows. We like to know that we are giving good advice--Or how to give better in the future.
And--You can make your own 25 amp load pretty easily... Use your inverter plus a heater or standard (if you can find them) high wattage filament light bulbs:
25 amps * 24 volts * 0.85 typical inverter efficiency = ~510 watt AC load
Get an inexpensive electric heater run on load (may be around 500 watts) plus a 100 watt light bulb--And there you go.
Concord says their batteries should supply 80% of rated capacity--less than that is a "failed battery".
Practically speaking--Say you plan on running your system to a maximum of 50% discharge (25% discharge for two day without sun)... If the batteries still have charge at the end of your test to 50% discharge--then the bank is "still good for your use". If the battery bank collapses--It no longer meets your needs.
Note--It is very possible you have a mix of "good" and "bad" batteries--Doing the testing will allow you to find the failed battery(ies)--You can replace them, run a reduced bank, or even try some charge/discharge cycles and see if you can "recover" the failed battery
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: AGS settings for Outback FM60
OK.
So as I'm slowly "reconditioning" each bank, monitoring capacity (whicg I think maybe getting better already as it was at 24.6 this morning and has been lower of late) - I'll be looking for a battery (or more) that simply refuse to come up to par?
As for the capacity testing - I have to do rgw whole bank though as I need 24V for my inverter. I would have thought that individual batteries should be tested for proving? -
Re: AGS settings for Outback FM60
Testing the whole bank and monitoring the voltage on each battery (with a meter) would probably be "good enough"... The first battery that drops below ~12 or 11.5 volts is your weakest.
You can test each battery--But then you would need to recharge each one separately (you don't want to mix charged/discharged batteries in the same series string).
Depends on your needs (your only place to do work, or do you have a shop/2nd home else where with grid power where you can take time/energy to test each battery)... You could do the single battery testing at your off grid location if you have parallel battery strings (take out one string and test the batteries separately). Just depends on what works best for you.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: AGS settings for Outback FM60
The only cautionary note that I'd add, is to monitor the bank voltage very carefully during this type of discharge testing. AND, monitor the voltage of every battery often, as BB Bill was indicating. Even weak batteries might be recoverable if they are not run down too far.
VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Re: AGS settings for Outback FM60
Yea--You don't want to kill a battery just because of testing for bad batteries.
-Bill "self fulfilling prophecy" B.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: AGS settings for Outback FM60
I don't feel comfortable discharging batteries at this moment as that is what I'm trying to amend! I charged this string up to 28.6V this morning with the generator (2 hrs) and it's been held at that with my CC's all day so this gives me confidence that I can hold a string at a higher voltage to de-sulfate them (eventually). So, same plan mañana as well as a first dose of 31V EQ for an hour, probably mid day after they've been held with the sun at 28.6V -
Re: AGS settings for Outback FM60
not so fast pilgrim... lets see what voltage we get down to in the morning after a nights use...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: AGS settings for Outback FM60
And cycle them as normal at night (probably at least 25% to ~75% state of charge, at least)--Discharging/Charging is going to be helpful in recovering capacity (if needed/possible).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: AGS settings for Outback FM60... so this gives me confidence that I can hold a string at a higher voltage to de-sulfate them (eventually).
There are two forms of the lead sulphate on the plates. The first is the "soft" or spongy form, which is initially created during periods of low SOC. It can be forced back into solution as Lead and sulphuric acid by proper charging. The second is "hard" or crystalized lead sulphate, to which the initial deposits eventually change if left undisturbed. These *cannot* be reclaimed by simple application of a charging or even equalizing voltage because the energy required to break them up is higher than the point at which all of the current is going to electrolyze water instead.
By all means be patient, but be aware that really badly abused batteries cannot recover completely through charging.SMA SB 3000, old BP panels. -
Re: AGS settings for Outback FM60
OK bosses! Will do, hold em at 28.6V all day for a few days more and check things out. Sorry - getting ahead a little.... -
Re: AGS settings for Outback FM60
Ah yes, the young Jedi learns patience...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: AGS settings for Outback FM60
One thing I don't think I asked/clarified:
Old school (flooded lead acid batteries) told you they were bad when their voltage was low (24.6V) and would almost immediately increase to Absorb ~ 28+V when connected to an external charger ie a generator. Correct? Even though the newer AGM's are touted as faster recharge - are they meant to act this way too, or is it a similar situation?
Maybe this is a stupid question - I'm just trying to get my head around all this info that's been posted - young Jedis' brain sponge can get sulfated too!! -
Re: AGS settings for Outback FM60One thing I don't think I asked/clarified:
Old school (flooded lead acid batteries) told you they were bad when their voltage was low (24.6V) and would almost immediately increase to Absorb ~ 28+V when connected to an external charger ie a generator. Correct? Even though the newer AGM's are touted as faster recharge - are they meant to act this way too, or is it a similar situation?
Maybe this is a stupid question - I'm just trying to get my head around all this info that's been posted - young Jedis' brain sponge can get sulfated too!! -
Re: AGS settings for Outback FM60One thing I don't think I asked/clarified:
Old school (flooded lead acid batteries) told you they were bad when their voltage was low (24.6V) and would almost immediately increase to Absorb ~ 28+V when connected to an external charger ie a generator. Correct? Even though the newer AGM's are touted as faster recharge - are they meant to act this way too, or is it a similar situation?
Maybe this is a stupid question - I'm just trying to get my head around all this info that's been posted - young Jedis' brain sponge can get sulfated too!!
Not sure I understand this question.
FLA's and AGM's behave much the same for charging. How fast they come up to Absorb depends on how deeply they are discharged, the capacity of the battery, and how much current is put to them.
It is even possible to charge them too fast.
Some charge controllers (such as Outback) have a minimum Absorb time setting as well, because under certain conditions the Bulk stage can be too short to "run up enough time on the Absorb clock". Thus you could have "at least 1 hour Absorb" and "at most 4 hours Absorb" and "End Amps".
People tend to miss the point of how important the length of the Absorb stage is. -
Re: AGS settings for Outback FM60
I am presently working on one string of 6V 400AH Lifeline AGM's configured to 24V.
The morning low battery light is on and reads 24.6V
My generator is wired through the FX charger which if I rmember correctly limits current to 20A?
Anyway, on firing up the genny, I watched the voltage readout go up fairly fast (a few minutes) from 24.6 to absorb voltage of 28.6V
Maybe I should have mentioned this a while back - I thought it was one of the advantages of AGM's as they charge faster - but it really seems like they are acting just like flooded lead acids - gone bad.
This would also happen when I had the two strings wired up, albeit a little slower. -
Re: AGS settings for Outback FM60I am presently working on one string of 6V 400AH Lifeline AGM's configured to 24V.
The morning low battery light is on and reads 24.6V
My generator is wired through the FX charger which if I rmember correctly limits current to 20A?
Anyway, on firing up the genny, I watched the voltage readout go up fairly fast (a few minutes) from 24.6 to absorb voltage of 28.6V
Maybe I should have mentioned this a while back - I thought it was one of the advantages of AGM's as they charge faster - but it really seems like they are acting just like flooded lead acids - gone bad.
This would also happen when I had the two strings wired up, albeit a little slower.
Where were you reading this voltage ?? at the battery bank ? it's not odd for there to be a volt difference between the battery voltage and a meter . -
Re: AGS settings for Outback FM60
AGM can charge faster because they can accept more current than flooded cell during bulk stage, without over heating (when the battery can accept more current than the charge controller can output--charge controller is current limited).
Once the batteries are over ~80-90% state of charge, both will hit the absorb voltage, and the current will slowly tapper down to near 1-2% final charging current.
Of course, if the AGM has begun to sulfate, and the battery bank voltage begins to rise "too quickly"--Then its ability to accept high current will be compromised (and it storage capacity too).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed