Magnum MS4024PAE vs. MS4448PAE
Wxboy
Wxboy Solar Expert Posts: 70 ✭✭✭✭
My father currently uses on old Trace modified sine wave inverter/charger as night time battery backup during power outages and run the generator during the day. He is looking to buy a new PSW inverter/charger that can run 120 and 240 so he's looking at the 2 Magnums in the subject line. He knows the advantages of the 48 volt unit(lower amp draw based on the higher voltage and a little more rated power) but he asked if there were any disadvantages. They are the same price so I was pushing him toward the 48 volt. Please let me know what you think.
Currently he has 6 12 volt batteries set up on 2 battery switches so he can charge in banks of 2 and then when he draws power at night he can switch to all 6 if he needs to. He bought the batteries 2 at a time so they are slightly different ages and he grouped them together by age. They are deep cycle agm batteries, 100 amp hour. I told him one small disadvantage to the 48v is that he would only be able to hook up 4 of his batteries or buy 2 more and have 2 banks of 4. He realizes using batteries of different ages is not ideal but this is just for backup power so none of the batteries have been cycled more than a few times.
Thanks in advance for your feedback.
    BB. Super Moderators, Administrators Posts: 33,734 admin
    Re: Magnum MS4024PAE vs. MS4448PAE
    Does he need 24 VDC for anything (there are more 24 volt small water pumps, lights, and appliances--such as for long haul trucks/boating--Than for 48 volt systems).
    I don't like parallel battery banks--So keeping the paralleled battery strings to 2-3 maximum is my personal choice. There should be a fuse/breaker per string for safety.
    Look at generator to battery bank charging capacity (5% to 13% typical range, ~25% recommended maximum charging current--Although AGM will take more current than flooded cell). I like to have the minimum size generator needed to keep fuel efficiency high (and fuel costs low, and minimum storage/having to hunt for fuel in a power emergency)--I believe the Magnum inverters are programmable for maximum AC power rating of AC power source (generator, feed from grid). Make sure you get the "right" remote meter (there is a basic and advanced type meter--Not sure if the basic can program all the needed software settings or not, need to adjust charging voltage/float/no equalization voltage for AGM).
    Some other options to think about--The remote battery temperatures sensor option (not sure if RBTS comes with inverter or extra cost option). And a Battery Monitor (especially helpful for AGM which you cannot measure specific gravity because they are sealed). Magnum does have its own battery monitoring system (and other products)--Not sure if it is same better/worse than a stand alone Monitor.
    Otherwise--4kW inverter is pretty good sized--Does he need that much power? And what AH is/will be the battery bank?
    If he ever plans on adding solar, there are various pre-wired "E-Panels" to make things a bit easier/cleaner.
  • Wxboy
    The generator is a Honda EU6500is which is a big brother to your EU2000i. He won't be running any 24 volt loads, just 120/240v. Battery bank will be either 400 amp hours or 800 if he buys 2 more batteries and goes with 2 parallel strings but I think he'll start with the 4 100 amp hour batteries since he has the generator to fall back on. I don't anticipate that he will go solar because his house has too many tall trees around it.
    Thanks for the tips on the meters and monitors and sensors, good to know.
    Sounds pretty well balanced... A 400 AH @ 48 volts is good for about a 4kW inverter/charger... 800 AH @ 48 volts would be good for up to an 8kW inverter/charger (and good for 8kW/16kW surge ratings).
    The 48 volt version has a 60 amp battery charger--Which would pull from the genset (maximum rating):
    • 60 amps * 59 volts charging * 1/0.95 power factor * 1/0.85 charger eff = 4,384 VA (good match for a 6.5kW genset)
    And a 60 Amp charger would be good for a rated battery bank of:
    • 60 amps * 1/0.05 rate of charge= 1,200 AH maximum battery bank
    • 60 amps * 1/0.10 rate of charge= 600 AH nominal battery bank
    • 60 amps * 1/0.13 rate of charge= 462 AH maximum "good practices" charging rate
    • 60 amps * 1/0.25 rate of charge= 240 AH maximum "don't exceed unless you have a very good reason" rate of charge
    The above numbers are recommended rules of thumb for Flooded Cell battery banks--AGM batteries have much higher current limits and much lower self discharge--But there is not really much reason for designing a "balanced" Off Grid / Backup up system for AGM only unless it has special needs (UPS systems are designed to drain an AGM battery bank in 15-30 minutes until the computers can be shutdown and/or backup fuel power generators are brought on-line).
    If he ever decides to go with solar--Having a "smaller" battery bank and a (by ratios) "larger" solar array (i.e., 10% to 13% rate of charge) can help keep costs down (smaller battery bank to replace every 3-6 years for AGM) and a smaller array (even a 400 AH 48 volt can take a pretty good sized array):
    • 400 AH * 59 volts charging * 1/0.77 panel+controller derating * 1/0.10 rate of charge = 3,065 Watt array "nominal"
    Tall trees can be a "temporary" situation... Our neighborhood lost many of its trees over the last 50 years--Roads are hard on tree roots and having 200 foot trees around homes on 50-100 foot lots means that cars and homes were being "bisected" every few years when a heavy wind/rain storm rolled through.
    If he has more land--Can he put the array within a several hundred foot radius of the home and get some good sun?
    Also, if he has grid and this is purely for emergency/backup power--He could drop to 5% rate of charge, be a bit conservative about power used during the day, and still have a reliable/solid system.
    Anyway--My 2 cents worth of advice.
  • mtdoc
    mtdoc Solar Expert Posts: 600 ✭✭
    Wxboy wrote: »
    Just a heads up: 4 100 AH 12 volt batteries will give you a 100 AH 48 V battery bank, not a 400 AH 48 V bank.
    Good Catch Mtdoc!
    Note to Wxboy--4 batteries in series for 48 volts, vs 2 in series/2 in parallel, vs 4 in parallel (assuming all 12 volt batteries)--Will all store the same amount of total energy... It is just moving from 24 volts to 48 volts with the same batteries--The voltage rating doubles, the AH rating 1/2's... And the total energy storage is still the same (and the current will be 1/2, allowing smaller wire/longer wire runs because of the higher battery bus voltage).
    Thank you,
    You might want to read through this about different system Voltages: http://forum.solar-electric.com/showthread.php?15989-Battery-System-Voltages-and-equivalent-power
  • Wxboy
    Actually I was just about to correct the amp hour rating after I read Bill's charge rate section of his post but I see everyone already figured it out. I know how it works but I just wasn't thinking when I typed it since I'm more used to my 12volt system.