battery connections
Thanks in advance
Michael
Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
Comments
-
Re: battery connections
Six parallel strings of two in series.
There's you problem: the chances of all six strings sharing current equally is about 'nil'.
You can see the different methods at this Smart Gauge site: http://www.smartgauge.co.uk/batt_con.html
Method #1 is always the wrong way to do it.
Method #2 works best when limited to two parallel strings.
Method #3 is the only choice for three parallel strings or more.
Method #4 really only works with four parallel strings.
In your case you substitute two 6 Volt batteries in series for each single battery shown.
But really you should go to higher Amp hour batteries and reduce the number of parallel strings. -
Re: battery connections
Marc ah hem,,, "12 each 6 volt ( cr225s) in a 24 volt system" sounds like 4 - 6 volt cells X 3 strings = 12??
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: battery connectionswestbranch wrote: »Marc ah hem,,, "12 each 6 volt ( cr225s) in a 24 volt system" sounds like 4 - 6 volt cells X 3 strings = 12??
Right, right. So only three strings. Much better than six, but still possible problems.
(I'm restructuring the porch roof. Sure hope I'm not making that kind of math error there. ) -
Re: battery connections
I've been using the #3 that Carriboocoot mentioned, on my six L-16 batteries in my 12 volt system.The only way to go with 3 strings. Works awesome and by the way, my batteries are now over 10 years old and still good to go! -
Re: battery connectionsCariboocoot wrote: »Right, right. So only three strings. Much better than six, but still possible problems.
(I'm restructuring the porch roof. Sure hope I'm not making that kind of math error there. )
Seen on a passing sweatshirt:
1. Measure twice
2. Cut once
3. &)($#^!
4. Buy more material
5. Repeat steps 1-4SMA SB 3000, old BP panels. -
Re: battery connections
It is debugging time...
Here is a "list" and the order I would do them in. I highly suggest getting a DC current clamp meter (like this one or better) + DMM.- If flooded cell, check electrolyte levels (above plates, at least--not too full or you will have a mess). Charge again if added water.
- Measure and log the specific gravity of each cell.
- With a rested bank (a few hours of no load/charging) check the battery (or cell--if you can) voltages. Look for high/low voltage across cell/battery.
- Turn on a heavy load and let run for a few minutes. Log voltages
- Use DC Current Clamp to measure current in each battery string (and log).
- Use a DMM set to 2.00 or 0.200 (200mV) full scale and look for excessive voltage drop across each connection/length of cable.
- Turn of loads and start heavy charging. Log beginning voltages.
- Log current through each string.
Now look at the above logs and find any differences. If most connections/wires have near zero volt drops and you see one with "high" voltage drop--check for dirty/loose/corrosion connections (or corrosion inside wire insulation).
Looks at the battery/cell voltages. A high voltage during charging can be an "open" or sulfated cell. Similarly, a low voltage during discharging can indicate open/sulfated cells.
You have been equalizing--Are the cells close together in specific gravity (around 0.015 to 0.030 maximum difference from high to low cells)? Are you charging/equalizing until SG stops rising (checking every 30-60 minutes)?
What is your solar array/charge controller's typical maximum charging current? What is the voltage/AH rating of your battery bank? Are you running around 5% to 13% of rated current (of 20 Hour AH capacity) as a charging current?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: battery connectionsIt is debugging time...
Thanks guys, it is debugging time, and I reckon I am the bug! Yes I will follow your suggestions.
Here is what I did a few years ago, (as configured diagram) not sure why I did it this way but was probably without adult supervision, and I actually added the last string almost a year after the original setup. Seems like I just need to make this change? (as revised diagram)
Michael
Attachment not found.Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
-
Re: battery connections
Better, but still less than perfect.
Key here is to make sure that the wires between batteries are equal length and wires between battery strings are equal length.
Another hint: if you draw your diagrams with all the battery polarities the same way it's easier to understand, even though you have to have diagonal connecting wires. -
Re: battery connections
You have competing requirements here...
Marc is suggesting to rotate the batteries to minimize wire length (voltage drop). Short/heavy cables are ideal--along with equal current paths between each battery string.
The "problem" with short/low resistance wiring paths is that any differences between batteries (age, temperature, dirty/loose connections, etc.) will tend to "steer" the current more (i.e., a colder battery with slightly dirty connections will get less current that a warmer battery with "good" low resistance connections).
The other issue to review--Connections from the Inverter and Charge controllers should be short and heavy too.
The inverter takes lots of current and simply needs short/heavy wires for low voltage drop. For a 12 volt system, you probably want a maximum of ~0.5 volt drop, 1.0 volt for a 24 volt, and 2.0 volt drop max for a 48 volt battery system.
For charge controllers, you want short heavy wires so the the voltage drop in the wiring does not interfere with the accuracy of the voltage as read by the charge controller... Roughly, my suggestion is around 0.05 to 0.10 volts maximum drop for a 12 volt system and ~0.1-0.2 volt max for 24 volt, and 0.2 to 0.4 volt drop maximum for a 48 volt battery bank.
You can use a generic voltage drop calculator to play around with distances and wire gauges to see what "works best" for you.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: battery connectionsYou have competing requirements here...
Michael
Attachment not found.Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
-
Re: battery connections
The only wires that need to be equal length are those involved with parallel current paths. The negative and positive wires from the battery bank to the inverter and/or charge controller do not have to be equal length. -
Re: battery connectionsCariboocoot wrote: »The only wires that need to be equal length are those involved with parallel current paths. The negative and positive wires from the battery bank to the inverter and/or charge controller do not have to be equal length.
Thanks for your help. Iv'e ordered a DC clamp on meter, ( needed an excuse I guess) and the extra length cables I need to reconfigure the batteries. After I get things rearrainged I will run through the tests you outlined.
MichaelOff grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed