Solar Expert Posts: 336 ✭✭✭
HI
I was wondering what the forum considers the most adequate protection between the PV array and the grid-tie inverter for say, a 400V grid-tie PV series of around 5A Imp.
I have seen normal DINrail 10A fuses 10x38mm being used. The problem is these tend to arc on extraction.... begging the question of whether they are suitable at all for this purpose ??
I was wondering what the forum considers the most adequate protection between the PV array and the grid-tie inverter for say, a 400V grid-tie PV series of around 5A Imp.
I have seen normal DINrail 10A fuses 10x38mm being used. The problem is these tend to arc on extraction.... begging the question of whether they are suitable at all for this purpose ??
Comments
-
Re: Protection for grid-tie systemsHI
I was wondering what the forum considers the most adequate protection between the PV array and the grid-tie inverter for say, a 400V grid-tie PV series of around 5A Imp.
I have seen normal DINrail 10A fuses 10x38mm being used. The problem is these tend to arc on extraction.... begging the question of whether they are suitable at all for this purpose ?? -
Re: Protection for grid-tie systemsYou should NEVER pull fuses under load unless the fuse holder is load break rated. I don't know if any of them are. Your system should have a DC disconnect; many inverters have integrated discos. You should open the disco before opening the fuse blocks.
Same with disconnecting MC4 connectors under load, and to a lesser degree connecting them under load.
If you don't have a disconnect with safe interrupting capability, cover the panels.SMA SB 3000, old BP panels. -
Re: Protection for grid-tie systems
A touch safe fuse holder used for solar panel combiners will actually catch fire when the holder is opened under load (one brand model at least).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Protection for grid-tie systemsHI
I was wondering what the forum considers the most adequate protection between the PV array and the grid-tie inverter for say, a 400V grid-tie PV series of around 5A Imp.
I have seen normal DINrail 10A fuses 10x38mm being used. The problem is these tend to arc on extraction.... begging the question of whether they are suitable at all for this purpose ??
Are you asking about 'overcurrent protection' or 'disconnecting means'? They are two different things. Overcurrent protection is generally only required if you have more than two strings. Disconnecting means are always required, and as inetdog said you need a disconnect with a safe interrupting rating. -
Re: Protection for grid-tie systemsAre you asking about 'overcurrent protection' or 'disconnecting means'? They are two different things. Overcurrent protection is generally only required if you have more than two strings. Disconnecting means are always required, and as inetdog said you need a disconnect with a safe interrupting rating.
One thing which is also often overlooked is that the fuseholders and the fuses within them have to be capable of interrupting a high DC voltage (particularly in the case of GTI strings or strings for a 48 volt battery system. Automotive type fuses (and fuseholders) can fail miserably under those conditions, and a fuseholder which can catch fire when you pull the fuse can also catch fire when the fuse fails to interrupt the current safely. So the first step is to confirm that the fuseholder and fuse each have a DC rating for current and voltage which matches your system. Back in the days when nominal 12 volt panels were used to charge 12 volt batteries using a PWM controller, the interrupting capability of the fuses was not such a big issue.SMA SB 3000, old BP panels. -
Re: Protection for grid-tie systems
Thanks for your replies.
The system I was looking at had a failing inverter. Yet, I figure that the fuses would only arc if there was current flowing (under load).. so what this means is that current was flowing, even if the inverter was not recognising it.. does this sound correct? -
Re: Protection for grid-tie systemsThanks for your replies.
The system I was looking at had a failing inverter. Yet, I figure that the fuses would only arc if there was current flowing (under load).. so what this means is that current was flowing, even if the inverter was not recognising it.. does this sound correct? -
Re: Protection for grid-tie systems
Well that's a lesson learnt! Will check with clamp meter in future, even if inverter says there is no current... -
Re: Protection for grid-tie systems
DC current clamp meter. The AC current/voltage detection devices won't work with DC.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Protection for grid-tie systems
No worries, my clamp meter does DC.. i'd normally always check first, but as the inverter seemed to be registering zero.. I wrongly assumed no current was present... I dont like to make mistakes with 400 Volts , so it wont be happening again!
The truth is it's made me doubt the use of MMPT systems in general for off-grid (for grid-tie there isnt a choice). In our off-grid systems, we only put in normal PWM type charge controllers, basically due to cost, although it's a shame to lose on the efficiency side. However after this episode, i'm thinking that maybe simply for saftey's sake.. it's best to leave off-grid systems at 24V. People have a tendency to do silly things on their installations, and we could at least avoid risk on the DC side of the system. Food for thought
Larry -
Re: Protection for grid-tie systems, i'm thinking that maybe simply for saftey's sake.. it's best to leave off-grid systems at 24V. ..... Food for thought
Larry
yup, that's why I opted for 24 vs 48V on our new system.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed