Combining MPPT and Non-MPPT Charge Controllers

sepsolman411
Registered Users Posts: 16 ✭
Is there any harm to connecting either in series or parallel one 30 Amp MPPT Charge Controller with one 30 Amp Non-MPPT Charge Controller other than cancelling out the MPPT function altogether? Array size is simply (2) 120 watt panels with the following specs:
Open-Circuit Voltage (Voc): 22.0V
Short-Circuit Voltage (Isc): 7.37A
Voltage at Pmax (Vmp): 17.5V
Current at Pmax (Imp): 6.86A
Output Tolerance: +/-3%
For controller parallel connections, would voltage and wattage capability double? i.e., 24 volts to 48 volts and 720W to 1440W
For controller series connections, would amperage capability double to 60 Amps?

Any feedback is much appreciated.
Open-Circuit Voltage (Voc): 22.0V
Short-Circuit Voltage (Isc): 7.37A
Voltage at Pmax (Vmp): 17.5V
Current at Pmax (Imp): 6.86A
Output Tolerance: +/-3%
For controller parallel connections, would voltage and wattage capability double? i.e., 24 volts to 48 volts and 720W to 1440W
For controller series connections, would amperage capability double to 60 Amps?

Any feedback is much appreciated.
Comments
-
Re: Combining MPPT and Non-MPPT Charge Controllers
PWM and MPPT controllers can work fine together.
I've got to ask why you wonder, as two 120 Watt panels will only put out <15 Amps and you don't put two controllers on one array. There is no point to it.
You also do not connect controllers in series.
But you can use two different type controllers each with its own array to charge one battery bank. -
Re: Combining MPPT and Non-MPPT Charge Controllers
If they work fine together, can a 30A MPPT charge controller be connected in parallel to a 30A PWM Charge Controller if I were to add panels to the array to achieve maximum wattage 1.4kw and between 48-60 amps? -
Re: Combining MPPT and Non-MPPT Charge Controllerssepsolman411 wrote: »If they work fine together, can a 30A MPPT charge controller be connected in parallel to a 30A PWM Charge Controller if I were to add panels to the array to achieve maximum wattage 1.4kw and between 48-60 amps?
Yes, but you have to split the array between the two controllers.
On a 12 Volt system this would not be 1400 Watts total. One 30 Amp PWM or MPPT controller could handle four of the panels you list (6.86 Imp * 4 = 27.44 Amps). That would be 360 Watts per controller for a total of 720 Watts.
On a 24 Volt system this would be double the panels as you would first connect two in series to get the Voltage up to the proper level for charging; the current remains the same. Total power doubles. -
Re: Combining MPPT and Non-MPPT Charge Controllers
Now I see the advantage to bypassing 30 or 60 amp MPPT or PWM charge controllers and backfeeding into the grid with an inverter, it does not make sense to increase panel array voltage and amperage if there is very little room to store a 24 or 48 volt battery assembly. Thanks for your feedback. -
Re: Combining MPPT and Non-MPPT Charge Controllerssepsolman411 wrote: »Now I see the advantage to bypassing 30 or 60 amp MPPT or PWM charge controllers and backfeeding into the grid with an inverter, it does not make sense to increase panel array voltage and amperage if there is very little room to store a 24 or 48 volt battery assembly. Thanks for your feedback.
You're talking about a completely different scenario there: grid tie vs. off grid.
You can store tremendous amounts of power in a battery bank, but everything has to be sized properly. -
Re: Combining MPPT and Non-MPPT Charge Controllerssepsolman411 wrote: »Now I see the advantage to bypassing 30 or 60 amp MPPT or PWM charge controllers and backfeeding into the grid with an inverter, it does not make sense to increase panel array voltage and amperage if there is very little room to store a 24 or 48 volt battery assembly. Thanks for your feedback.
Are you saying that you think it would be better to go with a grid-tied system rather than a stand alone off grid system?
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed