                    ok, i know your first response will be i am doing this backwards, but i understand that and have a plan in mind.
if i have a 50w mono panel, and am in the cincinnati area, what size battery (12v) would be appropriate for daily usage.
meaning, how much charge would i be able to get from this setup assuming 50% discharge max per day?
thanks!
                        
        
        
      if i have a 50w mono panel, and am in the cincinnati area, what size battery (12v) would be appropriate for daily usage.
meaning, how much charge would i be able to get from this setup assuming 50% discharge max per day?
thanks!
Comments
- 
            Re: max battery for 50w panel
 What are the specs on that 50w panel?
 they will give you the answer based on the charge rate you desire. 3%, 5%, 10%? and the number of days autonomy you want
 KID #51B 4s 140W to 24V 900Ah C&D AGM
 CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
 Cotek ST1500W 24V Inverter,OmniCharge 3024,
 2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
 Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
 West Chilcotin, BC, Canada
- 
            Re: max battery for 50w panel
 specs: Maximum Power Voltage: 17.5V; Open Circuit Voltage: 22V; Maximum Power Current: 2.86A
 average sun hours here is 3.8 or so. so if i want to use 50% of the battery each night, and charged back full each day, what mah would i need?
- 
            Re: max battery for 50w panel
 Most battery manufacturers advise that you need at least 110% - 120% of the consumed power to recharge a FLA battery.
 Using 4 hours sunlight and 2.86A you would generate ~11 Ahr, which at 50% DoD will allow you to recharge a ~15 Ahr battery as there is a ~ 70% efficiency de-rating factor to apply...
 NOTE: these are very general, approximate numbers
 YMMV
 HTH
 KID #51B 4s 140W to 24V 900Ah C&D AGM
 CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
 Cotek ST1500W 24V Inverter,OmniCharge 3024,
 2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
 Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
 West Chilcotin, BC, Canada
- 
            Re: max battery for 50w panel
 perfect! that's exactly the info i was looking for!
 THANKS!
- 
            Re: max battery for 50w panel
 The other rule of thumb to be satisfied is that the panel should be capable of delivering current to the battery at the C/10 rate for flooded and higher for sealed.
 Applying that rule gives us a maximum battery size of about 25 AH, even if you want to go larger than westbranch's calculation to get more cycles out of the battery.
 Using your number of 50% discharge, sets the size based on panel energy, but the real determiner there should be how many watt-hours you want to use, independent of battery size.SMA SB 3000, old BP panels.
Categories
- All Categories
- 232 Forum & Website
- 140 Solar Forum News and Announcements
- 1.4K Solar News, Reviews, & Product Announcements
- 199 Solar Information links & sources, event announcements
- 899 Solar Product Reviews & Opinions
- 256 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 655 Solar Water Pumping
- 816 Wind Power Generation
- 624 Energy Use & Conservation
- 620 Discussion Forums/Café
- 313 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed