Magnum ms4024pae - (ghost) inverter load
Re: Magnum ms4024pae - (ghost) inverter load
Could be anything,, I would check the voltage at the battery with a good volt meter when you see it,, and then check the battery cables with a clamp on ammeter to see if there really is a 16 amp load. Not an insignificant load,, close to 400 watts.
PS Welcome to the forum -
Re: Magnum ms4024pae - (ghost) inverter loadCould be anything,, I would check the voltage at the battery with a good volt meter when you see it,, and then check the battery cables with a clamp on ammeter to see if there really is a 16 amp load. Not an insignificant load,, close to 400 watts.
Thanks Tony - will pick up a voltmeter and check - hard to see why the inverter would require such a draw internally.
Guy -
Note, to measure the current, you probably will want either a battery monitor (very nice--if your inverter/charger does not have one already) or a simple/inexpensive DC Current Clamp Meter.
It is difficult to understand where ~400 watts is going. Usual question--You are SURE there is no AC load on the unit when this occurs? A Kill-a-Watt meter is very handy for use with AC inverters and even around a grid connected home for conservation measurements.
Hmm.
Do you have anything in the system which logs highest or lowest voltages? A trimetric battery monitor, an Outback FM or a Tristar charge controller?
Can you here the inverter when this happens?
How often does this happen?
Is it any sort of regular interval or certian time of day?
Do you have any:
-automatic loads which you may not be accounting for?
-anything with freeze protection which may cycle?
-leaking pipes, faucets, a running toilet which causes a pressure pump to briefly cycle?
-a sump or septic pump?
-a bad motor with thermal protection?
-anti-frost refrigerators or frezers (the watts seem too high for this but you may check to see if your fridge has an "economy" setting which can disable it for testing)
-old wiring with "mystery" circuits?
On or off grid?
Alex Aragon -
One thing you might check when you get those readings is the temperature of the transformer and transistors of the inverter (which the Magnum ME-ARC, at least, allows you to see, if that's what you have). If they are significantly higher than a normal 'no load' temperature reading, that would suggest the power is being consumed by the inverter for some reason, presumably a fault.
As Alex suggested, things like refrigerators can seem to be off, yet in fact be drawing hundreds of watts as part of the defrost cycle. -
continuing from eric's comments that if you suspect there could be a fault then try resetting the inverter as per the instructions in the manual on page 36. -
Thanks all!!! I will pick up some measuring devices and begin to log details when I see it. This is a w/e cabin so don't see it that often. Will also look for a high load in data log. I am concerned if an internal fault.
Guy