Brown out, what happens?
solar_dave
What happens to a Grid tie inverter during a brown out? Since this is hard on lots of devices, would be interesting to know if the Utility drops the voltage.
Does it follow the grid voltage or is there some lower limit it tries to hold?
    BB. Super Moderators, Administrators Posts: 33,740 admin
    Re: Brown out, what happens?
    A Grid Tied inverter will limit output current and power so that is does not damage itself.
    Plus, they will measure the incoming voltage and line frequency. If they are out of specification, it will turn off its output and wait 5 minutes before attempting to reconnect (part of UL safety requirements. For example, the Xantrex XW GT inverter's GT AC voltage limits (PDF Spec. Sheet):
    L-N: 108 - 130 +/- 1.5 Vac; L-L: 214 - 260 +/- 3.0 Vac
    The GT inverter will not really impact the brownout on your home by more that a few volts... If you see a brownout occur--The GT Inverter will most likely have already shutdown for safety.
  • solar_dave
    Thanks BB I suspected as much, the operating voltage range on this PVP5200 is 211-264, I guess the power company would have to brown it pretty hard to keep this one from running.
    product pdf
  • tampasolar
    tampasolar Registered Users Posts: 90 ✭✭
    If you end up in a part of the country that has forced brown outs, you will be able to change the voltage window on the existing inverter. Many inverters give you this control with the addition of a control panel. Others may require a pass code from the manufacturer to change grid tie parameters.
    Nobody should be off-grid-tie just because of brown outs.
    hybrid: two xw6848 pro with five mppt60, 13 kw pv
    17 cell Eve 280ah LiFePO4 storage  14 kw (now at 3 banks) total 40 kw
    gridtie: sunny boy sma 2x 5k
    Gateway / Insight Local
    i have the remote for my mms1012 and i have it set for the highest ac point it allows before switching over to inverting. 100vac. it will also allow me to go as low as 60vac all in 5vac increments.
  • tampasolar
    I guess a good parallel is this:
    On the solar panel side you have mppt that adjusts to voltage and energy fluctuations. On the grid side the electronics in the inverter is designed to force current into a sizable range of ac line voltages too.
  • oil pan 4
    I tested my cheap inverters down to 90vac through a varrac.
    They just put out more power, since they were connected to batteries for testing.
    oil pan 4 wrote: »
    i'm not so sure you are understanding what it is we are talking about. when grid power dips in voltage creating a brown out my inverter can automatically switch on by how low that voltage is to take over where the grid has failed. it has nothing to do with lowering the output voltage of an inverter or creating a brown out from your inverter. if you have that occurring from an inverter you need another inverter.