Ammeter in circuit
squarebob
Registered Users Posts: 25 ✭✭✭
Is it "OK" to put a non shunt type ammeter on a single 85w 12v solar panel. I would think I should put it between the CC ( sunsaver 6 ) and the battery to get a grip on the amps being sent to the battery.
Bob
Bob
Re: Ammeter in circuit
What you have to check is the voltage drop of the amp meter + wiring... A shunt based system is around 0.050 to 0.100 volt drop. I would not want to see any more than that for a 12 volt system.
For a PWM controller, you could put the current meter in the PV- lead before the charge controller. It will then not put another voltage drop in the charge controller's battery voltage measurement.
If this is temporary/debugging, you might want to use a DC current clamp meter. Very handy for debugging and checking other points in your PV/Load system.
A non shunt type amp meter is not really a good idea.And as shunts are inexpensive and accurate its by far the prefered method. I put them between the battery/ies and the CC. -
This particular ammeter has a double wrap of 12 GA wire around the back of the meter to induce the meter to register. I checked the voltage drop on the ammeter circuit and there is a 0.02 voltage drop. The meter is about 2' away from the CC. I would assume that this will not cause me any ill effects. What would be the benefits / drawbacks of putting the ammeter circuit on the PV side of the system vs the battery side.
Bob -
Re: Ammeter in circuitThis particular ammeter has a double wrap of 12 GA wire around the back of the meter to induce the meter to register. I checked the voltage drop on the ammeter circuit and there is a 0.02 voltage drop. The meter is about 2' away from the CC. I would assume that this will not cause me any ill effects. What would be the benefits / drawbacks of putting the ammeter circuit on the PV side of the system vs the battery side.
Bob
With a PWM controller, every amp going to the controller, also goes to the batteries, so you still get a good reading. This does not apply however to a MPPT type controller, as they will use extra panel watts and convert them into higher battery charging amps than what actually came from the panels. Thus with MPPT controllers, panel amps and battery charging amps, often don't match. -
it is fine to use that meter if you acknowledge that it isn't needed to be actively reading the current all of the time as .2v drop is not good to have. the solution is to have a switch across the meter's leads so that when on it shorts across the leads and bypasses the meter. off will place the meter in series with the wire circuit and allow the reading. i probably made it sound more complicated than it is. -
It sounds like the meter is just using the magnetic field from the 12 AWG wire to move the needle. 0.02 volt drop is nothing to worry about and it should be just fine (as long as you do not exceed the meter's maximum current).
I am a big believer in monitoring the battery--so in this case, I would agree with placing the meter in the battery negative post (to meter) to negative bus. There you can monitor the sum of the load+charging current (see what the battery is actually getting, not just what the array current is).
oops, my oversite as i was a bit off on my decimal places and bill is right that .02v will be fine for a v drop. -
Re: Ammeter in circuit0.02 volt drop is nothing to worry about
-Bill -
Its OK Wayne--Your head was just blocking my view.
Anyway, there are many issues with designing, building, and operating your own power station--It is a bit like drinking from a fire hose at the beginning...
It is one reason I like to use "rules of thumbs" at the beginning. It helps everyone get the basics of the Off Grid solar system and see how it all plays together.
Once you get a clear picture (and Wayne moves his head), then we can discuss the ugly little details a piece at a time.
Thanks for all the info. Wayne - move a little bit to the right!! :roll: The meter is just to satisfy my curiosity as to how many amps the battery is getting from the PV. The system doesn't warrant a trimetric or other monitoring system at this point in the game. It's just good to have a visual aid to know that electrons are flowing!!
Bob -
Re: Ammeter in circuitThanks for all the info. Wayne - move a little bit to the right!! :roll: The meter is just to satisfy my curiosity as to how many amps the battery is getting from the PV. The system doesn't warrant a trimetric or other monitoring system at this point in the game. It's just good to have a visual aid to know that electrons are flowing!!
Bob
Actually I was reading about how scientists are working on making small things invisible, causing light to flow around small objects like water around a smooth stone. Thought that might work for me, but then realized there were two major problems to overcome. One, my head is way too swelled, and two, having a square head causes visible light turbulence as said light flows around the edges. So I fear there's no hope for me in this life.
- 228 Forum & Website
- 618 Discussion Forums/Café
