wire sizing
97TJ
Solar Expert Posts: 68 ✭✭
Hi I have been searching the forum for the answer to my question but I am still confused. I just received my crown 6 volt 245 amp batteries. I have a total of 4. Will wire series parallel. What size wire do I need to use for the connections? Right now they are going on the shelf for a float charge until I can install them this spring. Thanks for your help.
Craig
Craig
Comments
-
Re: wire sizing
Are you going to run a 12v or 24v system
If you are running 12v. wire the 2 sets in series then parallel them together. If you are running 24v, they will all need to be in series.
As for wire size, that also depends on how many amps you are using and over how long of a run. How many amps/volts need to travel over the wire and how far? -
Re: wire sizing
Assuming 12 volt (series parallel), you would need only about 1% rate of charge for "floating" the battery bank.- 490 AH * 1% = 4.9 amps minimum float charger rating
- 12 awg @ 4.9 amps and 5 feet (one way) run of wire -> 0.1 volt drop
Check the battery manual and see what they recommend for your battery bank (usually around 13.2 to 13.6 volts or so).
If the float charger appears to recharge at too high of voltage (voltage cannot be set), get a heavy duty lamp timer and set it for 1-8 hours a day or so (watch battery resting voltage, amount of bubbling, and water use).
Even a 1 amp charger can eventually boil a battery dry over time if it floats the batteries at too high of voltage.
If you were going to do this with solar panels and a small charger controller:- 4.9 amps * 17.5 Vmp * 1/0.77 derating = 111 Watt panel (roughly)
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: wire sizing
12 volt system. Per battery mfg, float is at 13.5 volts. Charger specs say float output is 13.2 volts. I'll add another question. When I end up putting this all together, I will be using an cotek 1000 watt pure sine inverter. What size wiring then? 2/0 from the battery bank t the inverter? I have "fooled around with the voltage drop calculator and I believe I have a good idea of what I need from the panels to the charge controller. Not quite sure all the placement of fuses and disconnects but I'm working at it. I hope to be able to get things set up some time this summer. Thanks again. -
Re: wire sizing
Using some generic numbers:- 1,000 watts * 1/0.85 inverter eff * 1/10.5 volts cutoff * 1.25 NEC safety factor = 140 amp minimum wiring/fusing
- 5' one way trip cable, 1 volt max drop, 140 amps load, 2/O cable -> 0.13 volt drop
The minimum cable would probably be:- 5' one way trip cable, 1 volt max drop, 140 amps load -> 6 awg @ 0.7 volt drop
Remember that fuses and switches will add voltage drop too--12 volt battery bank does not leave a lot of headroom for voltage drop (11.5 volt minimum battery voltage--charged under load, 10.5 voltage cutoff for most inverters). Add a surge current (typically a good inverter will surge 2x rated voltage)--You don't want the inverter to shut down when trying to start a heavy load/pump/motor.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: wire sizing
Wire can never be to big.. only to small! -
Re: wire sizingWire can never be too big.. only too small!
Technically, that is not always true... For example, say you have a breaker rated for 10,000 AIC (amps interrupt current) and a really large power source (a 10,000 Amp pole transformer or a large DC Battery bank).
If you have a dead short and too heavy/short of cabling, it is possible for the power source to exceed the AIC rating of the protective device. For example, commercial power users in (at least) Northern California that have a very short run from the pole/pad mounted transformer to the main disconnect cannot use standard main panel breakers. They have to use special high AIC fuses instead. If the main panel is more than XX feet from the transformer, then they are able to use standard rated breakers because of the additional resistance/impedance of the longer drop.
-Bill "generalizations are always wrong" B. :roll::p:DNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: wire sizing
i'm going to remind you that the series battery interconnects add to the run going to the inverter. i concur the 5ft run is good for #00, but if you have a 1ft intertie on the batteries this means the run to the inverter is now limited to a 4.5ft run as a 4.5ft run consists of 2 wires both 4.5ft long adding up to 9ft total to be added with the 1ft battery intertie for a total of 10ft of wire and that is a 5ft run. if the wire lengths are longer, or as was mentioned with fuses/breakers or even a switch, this adds extra resistance making a thicker wire necessary.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed