Panel wiring: series, parallel or both?? (Help!)
Mr.Cockburn
Solar Expert Posts: 34 ✭
Hi everyone,
I will be installing 4 kyocera KD185GX-LPU panels to charge 2 6v, 215ah batteries wired for 12volt loads. My charge controller is an Outback FM-80.
Here's the thing... I was going to wire the panels in series being that the array is located about 75 feet away from the cabin (save $ on wire, right?) BUT I read that series wiring is not good at all with shading or snow on panels, etc... Snow is really a concern on my site because we have some for like, 4-5 months a year. As for shading, not so much because I chose the site accordingly. I must also specify that I only go to the cabin on weekends so sometimes snow might cover some parts of the array for days on since I am not there to remove it.
Now I'm a little confused.... Do I go all parallel, (I know this will require massive wiring and quite a lot of dollars!) Or do I go for a series/parallel setup ? Or maybe a series-only setup will do after all?
I really need to maximise my panels as my location is (obviously) not ideal as to peak sun-hours, etc...
Any help you can provide will be greatly appreciated! Thank you.
Kyocera KD185GX-LPU panel specs:
Pmp: 185 Watts
Vmp: 23.6 Volts
Imp: 7.84 Amps
Voc: 29.5 Volts
Isc: 8.58 Amps
I will be installing 4 kyocera KD185GX-LPU panels to charge 2 6v, 215ah batteries wired for 12volt loads. My charge controller is an Outback FM-80.
Here's the thing... I was going to wire the panels in series being that the array is located about 75 feet away from the cabin (save $ on wire, right?) BUT I read that series wiring is not good at all with shading or snow on panels, etc... Snow is really a concern on my site because we have some for like, 4-5 months a year. As for shading, not so much because I chose the site accordingly. I must also specify that I only go to the cabin on weekends so sometimes snow might cover some parts of the array for days on since I am not there to remove it.
Now I'm a little confused.... Do I go all parallel, (I know this will require massive wiring and quite a lot of dollars!) Or do I go for a series/parallel setup ? Or maybe a series-only setup will do after all?
I really need to maximise my panels as my location is (obviously) not ideal as to peak sun-hours, etc...
Any help you can provide will be greatly appreciated! Thank you.
Kyocera KD185GX-LPU panel specs:
Pmp: 185 Watts
Vmp: 23.6 Volts
Imp: 7.84 Amps
Voc: 29.5 Volts
Isc: 8.58 Amps
Comments
-
Re: Panel wiring: series, parallel or both?? (Help!)
As for snow, can you mount the panels vertical? What you lose by not being aimed at the sun can be gained back by reflection off the snow on the ground.
As for wiring the panels in series, that is generally an excellent idea with a MPPT controller... BUT in your case I would worry that you might exceed Vmax for your controller... 4 panels at 29.5 Voc at low enough temperatures could exceed the 150 volt max for your controller.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Panel wiring: series, parallel or both?? (Help!)
Use Niels spreadsheet for voltage drop for each combo of panels, including 3 in series and see what you are willing to accept for losses.
http://forum.solar-electric.com/showthread.php?29-voltage-drop-calculator
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Panel wiring: series, parallel or both?? (Help!)
Not often I type this... "You have a lot of solar panel for your planned battery bank".
Will not hurt anything, but will require a larger charge controller because of the large(r) solar array.
What type of charge controller are you looking at... the minimum would be the MorningStar TS 45 amp MPPT charge controller (certainly a very nice controller but around $420 or so).
Shading of panels is not great in any case, and as Vtmaps said, mounting near vertical to shed snow can be a very good thing.
For a 75 wire run (one way, some voltage drop calculators require two way length) your two option extremes (all parallel or all series) using a generic voltage drop calculator. First all in parallel:- 75 feet, 23.6 Vmp, 4x 7.84 amps = 31.36 amps ; 3% voltage drop * 23.6 = 0.708 volts -> 75 feet @ 31.36 amps 0.7 volt drop with 1 AWG cable
- 75 feet, 23.6 Vmp, 4x 7.84 amps = 31.36 amps ; 1% voltage drop * 23.6 = 0.236 volts -> 75 feet @ 31.36 amps 0.24 volt drop with 250 kcmil cable
- 75 feet, 4x23.6 Vmp=94.4 Vmp, 4x 7.84 amps ; 3% voltage drop * 94.4 = 2.832 volts -> 75 feet @ 7.84 amps 2.25 volt drop with 12 AWG cable
- 75 feet, 4x23.6 Vmp=94.4 Vmp, 4x 7.84 amps ; 1% voltage drop * 94.4 = 0.944 volts -> 75 feet @ 7.84 amps 0.89 volt drop with 8 AWGl cable
- 17.5 Vmp ideal / 23.6 Vmp = 0.74 = 74% of rated panel power "lost" due to Vmp / Vbatt-charging mismatch
- 23.6 volts - 17.5 volts = 4.1 volt cable voltage drop "available"
- 75 feet, 4.1 cable drop, 31.36 amps Imp -> 75 feet @ 31.36 amps @ 3.6 volt drop with 8 AWG cable
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Panel wiring: series, parallel or both?? (Help!)
Thank you all for your replies. I plan on adding to my battery bank later on, (buying all new batteries) but for now I only have these two. As for my charge controller, it is an Outback FM-80 MPPT. Mounting near vertical will be hard because I was planning on mounting the array on an existing post about 11 feet high, so I was planning on a 45 degree angle (my lattitude). I guess I could go a bit more for clearing snow but how will this affect my summer performance?? I don't plan on changing angles every season.
So far, nobody has talked about a series/parallel setup, is this because it would not be good? -
Re: Panel wiring: series, parallel or both?? (Help!)
Series/Parallel setup will work too... And the wire gauge will be in-between what I estimated above (8 awg would probably work fine with ~2-3% losses).
There is also the issue, I believe, that some MPPT charge controller are most efficient with Vmp-array at ~2x Vbatt-charging voltage. If I recall correctly, somebody here had an Outback series (FM/MX?) charge controller with ~70-100 VDC array input voltage and 12 volt battery bank--It caused the charger to run hot enough that the fan needed to run. When re-wired to ~2x battery voltage, it ran cooler (not an expert by any means, do your reading of the manual and perhaps somebody here can elaborate/confirm/deny).
If you are going to install a larger battery bank, you probably will want/need to revisit the whole 12/24/48 volt battery bank and inverter choice.
Also, when you trench (I assume) for the PV array to battery shed cable run--I would suggest one or several large conduits so you can pull/upgrade cables without having to open the ground up again.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed