I am wanting to use a solar pump that requires 72-144 volts and 800-1500 watts. I am wanting to use Canadian Solar CSI CS6P-235PX 235W Solar Panel. My problem is i don't know how many panels and what configuration I need to meet the middle of the road requirements of this pump. Any help is appreciated
Re: new solar pump
What brand and model of pump? Need to know more about its input power requirements. Solar panels are not very "accurate" or "stable" in their voltage/current output. Their voltage changes with temperature and loads.
Re: new solar pump
Ok Lets try again if a pump calls for 72 volts and 1300 watts, how would you configure solar panels with Imp of 7.66 and Voc of 30 volts? If you hooked parallel 6 panels at 230 watts you would have 1380 watts but only 30 volts. If you hooked 3 panels in series you would have 90 volts but only 230 watts. How would you match both requirements of the pump? -
Re: new solar pump
again, what model/make of pump so one can look up the power ( Amps and Volts) needed by the pump and to compare to the various configurations of the panels.
HTH
Re: new solar pumpsolar pump that requires 72-144 volts and 800-1500 watts. I am wanting to use Canadian Solar CSI CS6P-235PX 235W Solar Panel
Panel spec. appears to be:Pmax=235W
Vmp=29.8V
Imp=7.90A
Voc=36.9V
Isc=8.46A
So, say the pump will accept a Vmp range of 72-144 volts:- 72 volts pump min / 29.8 volts Vmp-stc = 2.4 panels in series
- 3 panels (whole number) * 29.8 Vmp = 89.4 volts Vmp-stc
- 89.4 volts Vmp * 7.90 Amps Imp = 706.3 watts per string
- 706.3 watts * 0.80 derating = 565 watts "nominal" output power on typical warmish day
You could do the same thing with 4 panels in series:- 4 panels (whole number) * 29.8 Vmp = 119.2 volts Vmp-stc
- 119.2 volts Vmp * 7.90 amps Imp * 0.80 derating = 753 watts nominal per string.
A 4 string panel can easily exceed 144 volts on a cold day with no load (say water tank is full), and could damage your pump controller/electronics.