Back feed circuit breaker
![System](http://northernarizona.vanillaforums.dev/applications/dashboard/design/images/usericon.png)
System
Posts: 2,511 admin
I am planning on installing a 8 kw Grid Tied PV system. The building inspector (in Virginia) is requiring a back feed breaker in the main panel. Is this something new in the code? I haven't had it come up before.
Comments
-
Re: Back feed circuit breaker
In the 2011 code: 690.10 (E)
(E) Back-fed Circuit Breakers. Plug-in type back-fed circuit
breakers connected to a stand-alone inverter output in
either stand-alone or utility-interactive systems shall be secured
in accordance with 408.36(D). Circuit breakers that
are marked “line” and “load” shall not be backfed. -
Re: Back feed circuit breaker
There are two "Back Feed" requirements that I am aware of...
One is a fuse or breaker to prevent back feed into the solar array. An older requirement and one that my vendor got around by an engineering statement from the manufacturer that stated it will not back feed the solar panels at any time.
The second is what Jburgess posted. That is every GT inverter must have a branch circuit breaker from the main panel that is rated for the gauge wire used (i.e., 14 awg wire is 15 amp breaker, 12 awg is 20 amp, 10 awg is 30 amp, etc.).
And some breakers are marked "Line" and "Load" on their connections--those breakers cannot be back feed or it will violate their UL Listing.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Back feed circuit breakerIn the 2011 code: 690.10 (E)
(E) Back-fed Circuit Breakers. Plug-in type back-fed circuit
breakers connected to a stand-alone inverter output in
either stand-alone or utility-interactive systems shall be secured
in accordance with 408.36(D). Circuit breakers that
are marked “line” and “load” shall not be backfed. -
Re: Back feed circuit breaker
That exception was eliminated in the 2011 code.
Here's 690.64 in the 2011 code:
690.64 Point of Connection. Point of connection shall be
in accordance with 705.12. -
Re: Back feed circuit breakerThat exception was eliminated in the 2011 code.
Here's 690.64 in the 2011 code:
690.64 Point of Connection. Point of connection shall be
in accordance with 705.12. -
Re: Back feed circuit breaker
Good to know. Thanks.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed