Back feed circuit breaker
I am planning on installing a 8 kw Grid Tied PV system. The building inspector (in Virginia) is requiring a back feed breaker in the main panel. Is this something new in the code? I haven't had it come up before.
Re: Back feed circuit breaker
In the 2011 code: 690.10 (E)
(E) Back-fed Circuit Breakers. Plug-in type back-fed circuit
breakers connected to a stand-alone inverter output in
either stand-alone or utility-interactive systems shall be secured
in accordance with 408.36(D). Circuit breakers that
are marked “line” and “load” shall not be backfed. -
There are two "Back Feed" requirements that I am aware of...
One is a fuse or breaker to prevent back feed into the solar array. An older requirement and one that my vendor got around by an engineering statement from the manufacturer that stated it will not back feed the solar panels at any time.
The second is what Jburgess posted. That is every GT inverter must have a branch circuit breaker from the main panel that is rated for the gauge wire used (i.e., 14 awg wire is 15 amp breaker, 12 awg is 20 amp, 10 awg is 30 amp, etc.).
And some breakers are marked "Line" and "Load" on their connections--those breakers cannot be back feed or it will violate their UL Listing.
But that does not mean that they have to be secured with the extra fasteners that 408.36(D) requires. 705.12(D)(6) (referred to by 690.64, which was where this language was in the NEC200eight) grants an exception for listed utility-interactive inverters. I assume that this is because of UL1741 which requires that utility-interactive inverters shut off when they no longer "see" grid voltage on their outputs, so if you pull the breaker even under load all its terminals will be de-energized.In the 2011 code: 690.10 (E)
That exception was eliminated in the 2011 code.
Here's 690.64 in the 2011 code:
690.64 Point of Connection. Point of connection shall be
in accordance with 705.12. -
It wasn't eliminated, just moved. 705.12(D)(6) Fastening. says: "Listed plug-in type circuit breakers backfed from utility-interactive inverters that are listed and identified as interactive shall be permitted to omit the additional fasteners normally required by 408.36(D) for such applications." This is virtually verbatim what 690.64(B)(6) said in NEC2008, but in NEC2011, 690.64 simply points to 705.12, which says the same thing.That exception was eliminated in the 2011 code.
Good to know. Thanks.