Connecting batteries in Parallel
n1st
Solar Expert Posts: 77 ✭✭✭✭
I have four 6v 220ah batteries. I've split them into pairs. Each pair is made of 2 batteries connected in serial. One pair is 12.96v, the other is 13.01v. When I attempt to connect the two pairs to each other in parallel to double current, with cables that have fuses in them, the fuses are blowing. I started with 5a fuses and moved up to 7.5a. I'm puzzled, I've done this many times before with no issues.
Is the voltage differential enough to be causing this?
Re: Connecting batteries in Parallel
in series you place the 1st battery's + to the 2nd battery's -. do this for the other 2 batteries as well. after that tie the 1st string's - connection to the 2nd string's - connection. do the same with the top +s so that the 1st series string parallels the 2nd series string. if fuses are blowing you have it wrong and are creating a short circuit. -
It COULD be the difference in voltages, but still the voltage doesn't seem that far off. Are you really sure that by some slip of attention, or error, the two strings might not be connected + to + and - to - ? That is, the + from one of the two strings, connected to the + of the other string, and the same for the two - terminals.
You might try charging and doing an EQ on each of the two strings separately, then let them sit for a few hours until the voltages settle, hopefully very closely, and try connecting them together again, perhaps with a 30 amp fuse in case there might be some instantaneous surge if the voltages still don't exactly match. -
A Voltage difference of 0.05 should not blow any fuse.
Check wiring as per attachment. -
Thanks for all the input - I see the error of my ways. The parallel connects were coming off of the same battery in one of the pairs. It Looked like this(thanks CC).... -
That would do it. Putting 12 Volts to 6. :roll: -
Greetings
Learning here. Would this mean that n1st would have a 12 volt bank with 440 AMP hours now?
Regards
TDSolarguy -
Re: Connecting batteries in ParallelTDSolarguy wrote: »Would this mean a 12 volt bank with 440 AMP hours now?
Regards
TDSolarguy
Yes, but only IF all 4 of the batteries are up to scratch. Any single, or more of the batteries that aren't up to specs will drag down the lot.
- 616 Discussion Forums/Café
