Whew! Man, I have BAD GAS!
drew4justice
drew4justice Solar Expert Posts: 36
Just curious if anyone can answer a question about the absorpbtion stage on my Tristar MPPT45.
I'm currently in absorption as I type this and my batteries are bubbling like an aquarium! We've had a streak of an hour's worth of sun, but I'm trying to bring a new bank of Trojan T105RE's up to proper specific gravity but we've have lots of clouds/rain around here. I don't expect the sun to last much longer.
MY question: If get 100 minutes of sun then the sky clouds over for 2 hours (so I never hit float) and then another 80 minutes of sun, would that cumulate and complete the absoption stage, or will it start over again expecting a full, non-stop charge of 180 minutes?
Assumptions:
--The absorption time configured on my MPPT is 180 minutes.
--I have my inverter off, therefore no load connected.
I guess I could wait and find out myself but it's interesting and educational getting everyone's feedback.
Drew
    Re: Whew! Man, I have BAD GAS!
    What is the charging voltage and what is the battery temperature (and do you have a remote battery temperature sensor for the controller).
    You do not want to charge too high of voltage for too long... "Equalizing" a battery (charging ~15 volts) for long periods of time (over 30-60 minutes) is hard on a battery. Usually, you "Equalize" until all of the cells stop increasing specific gravity (back to back measurements every 30-60 minutes). And the usual plan is to equalize every 1-3 months--not every week or every day.
  • drew4justice
    Thank you for your input.
    The temp outside is 73F. I don't think it's much warmer where the batteries are located since they're in the shed. I do however have a remote sensor installed on one of the (-) terminals in the middle of the bank. At any rate, the battery bank is about 4-5 feet below the mppt controller so the temp difference shouldn't be huge unless the batteries warm internally. They also feel fine to the touch.
    I have 4 batts in series for a 24v bank. The charging (absorption) voltage is 29.4v. I'm not in EQ mode, just absorption. I'm a little concerned. Should they not gas in absorption? EQ for the T105RE's is 30.96 and my Trimetric as well as my Fluke meter show me at 29.4v. (Actually I made it sucessfully through the absorbtion and now I'm currenty in float at 26.4v with no more bubbling.)
    EDIT: The S.G. is coming around just under the desired mark of 1.260. I have a cheap (read non-precise) hydrometer from Amazon, but I'm pleased to see the system bringing the S.G. up from around the 1.220 it was.
    Drew
    Sounds like everything is working well... You can adjust the voltages and timers to meet your needs.
    I believe some folks here will set shorter absorb times in summer (lots of power) and longer times in winter (sun sets before charge controller times out).