We recently added PV to an older (2005) Outback system which has the negative and ground tied to the same bus bar. Since this is the case, we could not add in a GFCI as required by the NEC. We would like to suggest upgrading the system by adding a negative bus and separating the negative and ground wires. Otherwise, it is not clear how the GFCI will work if the negative and the ground are bonded together. Any clarification would be appreciated.
Also, we think we should add a separate GFCI for each PV system (the original installed in 2005 and the one we just installed). Does this make sense?
Also, we think we should add a separate GFCI for each PV system (the original installed in 2005 and the one we just installed). Does this make sense?
Comments
-
Re: GFCI upgrade to older Outback system
If it works as is, don't change it. Just my opinion but this GFCI obsession of Wiles' is getting out of hand. Next the NEC will demand arc-fault breakers on all panels over 0.5 Watts. :roll:
But if you feel you must comply with this code change then yes you'll have to separate the ground and negative and make sure the two are isolated save the GFCI connections. And you should do all the arrays because inevitably the negatives are shared in common throughout so leaving even one -/G connection could foul the whole system. -
Re: GFCI upgrade to older Outback system
Yep my feeling is about the same. If there is not a large gauge bond between Battery - and earth ground then the Battery - actually becomes a current carrying conductor like the Battery + not a Grounded conductor like IT SHOULD BE. So I feel that there at minimum needs to be breakers on + and - conductors when GFP is used.
BB did a wonderful paper on the hazards of GFP and I completely agree with his statements made and actually verified a few for him here at MidNite. Here is a link to the paper that was submitted to Wiles.
http://www.midnitesolar.com/pdfs/DC-GFP-Draft3-5.pdf -
Re: GFCI upgrade to older Outback system
What I hear you recommending is to NOT upgrade the existing system unless we have to, but if we have to, make sure there are OPDs on both positive and negative conductors. Is my understanding correct?
Also, if we do add the GFCI, do I need two (one for each PV array), or should there be a triple pole GFCI (if one exists) so they both open at once if one faults? -
Re: GFCI upgrade to older Outback system
If you have solid battery to earth grounds--you only neeld one breaker/fuse on each + connection.
If you fuse/breaker the battery to earth ground--my opinion is you need dual breakers (sort of like the pair of 240 VAC breakers you see in your home breaker panel) for safety.
I am not sure if you have two+ solar arrays how you do the GFI. Partially, depends on the charge controller you select...
If you use the external DC GFI setup--You might have to simply parallel the two 1 amp breakers, one for each 1a/63a Solar Array disconnect.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: GFCI upgrade to older Outback system
My take (which may not be right): all panels connected to one charge controller is a single array which should be protected by one GFCI system - one which interrupts both (+) and (-) like Bill said.
If there is a second charge controller its panels would be considered a separate array and would require its own GFCI system.
And good luck getting the negative and ground separated everywhere. Next thing you know one GFCI per array won't be good enough; they'll want one per string. Meanwhile more houses burn down from over-loaded 18 AWG extension cords that have the ability to connect between a source and a load capable of exceeding their capacity, but have no circuit protection requirements for the cords themselves. Go figure. :roll: -
Re: GFCI upgrade to older Outback system
Bill,
What has been your feedback from John Wiles ? I have not agreed with you in one aspect of GFCI. This is with XWCC's when operated as part of an XW system. Care to guess? It is a reason to want GFCI as implemented by Xantrex in the XW.
--Dave"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Re: GFCI upgrade to older Outback system
Dave,
Sorry, I lost the thread and never replied to your question...
No, I have not heard from anyone about my issues that is connected with the NEC process (that I know of).
I have had about a 1/2 dozen people that emailed and called--And those that expressed an opinion/discussion back with me all believed that a breaker/fuse between return and frame/earth ground was not acceptable in their fields of engineering/product design.
I did send an email take discussion of the NEC ground fault code overlaid against the UL requirements for safety grounding in Solar Charger Controllers and Inverters... Basically, one of the major requirements is to pass a 30 amp (I think it is around 30 amps) test current between return and frame ground in order to define it as a safety ground. Obviously, a 1 amp breaker or fuse is not going to meet that requirement.
Dave, regarding why you like the XW integration of ground fault detection... My guess is that a ground fault will indicate it on the inverter/charge controller so you can take positive action and fix the shorted circuit instead of waiting for other failures to manifest (such as a fire, shock, or failure to charge battery bank which then cost a bunch of $$$ to replace).
However, I believe the safety and system integration issues are still problems that cannot be fixed/addressed by the current GFP detection breaker scheme--which (as near as I can tell) was intended to reduce the chances of sustained arc faults causing a fire (and which the GFP detection breaker does a fairly poor job at preventing/suppressing).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed