Backfed breaker or Line side tap?
Re: Backfed breaker or Line side tap?
How do you know if you need a service feed upgrade from the transformer?
I live in a subdivision built in 1995 and all the wires are buried underground.
I currently have a full 100amp panel. If I upgrade to a 200amp outside load center will I have to have the power company do something else? in order words is the wire going to my house capable of delivering 200amps? -
Re: Backfed breaker or Line side tap?rollandelliott wrote: »How do you know if you need a service feed upgrade from the transformer?
At least in my experience (my house), I have 100A service, and I think the wire is good for 125-150A (don't remember exactly). And the conduit is not up to current codes, so new conduit would need to be run. This means digging a 30ft long 18" deep trench from my main service panel to the utility hand-hole. The quote I got for doing this was crazy expensive.
IMO, the best solution in this case (where I don't actually need 200A service, but need the bigger panel if I want to add more PV) is to upgrade the panel to a 200A panel and size the main breaker for whatever the wire is rated for. This gets you as much room for as much PV as you'd ever want to add, and if you really do need/want 200A service down the road, you can dig the trench and pull new wire then. -
So I would just take out the preinstalled 200amp breaker and replace it with a 100amp breaker and be able to add up to 140amps of solar power?
which is probably around 20KW! More than I would ever install. -
Re: Backfed breaker or Line side tap?rollandelliott wrote: »So I would just take out the preinstalled 200amp breaker and replace it with a 100amp breaker and be able to add up to 140amps of solar power?
Re: Backfed breaker or Line side tap?Well, yes, but understand that when you do that, you reduce by half the amount of power that your house can pull from the grid.
I think the point was he only has a 100 amp service now. This was to allow a decent backfeed percentage on the panel. -
Re: Backfed breaker or Line side tap?solar_dave wrote: »I think the point was he only has a 100 amp service now. This was to allow a decent backfeed percentage on the panel.
Make sure the inspector and the utility co. will sign off on it before you do it.
If there is a chance someone could come along later and swap out the 100a breaker for a 200a - but the feed wire isn't rated for 200a...
It's likely they won't even allow an upgrade to a 200a panel unless the feed is wire is also upgraded.
THEN, of course, you can install a 100a main breaker if you want. -
Re: Backfed breaker or Line side tap?If there is a chance someone could come along later and swap out the 100a breaker for a 200a - but the feed wire isn't rated for 200a...