wire sizing confusion,
zozomike
Solar Expert Posts: 134 ✭✭✭
Hi, I have 12 Shell/ Solar World 165 panels set at 45 degrees, with orientation true south. They are divided into 4 strings with a combiner feeding to a FX80, the run to controller is almost 80'. Summer FX80 readings are voltage mid day hovering around 110vdc, amps 20. Those seem to indicate a feed wire #8, I had #10 before but a backhoe (ahem, accident ) means 1'm upgrading again. My confusion is when I read the specs on the panel it says peak power current is 4.72A, times 12 that's 56 A, which would require a $#4 run? I must be misunderstanding the spec? I hope?
Thanks
Thanks
Off grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
Comments
-
Re: wire sizing confusion,Hi, I have 12 Shell/ Solar World 165 panels set at 45 degrees, with orientation true south. They are divided into 4 strings with a combiner feeding to a FX80, the run to controller is almost 80'. Summer FX80 readings are voltage mid day hovering around 110vdc, amps 20. Those seem to indicate a feed wire #8, I had #10 before but a backhoe (ahem, accident ) means 1'm upgrading again. My confusion is when I read the specs on the panel it says peak power current is 4.72A, times 12 that's 56 A, which would require a $#4 run? I must be misunderstanding the spec? I hope?
Thanks
Your max current from the array will be (1.25)(4)(Isc). You'll want to derate the conductors for continuous use/conditions of use and then size them up if you need to to get to whatever voltage drop is acceptable to you. -
Re: wire sizing confusion,
The Solarworld 165's Isc is 5.3 Amps. You've got four strings in parallel, so that's 21.2 for the whole array. Times the NEC derating is 26.5 Amps. The Voltage on three in series will be around 120 (103.2 Vmp, 129.9 Voc) so using the only V-drop calculator I can get to work on this netbook ... 80 foot run I get a result of 2.7 Volts drop using 8 AWG and that's less than 3% of the low Voltage figure, so that's what I'd pick. -
Re: wire sizing confusion,
Ah, I was adding all the amps of each panel, I thought I was correct with #8 but having failed at this "simple " stuff too often wanted to check before digging another ditch. thanksOff grid, all solar, passive and active (winter wood heat supplements) PV DHW.
Array 1-- 12 Sunpower 250, Outback FM 100 3kw
Array 2-- 12 Sunpower 250, Outback FM 100 3kw
Well array 780w, 6 Kyocera 130 w with Grundfos sqflex 11 and cu200 to elevated storage, ( 2- 330 g tanks,) no battery storage at well
10 24 volt Battle Born Lithiums
Outback Flexpower Two, VFXR 3524A 7kw
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed