Sizing Batteries
czars
czars Registered Users Posts: 16
Does anyone have a suggestion about how to properly size a 48v battery bank for a 4500 grid-tied inverter?
    BB. Super Moderators, Administrators Posts: 33,734 admin
    Re: Sizing Batteries
    What setup are you asking about? A Xantrex 4.5kW 48 volt Hybrid Inverter setup?
    The normal recommendation would be 450 AH @ 48 volt minimum battery bank to support the maximum charging/load surge currents.
  • czars
    You guessed correctly - Xantrex XW4548. Thanks for your input.
  • Solar Guppy
    A common mistake is only sizing for the backup condition.
    The requirement is not only based on what the inverter load ( AC out ) is but what the load to the grid in sell mode can be ( AC in 1 ) as the inverter is bi-directional.
    Which ever is greater load ( selling to the grid OR backup load ) the battery bank minimum needed is 100ah @ 48V nominal bank voltage per kW