Sizing Batteries
czars
Registered Users Posts: 16 ✭
Does anyone have a suggestion about how to properly size a 48v battery bank for a 4500 grid-tied inverter?
Comments
-
Re: Sizing Batteries
What setup are you asking about? A Xantrex 4.5kW 48 volt Hybrid Inverter setup?
The normal recommendation would be 450 AH @ 48 volt minimum battery bank to support the maximum charging/load surge currents.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Sizing Batteries
You guessed correctly - Xantrex XW4548. Thanks for your input. -
Re: Sizing Batteries
A common mistake is only sizing for the backup condition.
The requirement is not only based on what the inverter load ( AC out ) is but what the load to the grid in sell mode can be ( AC in 1 ) as the inverter is bi-directional.
Which ever is greater load ( selling to the grid OR backup load ) the battery bank minimum needed is 100ah @ 48V nominal bank voltage per kW
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed