Using Load center for BOTH 120v and 12v?
santaigo
Registered Users Posts: 22 ✭✭
[IMG][/img]
Here is a SquareD QO 100 amp load center with two hot busses and 6 slots. In a small off grid system, is there any reason why I can't make one bus (top in the photo) 120v and the other bus as breakers form my two PV (195 watts, 12 v, 13 amp each).
Square D help line says that the breakers for this box will handle up to 48 volts DC. In essence, this would be my "fused-combiner" box for the two panels and still have three 15 amp circuits for the cabin, which is plenty.
When I essplained all this to the help guy at Square D he was quiet for some time and finally said "well, I can't recommend you do this, and it won't pass inspection but probably will be fine".
Will this work??:roll:
Here is a SquareD QO 100 amp load center with two hot busses and 6 slots. In a small off grid system, is there any reason why I can't make one bus (top in the photo) 120v and the other bus as breakers form my two PV (195 watts, 12 v, 13 amp each).
Square D help line says that the breakers for this box will handle up to 48 volts DC. In essence, this would be my "fused-combiner" box for the two panels and still have three 15 amp circuits for the cabin, which is plenty.
When I essplained all this to the help guy at Square D he was quiet for some time and finally said "well, I can't recommend you do this, and it won't pass inspection but probably will be fine".
Will this work??:roll:
Comments
-
Re: Using Load center for BOTH 120v and 12v?
Will it work?
Short answer is yes.
Should you do it?
Absolutely not. In my opinion there is way to much chance for really bad things to happen here to save 20 bucks or so. -
Re: Using Load center for BOTH 120v and 12v?
Half beat me to the punch. If you are CAREFUL, should work. It is NOT code. I would not do it.
Midnite offers very affordable breakers, and small boxes, like the 'Baby' box and the 'Big Baby' (IIRC), which could perform the indoor combiner box duty. These are sold by the host of this fine site at very reasonable prices.
The DIN Rail breakers used in these boxes have screw terminals for both the input and output wiring, which I much perfer over the push-on-bus connections in most consumer grade load centers.
Good Luck, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Re: Using Load center for BOTH 120v and 12v?
For $ 18.77 would get a second load center. When, not if, you mix up 12 & 120 source. You are going to do more than $ 20.00 in damaged.
I am using one as my battery/solar/charger combiner. -
Re: Using Load center for BOTH 120v and 12v?
Thanks guys - I kind of assumed this was a bad idea - I'll get another load center to act as my combiner box.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed