No power at night
castilloj
Solar Expert Posts: 208 ✭
I have a fx2524 connected to 8 rolls s600 batteries, and i run my 11kw generator from 8 am to noon. From noon till 6pm i use my inverter for power. then from 6pm till 10:30pm i run the generator again.
lately ived been having problems like when i switch to inverter power at night. The PV/Output Breaker in My E-panels trip, causing the house to not have power at night.
The thing is that it only happens at night not during the day. any suggestions?
Also i have another question im using 8 s600 batteries on a 24 volt system. i only have one inverter, and when i talked to Rolls they mentioned that i would need to have around 25-28 amps AC to properly charge 2 strings of batteries. My question is could i just use 4 of the batteries and still get the same ammount of power at night? and have the batteries get a real charge?
Re: No power at night
Let's see, Rolls s600 is 6 Volt, 450 amp hour.Eight of them in a 24 Volt configuration would be two strings of four parallel for 900 Amp hours. That's about 10 kW hours of power. Lot's of capacity for off-grid. But it's going to require lots of charging.
Outback VFX2524 has only a 55 Amp charger - pretty slim for that much battery. Having 11 kW of generator is irrelevant as the inverter itself will only draw about 1600 Watts. Add maximum load capacity (2.5 kW) and you've got more than twice the generator you need, so to speak.
The big question is; what are the loads you're trying to supply?
Also, check the SG on the batteries to see if they are getting charged fully. Check the charge setpoints on the inverter as well, including Absorb time.
Is there any PV on this set up? If so, how much and what charge controller?
It's odd that the breaker would trip out. Usually the inverter faults from overload or low Voltage first.
Please supply us with some more system details so we can get a better feel for how it should operate and figure out why it doesn't. -
Attachment not found.I use about 6 amps AC from 11pm till 8 am. running a tv,satellite dvr , 3 ceiling fans,internet modem, and 2 box fans.
I have 8 photowatts pw-1000 and 8 Astropower AP-120
also ive never know excatly what to set charge setpoints or float. so i just left them on the default setting.
i also have solar panels which right now at 11:32 am im getting: -
6 Amps @ 120 Volts = 720 Watts. Times nine hours = 6480 Watt hours.
Are you sure? That's a pretty healthy consumption. More than half the available Watt hours.
Eight Astropower @ 120 Watts each = 960 Watts.
The Photowatts seem to be 100 Watts each so that's 800 Watts.
Grand total of 1760 Watts. Derated 1355 Watts, divided by 28.4 Volts = 47 Amps. A minimal charge current for 900 Amp hours of battery but doable (depending on loads).
But if you look at the "harvest" you get something like this: 1355 Watts * 4 hours = 5420 Watt hours.
I'd run PV Watts to check potential in your area. http://rredc.nrel.gov/solar/calculators/PVWATTS/version2/
With the additional generator charging, however, it should make it.
Definitely need to check the Absorb Voltage set point and the Absorb time. As well as the batteries' SG. It looks a bit like undercharging. Providing we're looking at the right fault. If the breaker is tripping but the battery Voltage remains high, then perhaps their is a wiring fault or some load assignment it can't handle.
P.S.: I can't actually see the attachment on my netbook. There may be a vital clue lurking in the data there. -
absorb setpoint-28.8
absorb time limit-1.0 hrs
Float setpoint-27.2
float time limit-1.0- hrs
refloat setpoint-25.0 vdc
EQ-28.8
Eq time-1 hrs
Batteries are at 25.21 vdc
right now using 5.0 aac
batteries are :
1.225/1.225/1.225 --1.225/1.225/1.250--1.225/1.100/1.225--1.225/1.210/1.210
1.225/1.210/1.225-- 1.210/1.210/1.210--1.225/1.225/1.210--1.210/1.210/1.210
Array Voltage-49.27v
Array Current-24.5 amps
sweep VMP-49.27
Sweep VOC-67.09
Sweep Pmax-1182 watts
Battery Volatage- 25.68
Target Voltage -30.61
Charge current-36.8 amps
output power-1170watts -
Re: No power at nightcastilloj wrote:1.225/1.225/1.225 --1.225/1.225/1.250--1.225/1.100/1.225--1.225/1.210/1.210
Big problem there... May be a bad cell/battery. That cell is pretty much dead and even if you get it recharged, it still may not last very long.
That can cause its string to over charge and the parallel battery string to undercharge/discharge with light loads on the system.
Should i just use 4 batteries in series? -
1 hour in absorb is too little in my opinion. Since you're running on the generator, I'd increase this to around 3 hours to make sure you're properly charging.
Too little time in absorb = sulfation = premature battery death
Too much time in absorb = more water use -
Ok i just changed absorb to 3 hours.
- 886 Solar Product Reviews & Opinions
- 651 Solar Water Pumping
- 608 Discussion Forums/Café
