Resistive load
greenthumb76
Solar Expert Posts: 40 ✭
Could someone please explain (or point me to an explanation) of what problems there are with a modified sinewave inverter and a resistive load?
Thanks!
Thanks!
Comments
-
Re: Resistive load
Typically, no problems with MSW inverters and resistive loads (filament lamps, electric/resistance heaters, etc.)--Other than the large amounts of power resistive loads (typically heaters) vs what can be supplied by other fuel sources (fuel, solar thermal, wood, etc.).
Do you have some specific application you wish to support?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Resistive load
Green thumbs I am going to try give simple explanation as to the difficulties of certain resistive loads.. this example it not a scientific one .ok??
ok you have a electric wood bench saw ,, now when you start it its not under much load .ok? its only under load and drawing a lot of current when actually cutting the wood.
so its on load time is most likely less than its off load time . so while the motor gets hoter when under load it self cools with its built in fan when not in use.
Now lets take a stove element its cold load is high it settles as it heats up BUT it is drawing its full rated power the whole time its on, (for this example its on HIGH ) OK? Cheap inverters are not designed to provide power to such devices. Have a look at any available ones the fans are too small and the usual aluminium case is too small to disipate the heat.., that is why a 1000 w inverter is unhappy with heater elements above 500w,, If you really want to get an inverter designed for heavy duty use you need to look at industrial inverters..but at 3 to 4 times the price for same size.. -
Re: Resistive load
Yes--what John says--Inexpensive inverters are not usually very happy running near 100% load for extended periods of time (100% power for minutes/hours is virtually impossible when running a skill saw--very easy with a heating element/resistive lighting load/etc.).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Resistive load
I had a different post, regarding the fuse size needed, based on having a 1500watt /3000 peak MSW inverter. I wanted to run my 1200 w toaster oven (at about 350F for 5-10 minutes) or my 1000w bucket heater for 10-15 minutes. (With about 200 amp hours of batteries, and 70 watts of solar panels, I obviously would not be doing this very often.) I was told the inverter would not like this. I was curious as to the reasons why. -
Re: Resistive load
I am going to run a lot of math by you as way of explanation of the issues. It is all pretty straight forward, and uses typical derating factors that give good results.
Usually it is much less confusing to present a set of requirements (Watts*Hours per day; location, and seasonal use--summer vs winter) to give a balanced system design.
What I have done below is sort of backwards, showing what would be required (roughly) to meet your needs--And showing how your existing setup would have issues running the desired loads.
If this is too confusing--Let us know and we can figure instead design a system that would support your needs (I.e., in Northern Nevada, need solar 9 months of the year to run a 1,200 watt toaster oven for 20 minutes per day without using a generator).greenthumb76 wrote: »I had a different post, regarding the fuse size needed, based on having a 1500watt /3000 peak MSW inverter.- 1,500 watts * 1/10.5 volt cutoff * 1/0.85 eff * 1.25 fuse/wiring safety factor = 210 amp fuse / breaker / wiring
And, inexpensive inverters (and some expensive ones) actually have problems running over 80% of rated load for any length of time.
And high loads on a 12 volt battery bank is very difficult--Run the battery down to 11.5 volts (less than full charge, and voltage drop from heavy loads), gives you a 1.0 wiring drop for typical inverter with 10.5 volt cutoff.I wanted to run my 1200 w toaster oven (at about 350F for 5-10 minutes) or my 1000w bucket heater for 10-15 minutes.- C/10 to C/20 are efficient loads
- C/8 is about the maximum continuous load (battery may overheat on load or charging in excess of C/8)
- C/2.5 is about the maximum surge current supported by flooded cell batteries--More current and you may collapse the battery voltage
- 1,200 watts * 1/10.5 volts * 1/0.85% = 134.5 amps
- Capacity (20 Hour Rate) = 134.5 amps * 20 (5% discharge rate) = 2,690 AH
- Capacity (20 Hour Rate) = 134.5 amps * 10 (10% discharge rate) = 1,345 AH
- Capacity (20 Hour Rate) = 134.5 amps * 8 (12.5% discharge rate) =1,076 AH
- Capacity (20 Hour Rate) = 134.5 amps * 2.5 (40% discharge rate) =336 AH
If you have AGM batteries, some of them can support upwards of C*4 current:- Capacity = 134.5 AH / 4 (400% discharge rate) = 33.6 AH
Note that this would fully discharge the battery in 15 minutes--This is UPS type loading--Can be done, but probably not a good choice for daily use (running battery dead is never a good idea).(With about 200 amp hours of batteries, and 70 watts of solar panels, I obviously would not be doing this very often.) I was told the inverter would not like this. I was curious as to the reasons why.- 70 watts panel * 1/14.5 volts charging * 0.77 efficiency * 1/0.13 charge rate = 28.6 Amp*Hours @ 12 volts minimum battery capacity
- 70 watts panel * 1/14.5 volts charging * 0.77 efficiency * 1/0.05 charge rate = 74 Amp*Hours @ 12 volts
- 200 AH battery * 14.5 volt charging * 1/0.77 derating * 0.05 rate of charge = 188 watts of solar panel minimum
- 200 AH battery * 14.5 volt charging * 1/0.77 derating * 0.13 rate of charge = 490 watts of solar panel maximum
- 70 watts * 4 hours of sun per day * 0.52 derating = 164 Watt*Hours per day
- 164 Watt*Hours per day / 1,200 Watt Load = 0.137 Hours per day = 8.2 minutes per day
There are a lot of reasons why what you asked for is difficult to do... Solar power is expensive and, typically, for simple heating projects, a solar thermal heating setup (insulated bucket with south facing plastic panel to let sunlight in to heat bucket) would probably work better.
And for running a toaster oven--a 20lb tank of propane will last you quite a while running a little catalytic oven.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Resistive load
Green thumb I thought I explained it in this thread post#3
put simply again the inverter is just going to overheat. it will then either shut down or do a melt down.. lack of large enough case on inverter to dissipate the heat and inadequate fans -
Re: Resistive load
John--Thank you for your help. Please don't get all bent out of shape. I'm answering Bill's question:
Do you have some specific application you wish to support?
-Bill
Bill--thank you so much for taking the time to explain this all, especially with the numbers that pertain to my system! It gives me what I need to know in terms of expanding my system, or learning to live with what I've got. -
Re: Resistive load
sorry greenthumbs just thought you not understood so was trying to be helpful..:cool:
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed