Proposed small system
ScottBarMtn
Registered Users Posts: 6 ✭
Here's the situation: The solar project that I am planning is for a workshop that is not grid connected. It is across the creek and down a ways from my house (which is connected to the grid). For a number of reasons, it is not feasible to run grid power to the workshop. I would call it a small system, with the goal of being able to run lights inside for working, and a few small power tools. For those times when I need to power heavier equipment or I have a big project going, the fall-back plan will be to fire up a generator for power.
Typical power needs, on a daily basis. If I need more power than this, I would plan to run a generator:
- Two 55 watt 12 volt halogen light fixtures running 6-8 hours per day (no inverter needed for these...)
- Occasional use of small tools (drill, etc.) during the day. Maximum 7 amp 120 volt motor for one hour per day. I would turn on the inverter only when I use a tool.
Proposed system:
- Solar Panel: One of Kyocera KD135SX-UPU - 135 Watt, 12 Volt Solar Panel (Junction Box)
- Charge Controller: Xantrex 12 Amp, 12 Volt Charge Controller
- Batteries: Two of Trojan T105-RE 6 Volt, 225 AH Deep Cycle Battery
- Inverter: Samlex 1500 Watt Pure Sine Wave Inverter 115 volt AC output, 12 volt DC input
- Charger: Xantrex Truecharge2 12-Volt, 20-Amp Battery Charger
- Battery sensor: Xantrex Battery Temperature Sensor, 15 foot cable
- One kill-a-watt meter for AC
- Two DC amp-hour/watt-hour meter (one between panel and battery, one between battery and inverter)
- Generator: Existing Dayton 3000 watt generator (may buy a generator/welder as backup)
- Estimated cost: A little less than $2000
Questions
- Do you see any weak links in this configuration?
- What is the difference between an electronic-based inverter like the Samlex, and a transformer-based inverter like the Outback? Will I regret buying the Samlex?
- Could I get by with a 1000 watt inverter?
- Any other suggestions? Cost is a consideration...
Typical power needs, on a daily basis. If I need more power than this, I would plan to run a generator:
- Two 55 watt 12 volt halogen light fixtures running 6-8 hours per day (no inverter needed for these...)
- Occasional use of small tools (drill, etc.) during the day. Maximum 7 amp 120 volt motor for one hour per day. I would turn on the inverter only when I use a tool.
Proposed system:
- Solar Panel: One of Kyocera KD135SX-UPU - 135 Watt, 12 Volt Solar Panel (Junction Box)
- Charge Controller: Xantrex 12 Amp, 12 Volt Charge Controller
- Batteries: Two of Trojan T105-RE 6 Volt, 225 AH Deep Cycle Battery
- Inverter: Samlex 1500 Watt Pure Sine Wave Inverter 115 volt AC output, 12 volt DC input
- Charger: Xantrex Truecharge2 12-Volt, 20-Amp Battery Charger
- Battery sensor: Xantrex Battery Temperature Sensor, 15 foot cable
- One kill-a-watt meter for AC
- Two DC amp-hour/watt-hour meter (one between panel and battery, one between battery and inverter)
- Generator: Existing Dayton 3000 watt generator (may buy a generator/welder as backup)
- Estimated cost: A little less than $2000
Questions
- Do you see any weak links in this configuration?
- What is the difference between an electronic-based inverter like the Samlex, and a transformer-based inverter like the Outback? Will I regret buying the Samlex?
- Could I get by with a 1000 watt inverter?
- Any other suggestions? Cost is a consideration...
Comments
-
Re: Proposed small systemScottBarMtn wrote: »Typical power needs, on a daily basis. If I need more power than this, I would plan to run a generator:
- Two 55 watt 12 volt halogen light fixtures running 6-8 hours per day (no inverter needed for these...)
- Occasional use of small tools (drill, etc.) during the day. Maximum 7 amp 120 volt motor for one hour per day. I would turn on the inverter only when I use a tool.- 2x55 watts * 8 hours per day + 120 volts * 7 amps * 1 hour per day = 1,720 Watt*Hours per day
Anyhow--Assuming you are sort of near Medford Oregon (weather wise inland a bit), using PV Watts website, 1kW panel (even number), 0.52 system efficiency, fixed array:"Station Identification"
"City:","Medford"
"State:","Oregon"
"Lat (deg N):", 42.37
"Long (deg W):", 122.87
"Elev (m): ", 396
"PV System Specifications"
"DC Rating:"," 1.0 kW"
"DC to AC Derate Factor:"," 0.520"
"AC Rating:"," 0.5 kW"
"Array Type: Fixed Tilt"
"Array Tilt:"," 42.2"
"Array Azimuth:","180.0"
"Energy Specifications"
"Cost of Electricity:"," 7.2 cents/kWh"
"Results"
"Month", "Solar Radiation (kWh/m^2/day)", "AC Energy (kWh)", "Energy Value ($)"
1, 2.33, 34, 2.45
2, 3.43, 47, 3.38
3, 4.99, 74, 5.33
4, 5.53, 78, 5.62
5, 6.35, 92, 6.62
6, 6.42, 87, 6.26
7, 7.25, 99, 7.13
8, 7.14, 98, 7.06
9, 6.34, 86, 6.19
10, 4.91, 72, 5.18
11, 2.44, 34, 2.45
12, 1.92, 28, 2.02
"Year", 4.93, 828, 59.62- 47 kWH per month / 30 days per month = 1.567 kWH = 1,567 WH per day
- 1,720 WH per day loads / 1,567 WH per day per 1,000 Watt of panels = 1,098 watts of panels
Battery bank wise, we recommend 3 days of no sun, and a maximum of 50% discharge--For a work shed (not used every day)--You might go as low as 1 day of no-sun and 50% maximum battery discharge (assume 12 volt battery bank):- 1,720 WH * 1/12 volt battery bank * 1/0.85 inverter efficiency * 1 day of no sun * 1/0.50 max battery discharge = 337 AH minimum @ 12 volts
- 1,720 WH * 1/12 volt battery bank * 1/0.85 inverter efficiency * 3 day of no sun * 1/0.50 max battery discharge = 1,012 AH maximum @ 12 volts
Proposed system:
- Solar Panel: One of Kyocera KD135SX-UPU - 135 Watt, 12 Volt Solar Panel (Junction Box)- 135 Watt panel * 3.43 Hours of sun * 0.52 system eff = 241 WH per day (February)
- Charge Controller: Xantrex 12 Amp, 12 Volt Charge Controller
- Batteries: Two of Trojan T105-RE 6 Volt, 225 AH Deep Cycle Battery
- Inverter: Samlex 1500 Watt Pure Sine Wave Inverter 115 volt AC output, 12 volt DC input
- Charger: Xantrex Truecharge2 12-Volt, 20-Amp Battery Charger
- Battery sensor: Xantrex Battery Temperature Sensor, 15 foot cable- One kill-a-watt meter for AC
- Two DC amp-hour/watt-hour meter (one between panel and battery, one between battery and inverter)- Generator: Existing Dayton 3000 watt generator (may buy a generator/welder as backup)- Estimated cost: A little less than $2000
Depending on what your actual sun availability and power needs (I may be 20% on the conservative side)--Your panels may cost you $2-$3+ per watt--so that would be $2-$3k+ just for solar panels. Obviously, for ~7 months of the year, a system with 1,100 watts of solar panels will generate way more than 1,098 WH per day.Questions
- Do you see any weak links in this configuration?
- What is the difference between an electronic-based inverter like the Samlex, and a transformer-based inverter like the Outback? Will I regret buying the Samlex?
- Could I get by with a 1000 watt inverter?
- Any other suggestions? Cost is a consideration...
Not sure which inverter to recommend yet--Need to understand AC loads more. Certainly, you are comparing less expensive against more expensive inverters--It sounds like the less expensive inverter would meet your needs.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Proposed small system
Wow - Excellent information that you have provided! I will take some time and rethink both my power needs, time of year, expected costs, etc, and will come back to this forum when I have a revised plan.
Thanks,
Denver -
Re: Proposed small system
After giving this some thought, I am coming to the conclusion that solar may not be a good solution for what I need.
Most of the work that I do in the workshop is typically done with these new generation of rechargeable tools using lithium batteries (e.g. Makita). They last a long time, and when recharge is needed it only takes about 20-30 minutes. When I need to use something like a drill press or table saw occasionally, it is no big deal to fire up the generator.
So that leaves indoor lighting as my main need for solar power. Unfortunately, the time that I need this most is in the winter when it is too stormy or cold outside to open the doors and let in the light, but this is exactly the same time when the solar potential is at its lowest where I live. The place does have creek running through it, which runs strong in the winter, so for my case some type of mini-hydro might be a better renewable source of power.
As a result, for the short term I am leaning toward simply purchasing the Makita work lights that use the same type of lithium battery. And perhaps one of these new breed of economical generators (e.g. Honda eu2000) for when I need the extra light or power.
Anyway, I appreciate the outstanding advice that is given on this forum - it saves a lot of wasted effort and money to say the least, and it is a pretty good way to learn all about solar.
Denver -
Re: Proposed small system
Welcome to the solar forum anyway.
Hope to hear more about a hydro project from you... We do not get a lot of those here and it would be neat to see what you come up with.
Sorry about the solar--Lots of power requirements in the winter really does make solar pretty difficult to justify.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed