Combiner Box
With54
Registered Users Posts: 21 ✭
I came across this article on the web about building your own combiner box from an AC Breaker Panel (http://www.freesunpower.com/project1.php) using 15 amp AC breakers. Is this safe? Will any 15 amp AC Breaker do the job?
Thank you for any information.
Thank you for any information.
Comments
-
Re: Combiner Box
Some Ac breakers are rated for DC ... most are not! Unless you have the parts lying around; it would be cheaper and safer to buy a UL listed combiner box. -
Re: Combiner Box
Just a few comments on that use of AC rated panel. He shows several bad examples of poor workman-ship.
As a minimum if you are going to do this and you need a outdoor rated box get one, they are available in the stores, don't use silicone to try and make it raintight.
Don't run wires thru box knockouts with a raintight box connector if outside or at least a proper box clamp if used indoors.
Don't mix color codes on the wires, NEC say's black would be "Hot" or positive and white would be neutral or negative. If you are off grid and will never be inspected can do what you want but at least mark them for what they are.
Be sure and correctly size the wire's for the current they will carry. Jumper from buss #2 to #1 buss will carry the combined current of breakers that use it.
Getting DC rated breakers is questionable at best.
Best advice has been given and that is to get a Rated Combiner-box and appropiate DC rated breakers or fuses and be safe.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Combiner BoxJust a few comments on that use of AC rated panel. He shows several bad examples of poor workman-ship.
Yea he does. Horrible.Don't mix color codes on the wires, NEC say's black would be "Hot" or positive and white would be neutral or negative.
That's for AC. For DC common usage would be black for negative and {some other color - usually red or white} for positive.
NEC doesn't really specify colors for hot (other than phase labeling black/red/blue) - it specifies colors for neutral and ground, but pretty much any color that isn't neutral or ground is fine for hot. -
Re: Combiner Box
So by what you just said that White or gray is for neutral or grounded conductor and not positive.
So the earliest NEC dealt with DC, including
color coding for conductors that still holds today. If the
conductor is a grounded circuit conductor, the insulation or
marking on larger conductors must be white or gray. If the
conductor is an equipment-grounding conductor, it must
have green or green with yellow-striped insulation—or be
bare. Ungrounded conductors may be any color other than
the ones listed above, with black and red being the most
common in the field.
so red could be OK for positive but not with a White Input from the solar panels switching to Red. If nothing else stay consistant is what I meant by my statement. He is using White for and ungrounded conductor! HOT from the panels.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Combiner Box
Wow this guy should be in jail. I love his way of sizing wire and his blatant disregard for safety let alone the NEC I absolutely despise people that reverse white and black like he did that is a death waiting to happen when someone uses the right color code down stream and gets electrocuted from the white supposed grounded conductor that they made hot. -
Re: Combiner BoxSo by what you just said that White or gray is for neutral or grounded conductor and not positive.
Again, that's for AC. There is no neutral in DC.So the earliest NEC dealt with DC, including
color coding for conductors that still holds today. If the
conductor is a grounded circuit conductor, the insulation or
marking on larger conductors must be white or gray. If the
conductor is an equipment-grounding conductor, it must
have green or green with yellow-striped insulation—or be
bare. Ungrounded conductors may be any color other than
the ones listed above, with black and red being the most
common in the field.
so red could be OK for positive but not with a White Input from the solar panels switching to Red. If nothing else stay consistant is what I meant by my statement. He is using White for and ungrounded conductor! HOT from the panels.
That's what I'm saying - for DC it's black that is normally used for negative (even if it is a "grounded conductor") - not white or gray.
So white for positive is okay in DC wiring, and that is how it's often done. For a DC circuit, using a cable with say a black, white and green - green is ground, black is negative. What's that leave for the positive?
As far as I know the NEC doesn't specify. Wiles has recommendations, but it's not consistent - on one he uses white for negative, on another black.
Consistency would be great, and they'll probably get around to fixing it in the NEC.
EDIT: Also, there are lots of low-voltage cables out there. They are commonly black (for -) and black w/white stripe (for +). Take a look at 12/2 Malibu lighting wire - it's all black, but one strand has a raised stripe (a ridge all the way down). That ridge is the same as the white stripe - it's to signify positive (or hot). -
Re: Combiner Box
NEC by definitions in Article 100 definitions of Grounded and ungrounded conductors and Section 200.6 of NEC, 310.10 (a) grounded conductor, 310.10 (c) ungrounded conductor. These cover both AC and DC systems.
Grounded conductor does not necessarly mean one going to earth/ground. In case of a (-neg) ground system the negative would be colored white or gray. Could be a black wire marked with white tape etc.
Ungrounded conductor (+Pos) could be red or any other color other than white or gray.
This would be reversed if you were using a Positive ground system such as some panels are. (+pos / White or Gray), (-neg black/red etc)
Automotive and other equipment can use what colors they want as they are not covered by the NEC as PV systems are, Stand-alone or on grid are no different.
Correctly colored tape at the ends of the wires and/or tape labels identifying them as either + or - DC would help someone from getting hurt or killed from incorrect contact.
Back to my orginal concerns was that this web site shows very poor workmanship, multiple code violations and the improper use for location and type of equipment, and people are using it to make installations at there own sites. I have seen post here were people have purchased equipment, installed it and can't read a Digital Volt Meter. If they would ask for help first as many do, it would save lots of injuries and burnt-up equipment.
We should all strive to keep this as safe as possible!!GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Combiner Box
The NEC specifically addresses ac or dc conductors. Any one installing a PV system should have a grasp on simple color coding or hire an electrician in my opinion. I have seen crap like the linked combiner on grid tied systems running at 500vdc and it really burns my you know what. Someone could get killed or seriously injured if they assume the white is a grounded conductor as NEC says it is. -
Re: Combiner Box
I think the problem is most peoples experience with DC is automotive or computers. Cars typically have black and brown as ground and other colors as positive.
It gets really confusing in my motorhome where the chassis electrical system has black ground wires and the coach side has white with black as positive.
I do agree with most of you. It is better to use the parts designed for the application. I've been down that road before. Call it a noob tax. -
Re: Combiner Box
The nice thing about standards is that there's so many of them. From my 30+ years of industrial electronics and electrical work, I've learned colors on wires don't mean a lot even on the AC power side. Always check an unfamiliar circuit with a good meter and label it.
The NEC codes are great but still allow for totally ungrounded power circuits without even a neutral to exist. So be careful, a hack job can get you killed. -
Re: Combiner Box
Well, I don't see anything in 310.10 about DC, and I can't seem to find Article 100 on the net. My local library doesn't have the NEC so I'd have to have it sent over from another branch (and only one has 2005, all the rest are older) which would take days at least.
However, I do find that the NEC color code applies to grounded systems, but not to ungrounded systems.
I also find that there is some debate on whether or not the PV system falls under the definition of "premises wiring" - if it does, then NEC applies, if it doesn't then NEC does not apply.
In any case, I'll refer to Wiles:
"If the PV system were an ungrounded 12 volt PV
system, the NEC has nothing to say about the color of the
insulation on the two ungrounded conductors."
http://www.nmsu.edu/~tdi/pdf-resources/cc99.pdf
But not just 12v:
"Twelve and twenty four volt PV systems have open circuit voltages
less than 50 volts and therefore are not required to have one
conductor grounded."
"The local inspector will be looking for that green or bare grounding
conductor in all PV systems and a white grounded conductor in
those over 50 volts or those which are grounded below 50 volts."
http://www.nmsu.edu/~tdi/pdf-resources/cc18.pdf
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed