Trojan L16Re-2 volt Batteries
andyrud
Solar Expert Posts: 70 ✭✭
My 6 six year old Interstate 380 amphour L16 batteries need changing. I am thinking about using 6 of the 1110 amphour Trojan 2 volt batteries in series. What is the general feeling about these batteries? To go from Interstate batteries to Trojan 2 volt batteries is about $600.00 more. I am willing to pay it if it is worth it, but need some opinions.
thanks in advance,
A new member, Andy
thanks in advance,
A new member, Andy
Comments
-
Re: Trojan L16Re-2 volt Batteries
If I'm reading this right, you have three parallel banks of 2 in series 6V 380 Amp/hr batteries for a total of 1140 Amp/hrs @ 12 Volts?
Trojan batteries are excellent, and putting in "all in series" instead of "three in parallel" is always a good idea for such a large capacity bank.
Curiously, I went from Trojan batteries to Interstate and was dissatisfied with the quality of the Interstates. Thus I'm going to switch back to Trojan. :roll: -
Re: Trojan L16Re-2 volt Batteries
Hi Andy!
First, regarding your current vs proposed battery bank capacity...
That is 3x the capacity of your current battery bank. Do you have enough solar panels + battery charger + backup genset to keep the bank fully charged. [Oops--My mistake--The old and new banks are about the same AH capacity]
As a starting point, we use a 5-13% rule of thumb based on the 20 Hour AH bank capacity...- 1110 AH * 0.05 = 55.5 amps ~minimum charge rate
- 1110 AH * 0.13 = 144 amps ~maximum useful charge rate
- 55.5 amps * 14.5 volts charging * 1/0.77 system derating =1,045 watts minimum solar panels (without using genset)
- 144 amps * 14.5 volts charging * 1/0.77 system derating =2,711 watts reasonable maximum solar panels
- 1,110 AH / 6 = 185 AH per day at 12 volts
- 185 AH * 12 volts = 2,220 Watt*Hours per day
Once you have decided on a workable bank capacity--then look at the cells to meet your needs.
But yes, I really like large cells in a single string vs a bunch of 12 batteries all connected in parallel.
Also, as you system grows, you should be looking at your total peak power needs... Generally, running more than 1,200 watts through a 12 volt bank or 2,400 watts through a 24 volt bank means some very large currents...
You may want to look at the inverter/charge controller/etc. side of the 12/24/48 volt question too.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Trojan L16Re-2 volt Batteries
Thanks for the reply Bill. My battery bank is about the same amphour size, 380 amphours times three = about 1140 amphours. My average daily wattage is about 2500 watts. I have about 1000 watts of 12 volt panels through a Morningstar TS 60. The Morningstar is maxed out as a few times the current went over 60 amps. Do you think the Trojan 2 volt batteries are enough? My delema is that if they are not I would have to buy another complete set of six to add additional amphours where with the 6 volt Trojans I could just buy two more to add additional amphours. ( if added within a year) What do you think?
Thanks again,
andy -
Re: Trojan L16Re-2 volt Batteries
Andy,
Oops--My mistake on your current battery bank size... Yes, they are about the same size.
From a basic sizing point of view--your system meets the minimum size of the rules of thumb for solar panels, and is right in there for bank capacity vs daily usage.
I am guessing that 6 years from your existing bank/vendor is a good life--So you seem to be taking pretty good care of your battery bank.
Where are you located? If you are on the coast south of San Francisco--There are lots of micro-climates that can vary the amount of sun you will receive.
On the coast, you might get 4 days of fog and 2 days of sun in the summer (or even less). Go back a mile+ in the valleys, and you can get very nice warm and sunny weather.
Using PV Watts and SFO, 1 kW of solar panels, 0.52 derating (all losses together), fixed mounting, tilted at latitude:"Station Identification"
"City:","San_Francisco"
"State:","California"
"Lat (deg N):", 37.62
"Long (deg W):", 122.38
"Elev (m): ", 5
"PV System Specifications"
"DC Rating:"," 1.0 kW"
"DC to AC Derate Factor:"," 0.520"
"AC Rating:"," 0.5 kW"
"Array Type: Fixed Tilt"
"Array Tilt:"," 37.6"
"Array Azimuth:","180.0"
"Energy Specifications"
"Cost of Electricity:","12.5 cents/kWh"
"Results"
"Month", "Solar Radiation (kWh/m^2/day)", "AC Energy (kWh)", "Energy Value ($)"
1, 3.62, 54, 6.75
2, 4.59, 62, 7.75
3, 5.22, 79, 9.88
4, 6.11, 89, 11.12
5, 6.36, 95, 11.88
6, 6.47, 94, 11.75
7, 7.01, 105, 13.12
8, 6.67, 99, 12.38
9, 6.62, 95, 11.88
10, 5.41, 80, 10.00
11, 3.87, 55, 6.88
12, 3.35, 50, 6.25
"Year", 5.45, 958, 119.75
You will collect around 50 to 105 kWH per month (useful AC output of an inverter).- 50 kWH per month / 30 days per month = 1.67 kWH per day December
- 105 kWH / 30 = 3.5 kWH per day in July
With your system, your bank could easily manage upwards of 2.7 kWatts total of solar panels--but, again depending on your needs, that may be overkill/too expensive.
By the way, how are you monitoring your bank capacity and ensuring it is properly charged and not drawn down too much?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Trojan L16Re-2 volt Batteries
Bill, my cabin (off the grid) is in the mountains above Philo, Mendocino county. My residence is in Pacifica, San Mateo County. So you think the Trojan 2 volt batteries is the way to go?
Andy -
Re: Trojan L16Re-2 volt Batteries
Andy,
Spent the first 30 years of my life in Pacifica... Litterly we now live just over the hills now near El Camino (sunnier weather).
I would think they are a good match for your system. And you should get good life from them.
However, I am a Grid Tied guy (and not in the solar business)--So, others here can probably give you better first hand knowledge between Trojan, Surrette, etc. than me...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Trojan L16Re-2 volt Batteries
Assuming your usage estimate is correct:
2500 Watt hours / 12 Volts = 208 Amp/hours
At 50% DOD that's 416 Amp/hr battery bank. At 25% DOD it's 832, so the 1140 Trojans should be plenty.
Consider the advantages of the 2 Volt cells: fewer connections between batteries, fewer cells to check/water, and only one current path; in and out of all in a very equal manner.
I'd be concerned about charging, as with just one 60 Amp controller you're really undercharging what you've got now. This probably shortened the life by 3-4 years. The "tall case" batteries really do want a C/10 charge rate, as they are more likely to suffer from electrolyte stratification. That means you should have two 60 Amp controllers power by about 900 Watts each in order to achieve 100+ Amps of current.
Are you sure you need 2.5 kw hours a day? -
Re: Trojan L16Re-2 volt Batteries
Thanks for the reply Coot. For 6 weeks I ran the power used through a Kill a WAtt meter and the average was 2.5 Kw. I have a small swimming pool for the grandkids and an electric frig so that is where the power is being used daily. I thought I might need more panels. Would you suggest another Morningstar 60 amp or get rid of the one I have and get an 80 amp Outback MPPT Controller?
Andy -
Re: Trojan L16Re-2 volt Batteries
The 2v Trojan batteries are also a better deal than the Rolls 12CS11PS 357ah batteries by over 60%. The calculations: 330*6/1110=1.78, 1034*1/357=2.90. In other words, even if the Trojan batteries lasted 10 years instead of 15 years with the Rolls, you would still be ahead.
It was discussed awhile back, but hasn't anybody switched over to the large Thundersky lithium batteries? It would seem to require fewer cells even than the PbA chemistry, and the Depth Of Discharge can be about twice as much, and still get two thousand or so cycles. -
Re: Trojan L16Re-2 volt Batteries
Coot, I am confused about the charge current amount. Lets say the battery is fully charged. I start using 350 watts of power per hour.. Thats about 30 amps per hour used from the battery. Are you saying that 60 amps from my existing panels is not enough current to charge the battery? -
Re: Trojan L16Re-2 volt BatteriesCoot, I am confused about the charge current amount. Lets say the battery is fully charged. I start using 350 watts of power per hour.. Thats about 30 amps per hour used from the battery. Are you saying that 60 amps from my existing panels is not enough current to charge the battery?
It's the difference between being able to "put back the used Amp hours", which can be done over time at any charge rate exceeding the self-discharge rate, and charging at rate that will create enough "activity" in the cells to reduce the sulphation effects and stir the electrolyte. Trojan recommends a C/10 rate, which in this case is 111 Amps. That does not include deducting for power going out while charging. Net charge rate is Amps in minus Amps out, because none of us shut down our inverters while recharging the batteries. That would be silly!
In my opinion the best thing for you to do would be simply add another 60 Amp controller and panels to supply it so that the two array/controller set-ups add up to the 111+ Amps.
I just knew kids came into that power usage figure somewhere!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed