Wire Size Between Batteries
Re: Wire Size Between BatteriesIf I use the MPPT Morningstar Controller and add a remote display box, then do I need the shunt?
A typical Battery Monitor uses the shunt to measure current into/out of the battery bank. Those numbers are used to estimate the current state of charge of the battery bank.
Also, shunts+battery monitors tend to be much more accurate at measuring current flow than typical solar charge controllers.Is the shunt wired right after the batteries on the negative side?The Blue Sea Fuse you linked below, would go on EACH battery? So FOUR of them if I have FOUR batteries?The fuse I linked to would handle all the batteries after the lead comes off the battery, correct?
What size fuses on the batteries?What size fuses going to the inverter?
Note, you may have a 1,000 watt inverter and only plan on 500 watt loads--so you could fuse/wire based on 500 watt load limit.- 500 watts * 1/0.85 eff * 1/10.5 volts min batt * 1.25 NEC derate = 70 amp minimum wire+fuse rating
What size fuse going from the panels to the controller?
If you have 3 or more parallel strings of panels--then each panel string should have its own series protection fuse/breaker (fuse rating should be in data sheet). There are Combiner Boxes with lots of breakers for solar systems.
If your panel specs do not list a series protection fuse--then use a fuse at least 2x the Isc (short circuit current rating) of the panel (round up to next standard fuse size).
Couldn't have said it better myself,,, no really couldn't have!
T
PS The bluesea fuses are really clever, such that it makes a very clean installation with plenty of fuse protection. I wish I had know about them when I built my system.
- 230 Forum & Website
- 654 Solar Water Pumping