iota transfer switch and ground
bobdog
bobdog Solar Expert Posts: 192 ✭✭
I am looking into buying an automatic transfer switch for my set-up. The iota ITS-30R looks pretty good and my questions has to do with the ground from the generator. I have an old Honda 2500 watt gen and the neutral is not bonded. The gen itself has a little pigtail attached that you're supposed to clip to a ground but that's it. My inverter, Suresine 300 watt, has a true ground. So, is it going to work or will the different grounds be a problem? Thoughts?
Tim
    Re: iota transfer switch and ground
    I think you should be fine. The SureSine inverter should not care about grounding or not of the neutral.
    For the generator--is the Pig Tail the generator frame ground or the neutral bonding point?
  • bobdog
    It's the frame ground I believe. It is a fairly skimpy wire with an alligator clip attached and it is mounted to the generator head.
    Tim
    Unless you have some special application (telecom) or other safety related issues (lightning, other gensets in the area that may power common equipment)--I would just leave as is.
    If you are going to be using power tools in the rain--an AC Ground Fault Interrupter outlet or GFI extension cord might be nice.
    But here is where it is not a clear A > B choice... The SureSine (and your genset) is an isolated AC output. You cannot get shocked (or at least should not) by touching either lead and ground/earth/metal.
    If you ground the neutral (earth/metal), then you can get shocked if you grab the "hot lead". Now you need a GFI to protect you against Hot to Ground/Earth contact.
    Either method will give you fairly good protection against shock. If, option A (floating output)--one AC lead does get grounded (cut wire, in water--no indication of short), then you can get shocked by the other lead... So the GFI can be a nice safety / backup measure.