Grid Tie/Interactive Problems
solarpower2009
Registered Users Posts: 7 ✭
Hello,
We just installed a flexmax80 along with a gvfx3524 inverter and a battery bank. The flexmax80 works fine with the inverter. However, when we attach the inverter using AC in to the grid it works for sometime (8 minutes) and then trips the breaker between the batteries and the inverter. No problems with AC out. This has been happening repeatedly. Is there someone who has experienced the same problem? Any suggestions will be appreciated.
We just installed a flexmax80 along with a gvfx3524 inverter and a battery bank. The flexmax80 works fine with the inverter. However, when we attach the inverter using AC in to the grid it works for sometime (8 minutes) and then trips the breaker between the batteries and the inverter. No problems with AC out. This has been happening repeatedly. Is there someone who has experienced the same problem? Any suggestions will be appreciated.
Comments
-
Re: Grid Tie/Interactive Problems
What size circuit breaker? How long is the battery:inverter wire run and what gauge is it?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Grid Tie/Interactive Problems
The circuit breaker is 80 amp dc and the wire gauge 2 and is approx. 7 feet in length. The battery bank is a 24volt system. The AC panel end of the AC in wire goes through a 60 Amp AC breaker. Thanks for your help. -
Re: Grid Tie/Interactive Problems
How much GT power / off-grid peak power do you expect to output/use?- 80 amps * 24 volts * 0.80 efficiency = 1,500 watts
If I was defining the minimum wiring/breaker/fuse for full power operation of a 3,500 watt 24 VDC inverter:- 3,500 watts * 1/21 volts batt cutoff * 1/0.80 invtr eff * 1.25 NEC safety margin = 260 amp @ 24 VDC circuit rating minimum
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Grid Tie/Interactive Problems
Bill,
The whole system has been working fine for over 3 months. Problems started only when we hooked up the AC in connection. Right now the inverter is working fine (with the AC in breaker off) and running 3 fridges all the time and the basement bathroom lights including the upflush motor (intermitantly). I have not altered the battery bank in anyway. My system is 1 kw. -
Re: Grid Tie/Interactive Problems
Only thing I can think of is if something lost it programming--Or if this inverter has an internal charger--it is drawing more than 1,500 watts from the AC line to charge up the battery bank...
Circuit breakers can fail and false trip... If you have no indications of high current flow, it may just be a bad breaker.
That is about the limit of my knowledge.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Grid Tie/Interactive Problems
The breaker from the inverter to the batteries should be 250A DC, The wire size 4/0 or 120 mm ish, The charger will start a charge @ 85 ish amps when you connect AC in, An 80 amp breaker will take a while to go out at that, ( you should have 80a breakers either side of the FM)
Have a good one
Tim -
Re: Grid Tie/Interactive Problems
Hello BB and Blackswan555,
I will purchase that 250breaker right away. Thank you both for your prompt help. This forum is very helpful. -
Re: Grid Tie/Interactive Problems
Be sure to upgrade the wire size also , those inverters can easy pull 200 + amps ! If you need more specific details on setting it up to sell may also be worth an ask over on the outback forums http://outbackpower.com/forum/ they also have live help accsesable at the top of the page, ( IIRC 9pm > 1AM CET)
Have a good one
Tim -
Re: Grid Tie/Interactive Problems
And don't forget to address the wire--Fuses/breakers are to protect the wiring (and not really the devices).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed