"Line side" tap on sub panel for PV installation possible?
ggunn
Solar Expert Posts: 1,973 ✭✭✭
We have a customer who wants to install a substantial amount of PV on a ranch. The ranch is on a single meter with a 400A main feeding several subpanels and the PV inverter would be located at one of the subs...
I apologize for the edit here, but I misunderstood the question.
What we have is a 400A disconnect feeding multiple smaller disconnects which in turn feed subpanels. The rancher wants to install possibly as much as 35kW of PV out by one of the subpanels, which is probably 200A. Four SB8000's require a total of 160A OCP. The question is if we can combine the output of the inverters in an aggregation panel and tap into the 200A rated supply line feeding the 200A subpanel.
Sorry for any confusion.
I apologize for the edit here, but I misunderstood the question.
What we have is a 400A disconnect feeding multiple smaller disconnects which in turn feed subpanels. The rancher wants to install possibly as much as 35kW of PV out by one of the subpanels, which is probably 200A. Four SB8000's require a total of 160A OCP. The question is if we can combine the output of the inverters in an aggregation panel and tap into the 200A rated supply line feeding the 200A subpanel.
Sorry for any confusion.
Comments
-
Re: "Line side" tap on sub panel for PV installation possible?
this won't work for 35kw of pv for the most the 400a service can handle on the bus is 20% more for 80a. 80a x 240v = 19.2kw. if you put a smaller breaker for the main panel to account for the extra power he wishes to feed the grid, it may fly. -
Re: "Line side" tap on sub panel for PV installation possible?this won't work for 35kw of pv for the most the 400a service can handle on the bus is 20% more for 80a. 80a x 240v = 19.2kw. if you put a smaller breaker for the main panel to account for the extra power he wishes to feed the grid, it may fly.
-
Re: "Line side" tap on sub panel for PV installation possible?
ok, sorry for my misunderstanding and as far as i can see you should be able to go with up to the rating of the wire as the wire would carry the utility power and the output of the pvs. the wire would be acting like a bus technically.
maybe some of our linesmen in here can comment. -
Re: "Line side" tap on sub panel for PV installation possible?ok, sorry for my misunderstanding and as far as i can see you should be able to go with up to the rating of the wire as the wire would carry the utility power and the output of the pvs. the wire would be acting like a bus technically.
maybe some of our linesmen in here can comment.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed