AC disconnect sizing?
heynow999
Solar Expert Posts: 80 ✭✭✭✭
I have a 2.5kw central inverter system and I am adding a 3.3kw Enphase system. I need an AC (fused) disconnect which was not installed when my 2.5kw system was originally installed. I will have a breaker panel with a 15 amp 2 pole and 20 amp 2 pole breakers. I then need the disconnect between the breaker panel and the meter.
The 2.5kw needs a 15amp disconnect and the 3.3kw needs a 20amp discconnect. Will I have 15A and 20A on each phase so I need a 35A fuse in the dissconnect? Or will it be 30A on one phase and 40A on the second phase?
Thanks
The 2.5kw needs a 15amp disconnect and the 3.3kw needs a 20amp discconnect. Will I have 15A and 20A on each phase so I need a 35A fuse in the dissconnect? Or will it be 30A on one phase and 40A on the second phase?
Thanks
Comments
-
Re: AC disconnect sizing?I have a 2.5kw central inverter system and I am adding a 3.3kw Enphase system. I need an AC (fused) disconnect which was not installed when my 2.5kw system was originally installed. I will have a breaker panel with a 15 amp 2 pole and 20 amp 2 pole breakers. I then need the disconnect between the breaker panel and the meter.
The 2.5kw needs a 15amp disconnect and the 3.3kw needs a 20amp discconnect. Will I have 15A and 20A on each phase so I need a 35A fuse in the dissconnect? Or will it be 30A on one phase and 40A on the second phase?
Thanks
(5.80)(1000)/240 = 24.2A
(24.2)(1.25) = 30.2A
Next size up fuse is 35A. Same size fuse on both phases. -
Re: AC disconnect sizing?
Wouldn’t 220.5 (B) permit you to drop the fraction and use a 30 amp fused disconnect?
220.5 Calculations.
(B) Fractions of an Ampere. Calculations shall be permitted
to be rounded to the nearest whole ampere, with decimal
fractions smaller than 0.5 dropped. -
Re: AC disconnect sizing?
Yep, a single 30A disconnect should be OK - hard to say for sure without knowing exactly what the rating of your old inverter and how many Enphase inverters you have.
Otherwise 60A disconnect blade switches are readily available, though they might be a bit more expensive. -
Re: AC disconnect sizing?Wouldn’t 220.5 (B) permit you to drop the fraction and use a 30 amp fused disconnect?
220.5 Calculations.
(B) Fractions of an Ampere. Calculations shall be permitted
to be rounded to the nearest whole ampere, with decimal
fractions smaller than 0.5 dropped.
Good catch.
Now I have to go through all my electrical drawings and revise my OPD's.
Thanks a lot. ;^)
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed