My 24 panel KC120-1 solar array is 6 years old now and has not performed up to my expectations nor what I believe are the experiences of others.
Here is the current state of my solar array:
I have 24 KC120-1 panels.
The panels are in series in groups of 4. I.E. 48 volts per bank.
The panels that make up each bank are interconnected with 10 gauge wire.
Each bank of 4 is then routed via 10 gauge wire to an outback panel combiner.
From there 6 gauge wire leads to a C40 charge controller, and from there to a SW4048.
All of the wiring is inside sealed watertight conduit and fittings.
And here is the result after 6 years: http://home.worldcontrol.com/solar-output-20070812.html
The voltages are the open voltage from + to - on each panel, and the amperage is the amperage measured from + to - on each panel. Measured using the outer most screws.
The C40 measurements are via the C40 display panel. I turned off all the panels via the panel combiner breakers, then turned on one bank at a time and read the numbers from the C40 display panel.
Any thoughts on what might help this array produce better?
Here is the current state of my solar array:
I have 24 KC120-1 panels.
The panels are in series in groups of 4. I.E. 48 volts per bank.
The panels that make up each bank are interconnected with 10 gauge wire.
Each bank of 4 is then routed via 10 gauge wire to an outback panel combiner.
From there 6 gauge wire leads to a C40 charge controller, and from there to a SW4048.
All of the wiring is inside sealed watertight conduit and fittings.
And here is the result after 6 years: http://home.worldcontrol.com/solar-output-20070812.html
The voltages are the open voltage from + to - on each panel, and the amperage is the amperage measured from + to - on each panel. Measured using the outer most screws.
The C40 measurements are via the C40 display panel. I turned off all the panels via the panel combiner breakers, then turned on one bank at a time and read the numbers from the C40 display panel.
Any thoughts on what might help this array produce better?
Comments
-
Re: Help with my aged KC120-1 solar array
It is possible that your panels are part of a 2001 date code failure that Kyocera has been replacing (without much hassle) when people call them or the distributor... Check this Solar Guppy Thread for some details.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Help with my aged KC120-1 solar array
You apparently have a 4x6 array, with 4 panels in series x 6 panels in parallel.
#1. #10 wire is too small. You should have #8 as a minimum. #10 wire is only rated for 30 amps in free air (a little less in conduit), and you could be pushing up to 43 with that setup. And you are probably getting a fair voltage drop unless it is a very short run, even aside from the wires getting hot.
#2 What the previous poster said about some bad panels, contact Kyocera - you will need the serial numbers.
#3 The C40 is under rated for what you have. And you could also get over 60 amps out of those arrays with something like the Outback MX60. -
Re: Help with my aged KC120-1 solar array
Hi Snb ..
Just a couple of thoughts ...
1. Is this system Grid-tied, Off-Grid ?? Where is the PV power supposed to go ? During these measurments, what was the demand for PV power in excess of battery charging ? Selling to the grid ? AC loads on inverters ? So on ..
2. Assume that the second number for each of the panels is the Current, Isc, measured using a DMM on 10 Amp current scale ?
3. Wonder if you have a poor connection somewhere in bank 3 & 4.
4. What state C40 in when you took its ? If there is no demand for power in excess of that needed by your batteries, and the batteries are in Absorb, or Float, then you may only need the power shown on the C40 (which I am unfamiliar with--think 40 A PWM?). This system has been running 6 years, sorry for the lecture on that which you know.
5. Obviously, bank 6 does have some prob at the first panel in the table.
6. There does seem to be quite a large variation in the currents of each panel, more than I would guess, but have no experience with KC-120's, altho did not know that panels this large were available 6 years ago.
Some additional context would help ... where are you, type of system--Grid-tied etc, any panel shading at all, very humid (possibility of corrosion at connections) and so on.
VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Re: Help with my aged KC120-1 solar array
6 years = 2001 , many many many failed KC120's from that vintage and the reports still comming in from systems
Your test shows you have massive failures on two strings and some failures on two more, this would point to bad panels for sure
Call Kyocera ( use the link to my site which has contact info if you need it )
Kyocera will replace the entire array, whether they have failed yet or not -
Re: Help with my aged KC120-1 solar array
Simplest test to check for bad panels... Disconnect each panel and check Voc (voltage open circuit) and Isc (current short circuit).
To check Isc, just set the DVM to 10 amps max scale and connect to the solar panel +/- leads. In full sun you should get rated current, or a bit more. If significantly less--you have a bad panel (less than 80% rated current in noon time sun, clear sky, clean panels--for sure a bad panel).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Help with my aged KC120-1 solar array
Thanks for the info on the panel failures. Reading other threads on this subject my failure rate even matches that of others.
I will contact kyocera. Though I bought mine from Arizona wind & sun.
Is it preferred to contact kyocera directly?
Any particular number people a dialing? -
Re: Help with my aged KC120-1 solar array
I just talked with kyocera. All of my panels are from the bad time and
they are going to replace them. -
Re: Help with my aged KC120-1 solar array
By the way, I talked with Arizona Wind & Sun about my performance troubles about a year ago, and they did not mention "this" problem. -
Re: Help with my aged KC120-1 solar array
You should contact Wind-Sun directly to ask the question--they don't closely monitor this forum for direct business questions/issues and may miss your post.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Help with my aged KC120-1 solar array
Glad your going to get the panels replace for free!
all solar panels are warranted by the manufacture NOT the re-seller
My site gets allot of hits on this issue as if you google on KC-120 failure, my forum comes up with the #1 hit ... :roll: -
Re: Help with my aged KC120-1 solar array
Glad to here they stepped up seems like they have been very good about taking care of there customers. enjoy the full potential of the new array
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed