XW 4548 grid-tie and MPPT-60 hunting
aj164
Solar Expert Posts: 122 ✭✭✭
I just upgraded the firmware on a grid-tied XW setup. It has 105AH of AGM batteries (48V) and 3.2kW PV array. (The discussion on low battery cap vs PV is in another thread.)
With the latest firmware (from Xantrex website), I noticed the XW hunting between sell back and charge. (The charger on the XW is currently enabled.) We had about 500W of solar power available that evening. The battery amps would slowly alternate between +1.7A and -0.5A with a cycle time of maybe 15 seconds. Loads on the sub-panel were around 125W at the time, and the rest available to sell back or charge the battery.
I also changed the battery charge settings to those recommended by DEKA for their AGM batteries. The voltages are significantly lower than the Xantrex default for AGM, which we had been running. The new values are:
bulk/absorb: 55.2
absorb time: 120min
float: 54.0
eq: 56.4
XW sell voltage: 52.8
I know AGM is not supposed to EQ, but the DEKA EQ voltage is very low, and I think 56.4V was the Xantrex default for bulk/absorb.
We're waiting for a sunny day to see what it does under heavy PV power.
-AJ
With the latest firmware (from Xantrex website), I noticed the XW hunting between sell back and charge. (The charger on the XW is currently enabled.) We had about 500W of solar power available that evening. The battery amps would slowly alternate between +1.7A and -0.5A with a cycle time of maybe 15 seconds. Loads on the sub-panel were around 125W at the time, and the rest available to sell back or charge the battery.
I also changed the battery charge settings to those recommended by DEKA for their AGM batteries. The voltages are significantly lower than the Xantrex default for AGM, which we had been running. The new values are:
bulk/absorb: 55.2
absorb time: 120min
float: 54.0
eq: 56.4
XW sell voltage: 52.8
I know AGM is not supposed to EQ, but the DEKA EQ voltage is very low, and I think 56.4V was the Xantrex default for bulk/absorb.
We're waiting for a sunny day to see what it does under heavy PV power.
-AJ
Comments
-
Re: XW 4548 grid-tie and MPPT-60 hunting
The newer firmware hunts more than the older version, your inadequate battery bank will just make the issue worse. For a 4kw sell, your system requires 400ah battery bank, until you address this you will have issues.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed