MC connectors and wiring in parallel
Keet
Registered Users Posts: 7 ✭
So I'm onto the next phase of trying to design the wiring for my array.
I've taken the Isc of the panels and multiplied it by the 1.56, then divided the fuse rating by the number,
it gave me 3.74, so I should be able to parallel 3 panels and stay under the fuse rating, correct?
The next part is what is the best method to connect the panels in parallel;
There are MC connectors you can buy that are 2:1, or 3:1 or,
Can I bring them into a junction box and wirenut them together before going on to the fuse panel? (this is fairly low current, <7A)
Just trying to figure out a way to reduce cost a bit without having to buy a huge fusebox and 12-16fuseholders n fuses
Thanks!
I've taken the Isc of the panels and multiplied it by the 1.56, then divided the fuse rating by the number,
it gave me 3.74, so I should be able to parallel 3 panels and stay under the fuse rating, correct?
The next part is what is the best method to connect the panels in parallel;
There are MC connectors you can buy that are 2:1, or 3:1 or,
Can I bring them into a junction box and wirenut them together before going on to the fuse panel? (this is fairly low current, <7A)
Just trying to figure out a way to reduce cost a bit without having to buy a huge fusebox and 12-16fuseholders n fuses
Thanks!
Comments
-
Re: MC connectors and wiring in parallel
To be NEC complaint, each panel will need is own fuse. -
Re: MC connectors and wiring in parallel
But I thought as long as you remain under your panel and conductor current limits you could parallel them? -
Re: MC connectors and wiring in parallelBut I thought as long as you remain under your panel and conductor current limits you could parallel them?
Few panels have a maximum allowed current of 3X of there ISC ( short circuit current ) rating
Look at the rating of your panel, the maximum current should be listed and that will be what limits what you can parallel without additional fuses. -
Re: MC connectors and wiring in parallel
Nope. The logic to fusing each one, is if one panel shorts out, the rest could/will feed into their max current into that shorted panel.
This is also true if you parallel more than two batteries. -
Re: MC connectors and wiring in parallelSolar Guppy wrote: »Few panels have a maximum allowed current of 3X of there ISC ( short circuit current ) rating
Look at the rating of your panel, the maximum current should be listed and that will be what limits what you can parallel without additional fuses.
ISC is 1.19
Fuse rating on the back of the panel says 5A
isn't 3 panels x1.19 <5A ? -
Re: MC connectors and wiring in parallelSolar Guppy wrote: »Few panels have a maximum allowed current of 3X of there ISC ( short circuit current ) rating
Look at the rating of your panel, the maximum current should be listed and that will be what limits what you can parallel without additional fuses.
Ok, so can I do 2 panels and a 3A fuse?
If a short happens in one of the panels, the fuse would only let 3A in before popping,
and the other panel in parallel with it being 1.19A Isc,
would still be less then the 5A rating, yes?
Thanks for your patience.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed