Yet another grounding question...
czyhorse
Solar Expert Posts: 42 ✭✭
Hi all,
I have one more question about grounding...Can anyone explain the reasoning behind the NEC requiring your equipment grounding conductor to increase proportionally in size to oversized current carrying conductors?
I have a 1100 Watt inverter that will have 2/0 welding cable running to it from the batteries. It would normally require only a 6awg conductor, but I oversized it. Does that mean I need a 2/0 grounding conductor just for the inverter's equipment ground? This doesn't make sense to me.
What would be the minimum size equipment grounding conductor I could use in this instance?
I have one more question about grounding...Can anyone explain the reasoning behind the NEC requiring your equipment grounding conductor to increase proportionally in size to oversized current carrying conductors?
I have a 1100 Watt inverter that will have 2/0 welding cable running to it from the batteries. It would normally require only a 6awg conductor, but I oversized it. Does that mean I need a 2/0 grounding conductor just for the inverter's equipment ground? This doesn't make sense to me.
What would be the minimum size equipment grounding conductor I could use in this instance?
Comments
-
Re: Yet another grounding question...
I am not an electrician--but the sizing of the grounding conductor in the equipment I designed was to be large enough to trip the up stream circuit protection device...
So, if you have a 15 amp breaker and a 0000 welding cable, you would not need to up size past the standard 14 awg wire.
HOWEVER, if you had very long run and you installed 0000 to reduce voltage drop--At least I had to work out what was needed to both handle the over current and have low enough voltage drop to trip the breaker (i.e., a very long 14 awg wire would have too high a resistance to reliably trip the circuit breaker--so the ground would need to be scaled larger).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Yet another grounding question...
Since the breaker between my inverter and battery bank is 125A, then according to 250.122 of the NEC I would be required to use 8awg for the equipment grounding conductor? Is this correct?
-
Re: Yet another grounding question...
According to that table, #8 is good for *up to* 100a. Since you are using a 125a over-current device, you would need to move up to the next size - #6 if using cu, or #4 if using al.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed