24 v battery bank low voltage question
rrroae
Solar Expert Posts: 46 ✭✭
What should the low voltage setting on a 24 volt battery bank be set at? I thought it should be 2x the setting of a 12 volt bank of 12.1 to keep from going below 50% so I set it at 24.2.
My battery bank is 4 Crown 395amphr 6 volts wired together for 24 volt and I thought this should give me at least 180 amp hours of electricity bet we're closer to 70! Batteries are stored in basement and we have a 2" pvc vent pipe going into the enclosure. Battery temp monitor shows temp usually around 55' degrees this winter
I checked the specific gravity late today and all cells were in the 1.265 - 1.275 range.
Am I doing something wrong?
My battery bank is 4 Crown 395amphr 6 volts wired together for 24 volt and I thought this should give me at least 180 amp hours of electricity bet we're closer to 70! Batteries are stored in basement and we have a 2" pvc vent pipe going into the enclosure. Battery temp monitor shows temp usually around 55' degrees this winter
I checked the specific gravity late today and all cells were in the 1.265 - 1.275 range.
Am I doing something wrong?
Comments
-
Re: 24 v battery bank low voltage questionWhat should the low voltage setting on a 24 volt battery bank be set at? I thought it should be 2x the setting of a 12 volt bank of 12.1 to keep from going below 50% so I set it at 24.2.My battery bank is 4 Crown 395amphr 6 volts wired together for 24 volt and I thought this should give me at least 180 amp hours of electricity bet we're closer to 70! Batteries are stored in basement and we have a 2" pvc vent pipe going into the enclosure. Battery temp monitor shows temp usually around 55' degrees this winter
- Voltage measurements?
- Temperature corrected Hydrometer?
- Amp*Hours / Watt*Hour / Battery Monitor?
- Battery Tester?
I checked the specific gravity late today and all cells were in the 1.265 - 1.275 range.
How are the absolute values vs when the battery has just been equalized?
Is the above reading temperature compensated for 55F vs 77F?
You can make some temperature/charge compensated tables for your specific gravity like this gentleman. [note: I looked closer at the charts, and currently they have the SG temperature offset applied backwards--SG gets higher, denser, as temperature falls, not as temperature increases--I have sent an email to the person a while ago--so I don't know when/if this will be fixed]
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: 24 v battery bank low voltage questionHow are you determining the 70 AH capacity?
Heaviest daily load might be 12 amp.How are the absolute values vs when the battery has just been equalized?Is the above reading temperature compensated for 55F vs 77F? -
Re: 24 v battery bank low voltage question
Since you have a battery monitor--take a look at the Amp*Hours out--that is more accurate than measuring 24.2 volts under load (wait a least an hour for accurate battery "resting voltage" to estimate state of charge).
Regarding temperature compensation--I was asking about Specific Gravity Temperature compensation... From this chart, a 55F battery reading should be compensated by:- 1.265 at 55F - 0.010 = 1.255 at 80F (Temperature corrected SG reading to 77/80F standard condition)
Next time you have a chance, equalize (until the SG stops rising after 1 hour) and use those as your "maximum" SG levels to compare with for 100% charge.
And don't feel you have to hit 100% every day--hitting 90% every few days is fine. Trying for 100% charge every day will eventually cause damage to the battery (too much electrolysis/equalization drives oxygen into the positive grid causing corrosion).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed