80A Din Rail Breakers

Options
serge74
serge74 Registered Users Posts: 7
Has anyone here heard of a 80A din rail breaker that is UL listed for 24V? I found a SQD breaker that could possibly fit the bill but I am uncertain if it is really UL listed for 24V. It does say that it is listed for 48V but it doesn’t mention anything about 24V. Any ideas?

QOU Miniature Circuit Breakers
• Terminal lug wire size 1- #14 - #2 AWG Cu or Al
• Reversible line and load lugs for convenient flush or surface mount wiring
• DIN mounted (symmetrical rail 35 x 7.5 DIN/EN 50 022)
• UL Listed asHACR type -- 15 A to 70 A
• Field installable quick connectors
• Single handle with internal common trip
• UL Listed 48 Vdc (5,000 AIR)
http://www.squared.com/us/products/circuit_breakers.nsf/unid/BE0C1313F4DE3DB185256C870057204C/$file/QOUcircuitbreakerFrameset.htm

Comments

  • niel
    niel Solar Expert Posts: 10,300 ✭✭✭✭
    Options
    Re: 80A Din Rail Breakers

    the qo and qou type breakers are rated to 48v, but i don't see an 80a version.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    Re: 80A Din Rail Breakers

    And the rating is for 48 volt DC Maximum... Lower voltage use is fine (within the current rating).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Options
    Re: 80A Din Rail Breakers

    You might try Midnite Solar. They have an extensive selection of din rail breakers. Although 80 Amps DC is a bit stout. They may have a source, or something for a product in development. good Luck Vic
    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.