Invert on Demand with an XW6048 Inverter and a 200amp Generac Auto Transfer Switch
- If the grid goes down, the inverter goes into invert mode automatically. In invert mode, there is no load (whole house transfer with no dedicated circuits) on the output until the transfer switch is manually thrown. Has been made to work that way and functions perfectly with no faults or warnings.
- When the grid returns, the transfer back to the grid happens seamlessly and there is no evidence of, or anomalies associated with the transfer, like digital clocks or tv's/dvrs that need to reboot/reset.
- Grid tie disconnected from grid tie position and the transfer switch not switched; gets F30.
- Transfer switch activated with grid remaining connected - no Fault; as soon as the grid is disconnected (Transfer Switch changed to backup source and T1/T2 (house loads) connected to E1/E2 (utility or backup power source)), F29 (there's a clue here and need more info).
Here is what the Transfer Switch user manual says about the transfer of T1/T2 (house loads) to E1/E2 (utility or backup power source):
- E1/E2 (Generator Input): These lugs are directly connected to the standby generator. They are energized only when the generator is running.
- T1/T2 (Load Output): These terminals connect directly to the home’s main electrical panel (or a subpanel).
- Isolation Mechanism: Inside the ATS, a transfer contactor acts as a double-throw switch. When utility power is present, T1/T2 is connected to the utility lugs. Upon power failure, the controller breaks the utility connection and moves the mechanism to bridge T1/T2 to E1/E2, ensuring no backfeed occurs.
Seems reasonable to believe that in this case, there is standing power on T1/T2 bc the device used to trick the inverter into invert mode is to use a contactor to break its grid tie connection to the utility source in the transfer switch, when in all that is apparent, there is the assumption that power from the utility has been lost. This provides the moment of switching with an instant (make before break) where a backfeed can occur in this case. The fault remains (red led is lit) during the demand invert period, but disappears when the demand period ends and a subsequent 5 minute countdown ends. When the on demand invert period ends, the transfer back to the grid happens seamlessly and there is no evidence of, or anomalies associated with the transfer, like digital clocks or tv's/dvrs that need to reboot/reset or other faults.
The above design which uses a normally closed contactor to break the grid tie connection was originally and ideally designed to open the grid connection at the transfer switch. Unfortunately the availability of a normally closed 200amp contactor was not an item that I could find sans using one not specifically intended for such a project as mine; not to mention costs running into the thousands of $. Normally closed contacts provide for reduced energy usage in this case; "normally open" contactors in the 200amp range are available and reasonably priced.
Alternatively, the system as designed and how it's currently working could be used as is; it doesn't seem to have any adverse effects and the XW inverter manual suggests that F29/F30 are both "Automatic" which is what I believe is happening.
There are obviously some leaps of faith in all of the above, but I'm hoping that someone can cast some light on this.
TIA, Nick
Categories
- All Categories
- 229 Forum & Website
- 136 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 179 Solar Information links & sources, event announcements
- 892 Solar Product Reviews & Opinions
- 252 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 816 Wind Power Generation
- 620 Energy Use & Conservation
- 622 Discussion Forums/Café
- 316 In the Weeds--Member's Choice
- 74 Construction
- 125 New Battery Technologies
- 107 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed