powmr 6500w 230v inverter 2 wire L&N&G for USA?
patdufo
Registered Users Posts: 9 ✭✭
I bought this which has 50 or 60hz option and up to 240v,but did not know that it had 2 wire instead of 3,can i use this in the USA?Want to power a small hot tub or a 240v mini-split inverter AC?Can it be done?I also have a 110v to 120v 10000va transformer to work with?
Comments
-
also cant return unfortunately
-
Some 220/240 VAC appliances in North America will run just on two Hots (no neutral). Should work OK with those units.20
On units that require 120/240 VAC, in theory, you could run the 240 Side with 240 VAC, and use your 240 VAC transformer to step down and run the 120 VAC side--And if Neutral bonding required, just neutral bond the 120 VAC leg (probably the "floating" 120 VAC leg, not the leg connected to 240 VAC hot).
HOWEVER, while I have done some pretty "different" wiring schemes for 120/240 VAC / 3 phase mills and lathes, I had full schematics for them and could trace out the wiring and (for some) require them internally to "separate" the 120/240/single phase/3 phase connections).
I would be hard pressed to do this with any new equipment that I did not have any manuals for. The chances that something could go wrong, or the unit simply not work--I would not recommend doing this.
HOWEVER, if you had some equipment that you did not care about (a used AC system, etc.) and wanted to risk it--It may work. Older equipment with less internal safeguards may be a more reliable conversion.
In the end, there is no "one right" answer for this inverter+transformer. There will be "risk" (from damage to fire/shock hazard), and it would not be something to try without good knowledge of what you are attempting.
The other downside, transformers do take power, even if they have zero load... You could be getting a 5% (of transformer rated capacity) as losses... With solar, we try to avoid losses as they require more panels (and more batteries) to run the "extra" transformer.
And there are questions about the inverter... The manual for your inverter?
https://cdn.shopify.com/s/files/1/0746/0415/1079/files/POW-HVM4.5K-24V_6.5K-48V_User_Manual_V1.2.0601.pdf?v=1717209326
It does list H/N 220 VAC connections. In North America, we assume that H1/N/H2 connections have the N "ground Bonded" somewhere (typically in the main service panel).
Some AC inverters just pass thru the N connections, others will actually switch a ground bond to the N (for example) RV usage where sometimes the system is running from "shore power" (N+G bond in shore power panel), and other times open the G+N bonding when running off grid.
Given that 220 VAC single wire systems usually ground bond one of the leads--This is different vs 120/240 VAC split phase north American power where H1 and H2 are just 120 VAC with respect to ground/Neutral--How this would affect the Powmr inverter--I have know idea.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed