Hello everyone,
I need to add a breaker between my charge controller output to the battery busbar. The charge controller output about 100A but I have a 100A non polarity DC breaker which run very hot when the cc is at peak work hours.. pushing out about 95A.
I was considering running another 100A breaker using a Y connection ie terminate the cable from cc to a point and draw 2 equal length wires from that point to the 2 breakers. The breaker output would also be equally terminated to the battery busbar.
What are the dangers of this approach?
Comments
-
Are you just looking for a disconnect? Your breaker operates on heat and you can't escape that fact. Your single breaker probably won't even trip at 140A. I test a lot of breakers and many just don't qualify as useful protective devices.
-
I would not parallel breakers--But just get a larger Amp rated breaker and the wiring to support that current.
Normally, I suggest that Branch CirFcuits that are carrying "continuous loads" (such a gym lighting, large fans, and battery charging) use the NEC derating of 80% (at least) for branch circuits that are subjected to continuous loads (hours or more at "full current")...
For example, a 100 Amp breaker+wiring:
100 amps * 0.80 = 80 amps suggested max continuous current
Or for a 100 amp continuous load:
100 amps * 1/0.80 (or * 1.25 NEC derated) = 125 Amp minimum rated branch circuit
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed