Paralleling 2 non polarity dc breakers
bigbrovar
bigbrovar Registered Users Posts: 32 ✭✭
Hello everyone,
I need to add a breaker between my charge controller output to the battery busbar. The charge controller output about 100A but I have a 100A non polarity DC breaker which run very hot when the cc is at peak work hours.. pushing out about 95A.
I was considering running another 100A breaker using a Y connection ie terminate the cable from cc to a point and draw 2 equal length wires from that point to the 2 breakers. The breaker output would also be equally terminated to the battery busbar.
What are the dangers of this approach?
  • NANOcontrol
    NANOcontrol Registered Users Posts: 288 ✭✭✭
    Are you just looking for a disconnect? Your breaker operates on heat and you can't escape that fact. Your single breaker probably won't even trip at 140A.  I test a lot of breakers and many just don't qualify as useful protective devices.
    I would not parallel breakers--But just get a larger Amp rated breaker and the wiring to support that current.
    Normally, I suggest that Branch CirFcuits that are carrying "continuous loads" (such a gym lighting, large fans, and battery charging) use the NEC derating of 80% (at least) for branch circuits that are subjected to continuous loads (hours or more at "full current")...
    For example, a 100 Amp breaker+wiring:
    100 amps * 0.80 = 80 amps suggested max continuous current
    Or for a 100 amp continuous load:
    100 amps * 1/0.80 (or * 1.25 NEC derated) = 125 Amp minimum rated branch circuit