97TJ
Solar Expert Posts: 68 ✭✭
Hello, It's been some time since I've asked a question here. One of my 200 watt panels gave up the ghost and seeing that they are over 10 years old I thought I would replace them all and use the good ones on another project. I upgraded to a MPPT 150 volt 60 amp charge controller last year when I had to replace my old lead acid crowns with 3 100ah lifepo4 batteries. This last winter was brutal due to the lack of sunshine in my area. Instead of (4) 12 volt 200 watt panels in parallel for 800 watts, I want to series/parallel (6) 12 volt 200 watt panels for 1200 watts total. The panel I am looking at is rated at 22.5 volts VOC and 12.21A ISC each. So if I series two panels together then parallel the three sets of two in my combiner box will I have an array of 45 volts at 36.63 amps? I live in a cold snowy climate. While I'm not sure what it is, I know that there is an adjustment concerning the voltage for those cold sunny winter days but if my figures are correct I should be with the safety parameters. Thank you in advance.
Comments
-
Old model number and make? From my experience, you really need more solar. It does depend on your requirements but to me 1500 watts is entry level for a climate you describe Good Luck!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
As always, refer to the manual for safety limits (voltage, current, etc.)...
Just a quick set of math for sizing the array... Nominally, for an off grid system suggest 10-13% rate of charge, and upwards of 20% for areas with "dark" winters (I.e., not much sun, so over paneling does not "waste" much energy with an XX Amp controller)(Note: 300 AH @ 12 volt battery bank assumed):- 300 AH battery bank * 14.5 volts nominal charging * 1/0.77 panel+controller derating * 0.10 rate of charge = 565 Watt array minimum suggested off grid array
- 300 AH battery bank * 14.5 volts nominal charging * 1/0.77 panel+controller derating * 0.13 rate of charge = 734 Watt array (more or less optimum for Lead Acid Battery banks)
- 300 AH battery bank * 14.5 volts nominal charging * 1/0.77 panel+controller derating * 0.20 rate of charge = 1,130 Watt array suggested maximum for 300AH @ 12 volt battery bank
For a 60 amp MPPT controller... The maximum "most efficient" solar array for a 12 volt battery bank would be:- 60 Amps * 1/0.77 panel+controller deratings * 14.5 Volts charging = 1,130 Watt array "typical" cost effective maximum array for 60 amp MPPT controller on a 12 volt battery bank
Just for a quick summary of some other quick rules of thumbs... Normally would suggest that a battery bank is sized to deliver 1/4 of its storage capacity per day (i.e., 2 days of "no sun" stored energy, to 50% planned state of charge--And on rare occasions to 20% state of charge).
So, for a 300 AH @ 12 volt battery bank:- 300 AH * 0.25 discharge = 75 AH per day (or over night) discharge
- 75 AH * 12 volts * 0.85 AC inverter eff = 765 Watt*Hours per day/night discharge
https://pvwatts.nrel.gov/pvwatts.php
Worst case December with 1.85 hours of sun (not much) and a 1,200 Watt array (a little more clipping on cool/clear days):- 1,200 Watt array * 0.77 panel+controller derating * 1.85 hours of average Dec Sun = 1,709 WH per average December day (or a little less in December and "over paneled")
Need to have the exact specifications for your 200 Watt panels... Voc/Vmp/Isc/Imp... You would typically put 2 or 3 panels in series (check Voc-cold for your panels) and parallel the strings (2s*3p or 3p*2s)... 2s*3p would work with almost any solar panels and charge controller.
If you have three or more parallel strings, you are supposed to used a "Combiner Box" with fuses or circuit breakers (help reduce the chance of fire if one panel/wire run becomes shorted)... If you can go with 2s*3p, you can save the price of a combiner box.
Lots of details to work out--In general, size the battery bank to your loads, and size the solar array to your battery/loads/hours of sun. And in the "far north", a Genset, possibly a wind turbine (lots of issues), etc. are usually needed for those dark/stormy days...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thank you for your help. My kilowatt meter shows that over the last 79 days my average usage has been 682 watts per 24hr. Day/night. By time I add what it takes to run the inverter I'm just under 1050 per 24hr day/night . I do have a generator to top off the batteries as needed. So, I will go with 6 200 watt panels in 2S3P into the combiner box I already have. Thanks again.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed