Hi can i use a 7.5 kw inverter with 120 volts (10 battery X 12 volt) with 96 volts setup (8 batteries of 12 volts)
Tagged:
Comments
-
Welcome to the forum Soalr_Wale!
Specifically, what AC inverter do you have (Link)?
In general, many (most?) FLA (flooded cell lead acid batteries) set (for example) a "dead" FLA battery at 10.5 volts (for a 12 volt battery). When an FLA battery gets down to that voltage--There is very little energy left in the cells, and very likely with permanently damage the cell(s) / Battery.
So, for a 10 battery bank * 12 volt would report a battery bank as "dead" at 10*10.5 volts or 105 VDC.
An 8x12 volt bank with a nominal 96 VDC would normally be reported as "dead" with a 120 VDC nominal designed AC inverter.
Checking the manual for any possible configuration adjustments could possibly allow you to reprogram to use a somewhat lower nominal battery bank.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed