Utility AC too high. Set Xantrex XW 6048 limit lower?
lelson
Registered Users Posts: 6 ✭✭
For years, utility voltage was steady at 120VAC. Recently noted odd behavior with some appliances (microwave, chest freezer). Concurrently, got faults with both grid tie Sunny Boy and Xantrex inverters in early morning. Utility (AC1) occasionally offline (protected circuits showed change to battery backup). Odd thing was that unprotected circuits were still energized. After reviewing documents, I think this made sense. The utility admits several large voltage regulators in the substation failed and pegged high (134VAC). They're working on a permanent fix and instituting temporary fixes (linesmen manually adjusting voltage as loads change daily).
In the morning, usage is low, voltage goes up. When the sun comes up, the inverters try to match the high utility voltage and fail to do so at some (+5%?) voltage. Once the AC1 voltage reaches the advanced settings limit (AC1 Hi Volt set to default of 132V), the Xantrex disconnects from the utility. The protected circuits then are fed by the battery (and ultimately by the generator). Once the utility (AC1) drops below 132 for the required 300 seconds (as the day warms up and neighbors turn on their A/C, lowering the voltage), the Xantrex re-connects to the grid.
Although this has been a steep learning curve for me, other (old) posts on this Forum have addressed this in what I consider an odd way:their response to out of range utility voltages is to increase AC1 Hi Volt so the Xantrex remains connected to the utility. Utility linesmen say this can "burn down a house". At the very least, appliances can be damaged. The average neighbor will just think it is about time for his $10K fridge to burn out.
So here's my question: given that the standard tolerance for utility 120 AC is +-6V (5%) why doesn't it make sense to set AC1 Hi Volt to 126 and AC1 Lo Volt to 114? This would at least protect some of my appliances from this insidious situation that can happen with no warning.
Comments
-
lelson said:For years, utility voltage was steady at 120VAC. Recently noted odd behavior with some appliances (microwave, chest freezer). Concurrently, got faults with both grid tie Sunny Boy and Xantrex inverters in early morning. Utility (AC1) occasionally offline (protected circuits showed change to battery backup). Odd thing was that unprotected circuits were still energized. After reviewing documents, I think this made sense. The utility admits several large voltage regulators in the substation failed and pegged high (134VAC). They're working on a permanent fix and instituting temporary fixes (linesmen manually adjusting voltage as loads change daily).
Probably XW is in passthru. Wait for them to fix, if you can. Have them repair any damage! Nevada Energy?In the morning, usage is low, voltage goes up. When the sun comes up, the inverters try to match the high utility voltage and fail to do so at some (+5%?) voltage. Once the AC1 voltage reaches the advanced settings limit (AC1 Hi Volt set to default of 132V), the Xantrex disconnects from the utility. The protected circuits then are fed by the battery (and ultimately by the generator). Once the utility (AC1) drops below 132 for the required 300 seconds (as the day warms up and neighbors turn on their A/C, lowering the voltage), the Xantrex re-connects to the grid.
They need to fix this.Although this has been a steep learning curve for me, other (old) posts on this Forum have addressed this in what I consider an odd way:their response to out of range utility voltages is to increase AC1 Hi Volt so the Xantrex remains connected to the utility. Utility linesmen say this can "burn down a house". At the very least, appliances can be damaged. The average neighbor will just think it is about time for his $10K fridge to burn out.So here's my question: given that the standard tolerance for utility 120 AC is +-6V (5%) why doesn't it make sense to set AC1 Hi Volt to 126 and AC1 Lo Volt to 114? This would at least protect some of my appliances from this insidious situation that can happen with no warning.
If you do this the XW will just be on battery more as you are decreasing the range the utility will continue to power protected loads. I would do this in your situation but there always is the law of unintended consequences. What does your installer say?
I know they are long gone... XW6048 is the .oldest of 3 XW generations BTW
I would really make sure you have surge protection on XW inputs and whole house loads. Good Luck and where are you?
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
If your solar can support your loads, this would be a great time to go offgrid until it is fixed ! Good Luck from Gardnerville!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:
The way I see it, a big part of the reason for solar is to help during grid failures. Up til now that meant when the grid was down but "burning down my house" might be considered a grid failure. Sure, using the batteries for a few hours has financial consequences, but I think the tradeoff is good. My question was really "what (other) unintended consequences" might I expect?
If you do this the XW will just be on battery more as you are decreasing the range the utility will continue to power protected loads. I would do this in your situation but there always is the law of unintended consequences. What does your installer say?
I know they are long gone... XW6048 is the .oldest of 3 XW generations BTW
I would really make sure you have surge protection on XW inputs and whole house loads. Good Luck and where are you?Yep. Independent Power Corp went belly up some time ago Still love the XW6048 here in N. Douglas County. Thanks for your input...Dave Angelini said:If your solar can support your loads, this would be a great time to go offgrid until it is fixed ! Good Luck from Garnerville!
-
Other consequences ? I do not know all the particulars of your situation. I do this for a living. I have seen so many weird installations and people doing crazy things with electricity and their homes. Hopefully they get this fixed soon.
Good time to back up your data😉
Douglas county was rocking Saturday night at Bally's. We saw the Led Zep tribute band Zoso. They were really good!
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:
The way I see it, a big part of the reason for solar is to help during grid failures. Up til now that meant when the grid was down but "burning down my house" might be considered a grid failure. Sure, using the batteries for a few hours has financial consequences, but I think the tradeoff is good. My question was really "what (other) unintended consequences" might I expect?
If you do this the XW will just be on battery more as you are decreasing the range the utility will continue to power protected loads. I would do this in your situation but there always is the law of unintended consequences. What does your installer say?
I know they are long gone... XW6048 is the .oldest of 3 XW generations BTW
I would really make sure you have surge protection on XW inputs and whole house loads. Good Luck and where are you?Yep. Independent Power Corp went belly up some time ago Still love the XW6048 here in N. Douglas County. Thanks for your input...Dave Angelini said:If your solar can support your loads, this would be a great time to go offgrid until it is fixed ! Good Luck from Garnerville!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed