24v & 48v ground hookup
solarhills99
Registered Users Posts: 18 ✭✭
Dumb question for someone who has been at this for 40 yrs. but I have both a 24v and a 48v battery bank. I have to hook up the grounding wires to the same buss going out to my rod, yes?
Comments
-
Safety Grounding....
Assuming that both systems are in the same home/cabin/power shed, and share "metallic" items (electrical boxes, conduit, even on the AC inverter output side), then yes, connecting the Negative 24 VDC battery bus to the same ground rod/cold water pipes, AC grounding, etc. allows any short circuit from 24+, 48+, 120/240VAC, etc. to exposed metal (conduit, sinks, plumbing, electrical cabinets, etc.) to find a path the the common ground connection (typically at "the ground rod" can then find a return path to the "source (batteries, AC inverter output, etc.) and trip those fuses/breakers/electronic shut downs (prevent fire, electrocution potential, etc.).
For "safety grounding", a single point of ground for all of the AC and DC systems helps ensure there is only one path through the safety grounding system.
What we don't want is "multi-point" grounding (in general) because if we do two or more connections between "return" (DC negative, AC neutral wiring, etc.) then the green wire and (white/negative) wiring is in parallel, and the normal current flow is now "shared" between the power cables (hot/return/etc.) and green wire safety ground--Which we don't want.
There can be a case made for multi-point grounding to ground rods... Typically for lightning protection (i.e., a solar array mount tied to local earth ground rod, then 6 AWG cable from remote ground rod to local power shed/home "master" ground rod. Lightning likes to find the "shortest route" to earth ground and will typically find a "better path to earth" after 10-20+ feet of grounding cable run (the technical term is cable "impedance" and not just simple cable resistance). The local ground rod provides lightning to earth path, and the 6 AWG cable back to the main home/shed ground rod provides the DC/AC current path to trip breakers and fuses with short circuits.
Clear as mud?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks Bill,Crystal clear.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed