230 vac to 120/240 vac

signjack
signjack Registered Users Posts: 2
i have several off grid inverters 1 is 230 vac and I need to convert to split phase 120/240 vac. I need to run 2 hp well pump 240 vac 300' draw

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    edited May 2023 #2
    SingJack,
    Do you need to convert to 120/240 VAC split phase for well pump?
    Most 240 VAC motors (single phase) only need 2 hots (L1,L2) to run the motors...
    You may need 120 VAC to run pump "electrics" (relay, water level sensor, etc.) which could (possibly) use a simple 240 to 120 VAC transformer.
    I would try to avoid a 230 VAC L1/L2 to a split phase 240 VAC (L1/L2/N) transformer. An isolation transformer that large will be expensive and can waste power (plus need a lot of "magnetization" / start up current (hard on AC inverter).
    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset