Replacing old Mitsubishi panel
DanKegel
Registered Users Posts: 23 ✭✭
My 2008-era rooftop system, Xantrex GT 4.0 plus 22 Mitsubishi PV-UD175 panels, needs some love.
One panel shattered in the storm last month, and finding exact replacements is hard. I found some of the 185 watt panels, though.
Any risks with that substitution?
One panel shattered in the storm last month, and finding exact replacements is hard. I found some of the 185 watt panels, though.
Any risks with that substitution?
Comments
-
It sounds like you may have 11 series * 2 parallel strings or is it (probably not) 22 series string * 1 string of panels?
Your panels are(?):
http://www.solardesigntool.com/components/module-panel-solar/Mitsubishi/PV-MF175UD4/specification-data-sheet.html- STC Power Rating 175W
- PTC Power Rating 156.1W 1
- STC Power per unit of area 12.4W/ft2 (133.2W/m2)
- Peak Efficiency 12.7%
- Power Tolerances -5%/+10%
- Number of Cells 50
- Nominal Voltage not applicable
- Imp 7.32A
- Vmp 23.9V
- Isc 7.93A
- Voc 30.2V
Can you tell us a bit more about your solar array configuration?
Your options appear to be:- find a panel +/-10% on Vmp & Imp for replacement
- remove the "bad panel" electrically (and/or physically) and run a 20 panel array for now
- Find two new panels that "match" Imp (10%), remove one bad panel from string 1 and one good panel from string 2, and use the two new Imp matched panels (and keep the spare "good panel" as a replacement if ever needed).
- 23.9 volts Vmp * 11 = 262.9 volts Vmp-array-std
- 262.9 volts * +/- 10% = +/- 26.29 volts Vmp "new panel"
So, in theory, you can match a replacement panel with Imp=7.32 volts +/10% and Vmp=23.9 volts +/- 26.29 voltsThe above are possible "close enough to function" matches that I could quickly find... You might find the shipping costs of larger format panels to be pretty high... Checking with local to you suppliers and see what they have that could match are options.
In theory, you could simply bypass the broken panel and the array+GT inverter should be "OK" (albiet with the loss of 175 Watts of panel).
Or you can find a "reasonable match" 23.9 volts Vmp +/- a few volts and "match Imp" and the system will be pretty much good as new.
For example of a "sort of fix" here is a 140 Watt panel @ 12 volts (and some other single panel sort of matches):
https://www.solar-electric.com/ameresco-bsp140-12-140-watt-12-volt-solar-panel.htmlElectrical Specifications:
- Maximum Power (Pmax): 140W
- Voltage at Pmax (Vmp): 19.4V
- Current at Pmax (Imp): 7.21A
- Short-Circuit Current (Isc): 7.77A
- Open-Circuit Voltage (Voc): 23.1V
SLP150-12 Specifications:
- Has 35mm frame
- Maximum power (Pmax): 150 Watts
- Nominal voltage: 12 Volts DC
- Voltage at Pmax (Vmp): 18.5 Volts DC
- Current at Pmax (Imp): 8.11 Amps DC
- Open-circuit voltage (Voc): 22.2 Volts DC
- Short-circuit current (Isc): 8.68 Amps DC
- Power tolerance: +/- 5%
- Dimensions: 59.06" x 26.57" x 1.38"
- Weight: 26.68 pounds
SLP200S-24U Specifications:
- Maximum power (Pmax): 200 Watts
- Nominal voltage: 24 Volts DC
- Module efficiency: 20%
- Voltage at Pmax (Vmp): 33.73 Volts DC
- Current at Pmax (Imp): 6.17 Amps DC
- Open-circuit voltage (Voc): 39.21 Volts DC
- Short-circuit current (Isc): 6.5 Amps DC
- Power tolerance: ± 5%
- Dimensions: 61.81" x 27.76" x 1.38" (35mm)
- Weight: 26.84 pound
Replacing older panels is difficult. The available panels keep changing and can be difficult to find replacements for.
Another option would be took at replacing the entire array... New panels are in the $0.50 to $1.00 per Watt price range (not including labor and shipping). Much less expensive that my array from 20+ years ago....
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I think it's two strings of 11, as you suspected.
Dunno if they are literally connected in parallel, guess I should rtfm for the inverter.
Happy to just pull the old panel, I should check if there is enough slack in the cables to bypass the hole (assuming the strings aren't really jumpers in parallel?).
-
Assuming that your panels use MC4 connectors--You can get pre-made cable sets (and various "Y" adapters):
https://www.solar-electric.com/search/?q=mc4+cables
If you choose to jumper around the missing panel (or change to 10 series * 2 parallel) you are connecting the "missing panel" jumper (if needed).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed